Issue
Set up a two wire LTS80 Lini-Temp sensor on a 7700 DCU
Environment
7700 DCU
LTS80 Lini-Temp sensor
Cause
Conversion coefficients must be set for proper reading of temperatures.
Resolution
For Fahrenheit:
- M = 0.17582
- B = -279.4
For Centigrade:
- M= 0.09768
- B = -173.0
Refer to TCON 095 for Resistor(s) 41-55 to clip (suggest you clip only one side)