Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,842
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 7
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 17
    • 18
    • 19
    • …
    • 507
  • Next »

AS-P/B DHCP Server Configurability

Issue Webhelp and the Technical Reference Guide supply information for using the AS-P/B DHCP server option, however, a number of relevant questions have not been answered. Product Line EcoStruxture Building Operation Environment Building Operation Automation Server Premium (AS-P 0.62 hardware) Building Operation Automation Server Bundled (AS-B) Building Operation SmartX IP Multi-purpose Controller (MP-X) Building Operation SmartX IP Room Controller (RP-C) Building Operation SmartX Controller IP-IO Series Cause There are typically a number of options to configure DHCP servers, but since the DHCP server included with the AS-P/B is very basic and NOT configurable, it's important to understand which options are and are not available. Resolution Webhelp has some helpful information about the DHCP Server Options. The AS-P/Bs built-in DHCP server assigns unrouted IP addresses within the range of addresses from 10.110.210.2 to 10.110.210.254. This was developed to allow for a quick configuration of a private MP-X/RP-C network. The AS-P/B DHCP server can be disabled and another DHCP server can be used. Here is a list of other questions and answers that may come up based on typical options in other DHCP servers: Can the scope of the IP range be configured? There is no way to configure or limit the range of the standard IP address range or to have multiple scopes. Can IP exceptions be configured? There is no configuration option to prevent the AS-P/B DHCP server from assigning a specific IP address. The AS-P/B DHCP server is unaware of static IP addresses, so if a switch or other device has a static IP set in the 10.110.210.2 to 10.110.210.254 range, you run the risk of having the AS-P/B DHCP server assign an IP address twice which can cause a number of issues. Can a Default gateway be configured? Not configurable Can a Subnet mask be configured? Not configurable Is IP6 supported? No Can lease types be configured? No Can multiple DHCP servers be installed on the private LAN? No Should MP-X/RP-C IP level devices only be hosted within the private AS-P/B network? Most site IT departments prefer that the BAS networks be isolated, however, if the network switch (Not the AS-P/B) is used for assigning DHCP IP addresses, it could hand out addresses to the AS-P/B and the MP-X/RP-C devices if they are on the same subnet. A managed (RSTP Enabled) switch can reside as a client to the AS-P/B. This is due to how the Private DHCP option is advertised. On-site IT departments may not want the switch on the customer's LAN so it is placed in the private AS-P/B network. Does the AS-P/B DHCP server assign addresses to 3rd party devices? Yes, if the 3rd party device supports this. This would be a configurable option in the device.
View full article
Admiral Alan_Wood Admiral
‎2021-02-23 07:26 AM

on ‎2021-02-23 07:26 AM

Labels:
  • EcoStruxure Building Operation
4945 Views

SER8000 series room controllers communications options

Issue SER8000 series room controllers communications options Environment SER8000 series room controllers Cause Integration to SER8000 room controllers via Modbus is required.  Resolution Currently, the SER8000 series room controllers communications options are Zigbee Pro or BACnet MS/TP. Refer to the SER8300 datasheet.  To communicate on Modbus RS-485, an option would be to use the multi purpose manager (MPM-UN) as a gateway device.    * Updated July 2015 As per Product Annoucement PA-00428, the SE8000 with firmware 1.3 can now act as a Modbus slave using the RS-485 port. 
View full article
Picard Product_Support
‎2018-09-11 06:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:49 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
4916 Views

Cannot open a PCT project when the computer running PCT has no connection to the network DHCP server

Issue The Project Configuration Tool is installed as a Server. A project can be created but when it should be saved, an error says, "Failed to open project," and "Failed to start VM." Product Line EcoStruxure Building Operation Environment PCT version 1.1.1 Cause When PCT is installed as a server PCT, and a project is opened, the computer running PCT must have a connection to the DHCP server in the network. Resolution Make sure that the computer running PCT has a good connection to the DHCP server in the network.
View full article
Picard Product_Support
‎2018-09-10 08:52 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 09:47 PM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
4917 Views

PCT Installation Issue Error:1722, Error:1603, "The setup has detected no version of SBO Project Configuration Tool is installed."

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue During certain situations, it may be required to remove and re-install PCT to address software conflicts with other software applications. While trying to remove/install PCT you may receive an error preventing you from completing the installation. The setup had detected that no version of SBO Project Configuration Tool is installed.  The specific command-line options require that the application be installed to continue. The setup will now terminate. Error: -1603 Fatal error during installation. Consult Windows Installer help(Msi.chm)or MSDN for more information. Error 1722. There is a problem with this Windows Installer... Product Line EcoStruxure Building Operation Environment Client versions (64 Bit Only): Editions: Pro, Home, Enterprise Windows 10 Windows 8.1 Windows 8 Windows 7       Server versions (64 Bit Only): Editions: Standard, Enterprise Server 2008 R2 Server 2012 Server 2012 R2  PCT versions (64 Bit OS Only): SBO Project Configuration Tool v 1.0.0.487 - SmartStruxure Solution - Software SBO Project Configuration Tool v 1.0.0.510 - SmartStruxure Solution - Software SBO Project Configuration Tool v 1.1.0.47 - SmartStruxure Solution - Software SBO Project Configuration Tool v 1.1.1.49 - SmartStruxure Solution - Software SBO Project Configuration Tool v 1.1.2.57 - SmartStruxure Solution - Software Cause In order to get past a possible installation loop, you will need to locate and delete the following Windows registry key: [HKEY_CLASSES_ROOT\Installer\Products\B2A4F0AEC8BB0E2438706F07E2E2560B] Resolution Note: Always make a backup of your registry before making any modifications.   Run regedit.exe Locate/Search: Computer\HKEY_LOCAL_MACHINE\SOFTWARE\Classes\Installer\Products\B2A4F0AEC8BB0E2438706F07E2E2560B Delete Registry Key entry: B2A4F0AEC8BB0E2438706F07E2E2560B  
View full article
Picard Product_Support
‎2018-09-10 07:24 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-11-29 02:46 PM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
4904 Views

Rehosting a Vista 5 License on the FlexNet License Server

Issue Instruction on how to use your Entitlement to rehost Vista 5 License onto a new host computer or dongle. Product Line TAC Vista Environment Vista 5 Dongle Host ID Flexnet Licensing Entitlement Vista Licensing website Cause Limited documentation exists for how to properly rehost a Vista license on the Vista licensing website Resolution NOTE: Please remember that 5.0.X license files are not backwards compatible with versions of Vista 5.1.X. If your current license files are 5.0.X you must install 5.0.3 or earlier to properly rehost your license. Log onto https://schneider-electric.flexnetoperations.com and enter your Entitlement or Activation ID. To obtain an unknown ID, follow instructions in Lost license Entitlement ID Vista 5.x. In the top corner of the Home Page Select LICENSE SUPPORT and List Licenses This Entitlements license(s) will be listed. Select the License you wish to rehost by checking the Tick box located just left of the License. In the Action Menu, Select Rehost. Select Add New Host. From the Server Host Dropdown, select either ETHERNET (MAC address) or VENDOR DEFINED (Dongle) depending on your site. Enter the Mac address or Dongle ID to be used in the textbox *note that a Dongle ID must be entered as "TAC_HL_ID=##########" Select OK The New Server Hosts will now be populated with the correct Host ID. Click Next. Select Verify to verify the Host ID is valid Select Rehost to generate the new License. From the main page, select the License you wish to retrieve by checking the Tickbox located just left of the License. Select View and Save To File or Email license to obtain the .lic file. It may be a good idea to compare the old .lic file with the new .lic file in Notepad to ensure they contain the same features. It is possible that the site license was a combined license generated from multiple Entitlements. If this is the case, repeat the steps above for each Entitlement then follow instructions in Manually Consolidating License Files.
View full article
Picard Product_Support
‎2018-09-10 05:00 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:14 AM

Labels:
  • TAC Vista
4913 Views

MNL-V1RVx, MNL-V2RVx and MNL-V1RVx-2, MNL-V2RVx-2 differences

Issue MNL-V1RVx, MNL-V2RVx and MNL-V1RVx-2, MNL-V2RVx-2 differences Environment I/A Series Micronet LON VAV controllers Cause Part number MNL-V1RVx has been replaced with MNL-V1RVx-2 and part number MNL-V2RVx has been replaced with MNL-V2RVx-2.  The datasheet F-26365 indicates the parts as MNL-V1RVx and MNL-V2RVx.  Resolution The MNL-VxRVx and the MNL-VxRVx-2 are functionally the same. The '-2' was added to the part number to indicate an enhancement to the VAV actuator assembly to reduce the operation noise level of the actuator. 
View full article
Picard Product_Support
‎2018-09-11 06:00 AM

Labels:
  • TAC IA Series
4972 Views

Changing the Automation Server HTTP / HTTPS ports

Issue Changing the Automation Server HTTP / HTTPS ports, 1.3 or higher. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause There is a need to change the Automation Server's HTTP and/or HTTPS ports from the default ports of 80 (HTTP) and 443 (HTTPS). Resolution The HTTP / HTTPS ports of the Automation Server can be changed from Struxureware/EcoStruxure Building Operation WebStation, requires SBO/EBO V1.3 or higher.  From a web browser*, connect and log on to the Automation Server. After you have logged on, click on the 'Account menu' near the top right corner: EBO 4.0.3 or higher,  From the "Options" select 'Setting'. From the network tab, you can change the HTTP / HTTPS ports.    EBO V4.0.2 or lower, From the "Options" select 'Device Configuration'.   The TCP/IP configuration page should appear. From here, you can change the HTTP / HTTPS ports.       3. Perform a Warm Start on the Automation Server to apply the HTTP / HTTPS port changes to the server.     * Check supported web browsers for Struxureware/EcoStruxure Building Operation at the WebStation specification sheet, make sure to select the correct SBO/EBO version: WebStation (se.com)     Firefox 4 or later (32-bit)
View full article
Picard Product_Support
‎2018-09-10 11:30 PM

Last Updated: Lt. Commander Reza Lt. Commander ‎2022-08-19 10:41 AM

Labels:
  • EcoStruxure Building Operation
4886 Views

Netcontroller will not come online in Continuum

Issue Netcontroller will not come online in Continuum although the unit can be pinged. Product Line Andover Continuum Environment Continuum 2nd generation controllers (NC2 (CX9680), ACX57, CX9702, bCX4040, bCX9640) 1st generation addendum Cause Even though a unit can be pinged, that does not mean the unit will come online within Continuum, as the "ping" is a very low level communication Resolution Check all settings are correct (IP address, ACCNetID, Subnet Mask, Default Router(Gateway Address)) Check the correct network ports are open, see Router required open port numbers to run a Continuum system Check the site fits within the compatibility matrix, see Software and Firmware compatibility matrix for older versions of I/NET, Vista, Andover Continuum, Satchwell Sigma, I/A Series, and StruxureWare Building Operation Check there is only a single Network Card enabled on the CyberStation  For a second generation NetController (NC2, ACX57, CX9702, bCX) Check the web page can be accessed, if it can then double check the network settings. Connect a temporary single user Continuum laptop to the controller directly, manually reset the IP address and bring the controller online (using 169.254.1 Subnet). If this operates correctly then controller fault is eliminated. If the controller is not faulty then the network and/or the Continuum installations will need to be checked. Addendum for first generation controllers: Attach to the controller via hyperterminal to determine it's perspective and to verify the IP address, ACCNetID, Subnet Mask, Default Router. You can also verify if the netcontroller lists the Workstation as a controller indicating it can see the workstation. If not, perform a teach from the Workstation.
View full article
Picard Product_Support
‎2018-09-09 10:51 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:59 AM

Labels:
  • Andover Continuum
4879 Views

OPC or DDE with EcoStruxure Building Operation

Issue Support for OPC or DDE integration with EcoStruxure Building Operation Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Cause The OPC Server is a software program that converts hardware communication protocol into the OPC protocol. The OPC client software is any program that needs to connect to the hardware. The OPC client uses the OPC server to get data from or send commands to the hardware. Resolution Neither the OPC server nor the DDE configuration is supported at this time. There is not currently a roadmap for direct OPC client or server capability within the EcoStruxure Building Operation. To avoid problems with OPC Integration (and lose a project), there are two options for OPC integeration: It is possibe to use a converter to convert OPC to/from one of EBO supported protocols.  For example, use a 3rd party software to translate all the OPC points into BACnet Objects, “OPC Server -> BACnet Server”, or translate all EBO BACnet points to OPC. Perhaps one of the software programs below will be of benefit. Take into consideration what specifically will the ES be doing. If it is exchanging point values then it should work fine. Kepware Matrikon SCADA engine Note: These are 3rd party products that are not supported by Shneider Electric.    Use a SmartConnector Extension to be a middleware between EBO and OPC cilent or server. Check available extenstions at Exchange shop and SmartConnector Server and refer to EBO SmartDriver and Smart Connector KB article for more information.
View full article
Picard Product_Support
‎2018-09-10 05:35 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2022-07-25 04:27 AM

Labels:
  • EcoStruxure Building Operation
4875 Views

The differences between Function Block Editor and Menta Editor

Issue SmartStruxure uses two different function block programs. Menta Editor is used for Xenta programmable controllers while Function block editor is used in the Automation or Enterprise server. The two programs are not interchangeable and do have several differences. Product Line EcoStruxure Building Operation Environment Function Block Editor Menta Editor Cause There are several differences between Function Block Editor and Menta Editor that are important to know. Resolution Download the relevant version of the Function Block Editor and Menta Editor Difference Guide from Exchange. This guide will cover the following topics: An overview of Function Block programming The programming differences Function Block Editor and Menta Editor differences Program Conversion Importing Xenta programmable controller programs Building function block programs to I/Os Binding values Binding values using a binding template Time schedule and alarm blocks Trend logs Overview of Function Block Editor Block differences
View full article
Picard Product_Support
‎2018-09-11 08:35 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-08-26 06:25 PM

Labels:
  • EcoStruxure Building Operation
4888 Views

Examples for the new native EBO Notification Reports

Issue Are there any Example Reports for the new native Notification Reports which came out in EBO 3.2 to replace the now deprecated WebReports and Report Server? Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause As of EBO 2022 (4.0) WebReports and the Report Server have now been deprecated and replaced by External Log Storage using Postgres SQL and Timescale DB, plus the new native Notification Reports which are now built into EBO 3.2 and above, but there are no examples to help new starters to get going. Resolution A Schneider-Electric Community page has been set up specifically for Notification Report users so that they can share their Reports and collaborate on Reporting ideas: https://community.se.com/t5/EcoStruxure-Building-Operation/Reports-showcase-share-your-reports/m-p/388619#M75732
View full article
Admiral David_Kendrick Admiral
‎2022-05-17 02:00 AM

Last Updated: Janeway Omaelk ‎2022-10-19 12:51 AM

Labels:
  • EcoStruxure Building Operation
4885 Views

SQL Server Implicit conversion from data type datetime to int is not allowed

Issue An update from 1.94 to 1.94 SP1 will generate an "Installation error! Microsoft ODBC SQL Server Driver SQL Server Implicit conversion from data type datetime to int is not allowed. Use the CONVERT function to run this query." Product Line Andover Continuum Environment Continuum Windows XP Windows 7 Windows Server 2003 Windows Server 2008 Cause A column in the db doesn't get converted properly SQL Server Implicit conversion from data type datetime to int is not allowed Use the CONVERT function to run this query. Resolution To correct this issue apply the following hotfix AFTER installing 1.94 SP1 but BEFORE running the database update Hotfix for DataBase Update Error
View full article
Picard Product_Support
‎2018-09-11 06:54 PM

Labels:
  • Andover Continuum
4836 Views

Error when trying to activate embedded license

Issue When trying to activate a license in an AS-P/B the following error message was shown and the activation failed: Online activation: 12:57:24: Executing licensing command 12:57:24: Executing embedded operation: Activate ActivationID: ACT-xxx 12:57:32: Embedded operation: Activate failed: ASEmbeddedAPI internal error: Binary response does not contain feature information Error status information: FNO server response: Z(BACK_OFFICE%DEBACK_OFFICE+']\dBl&%MSM230312018I|B}~%ACT-xxxxx/jlSkkj1%<K!,b7OnpUy7 zqDFG#I$QGGR0:SYWJVGIuW}+iea 0\wR/`;yX'HGX*;;nEl]d0I+nHWh(VD"+a uwpf%XF[N6~!,^?R]y?VPCw\gB{"dSy2K7ph;_=qw.|c]Vp;.nlMbLl-~Z!UY<:=TFZEL~h=\V)>ML)ld0g'PPcjrosy&]p9Y((?II#*B5/U16X;o- 12:57:32: Licensing command completed 12:57:34: Activating licenses failed   Offline activation: 12:56:02: Executing licensing command 12:56:02: Executing embedded operation: ProcessResponseFile ResponseFile: C:\Users\Mitthem\Desktop\Garage\response\xxxxxxx\8ba20b60-b19c-4a5d-8fea-693ef9282c8c.bin 12:56:03: Embedded operation: ProcessResponseFile failed: ASEmbeddedAPI internal error: Binary response does not contain feature information Error status information:  12:56:03: Licensing command completed 12:56:05: Activating licenses failed Product Line  EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Building Operation Automation Server Bundled (AS-B) Building Operation Device Administrator (DA)  Embedded Licenses Cause The reason for the issue was that the number of available licenses for activation was 0, but the error message in DA was not indicating that. The Device Administrator (DA) showed that two licenses were available but were out of sync. Resolution When looking at the Entitlement in DA, it had a yellow dot on it, indicating that it was added offline. In DA version 5.0.2 and later, DA contacts the License server directly when adding an Entitlement in prior versions this was done through the AS-P. In DA version 5.0.2 and later, it is enough that the computer where DA is installed has an internet connection when adding an Entitlement online. After upgrading DA to version 5.0.2 and refreshing the Entitlement, the Device Administrator showed the correct number of available licenses.    If upgrading the site to this version is not possible, the Entitlement ID / Activation ID availability and device list can be verified by using the User Portal FlexNet Login (flexnetoperations.com) It is also possible to run Device Administrator version 5.0.2 with the concurrent site version used as long as the Servers are at 4.0.4 and above to check, verify and activate licenses.     Important Note: Device Administrator 5.0.3 and above will NOT support lower-version Automation Servers as 5.0.2 does.  This is due to new features of embedded licenses for servers as well as the handling of servers without internet connections.  In this case, ALL servers must run the same version as the Device Administrator version when handling licenses.         Further information on Automation Server Licensing Overview is available through the online WebHelp.  
View full article
Janeway Jonas_Brissman Janeway
‎2023-05-01 07:02 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2024-02-29 10:43 PM

Labels:
  • EcoStruxure Building Operation
4870 Views

TC900 Modbus bias, termination and number of devices

Issue What is the unit load of a TC900 thermostat and what are the bias and termination requirements when used with a SmartX Server. Product Line EcoStruxure Building Operation, Field Devices Environment TC907-3A4LMA TC907-3A4DLMSA TC907-4FMSA TC907-3A4DPMSA TC907-3A4DPMSA-24 TC903-3A4LMA TC903-3A4DLMSA TC903-4FMSA TC903-3A4DPMSA TC903-3A4DPMSA-24 SmartX Server Cause Documentation does not state the RS-485 transceiver type for the TC900 range, making it unclear how many devices can exist under a SmartX servers RS-485 serial port ComA or ComB. Resolution Use the Worksheet for Configuration of RS-485 Bus with generic RS-485 devices on Webhelp to determine the appropriate Modbus configuration. The answers to the transceiver interface attributes below can be applied to complete the worksheet. Q1 Failsafe Receiver : The TC900 uses an RS-485 transceiver with an integrated idle-state failsafe receiver. Q2 Data Transmission Speed : TC900 thermostats can be configured to communicate at 4800, 9600, 19200 or 38400 bps. Q4 Isolated Interface : The TC900 does not provide an isolated RS-485 interface. Q6a Measured Resistance : With no electrical connections to the TC900, the measured resistance between the RS-485 low-side (-) signal and the communications common is 8.2K ohms. Based on this the unit load of the TC900 is 1.46 (12.000/8,200) Bias requirements and number of devices If there are only TC900 devices on the RS-485 bus then Generic RS-485 Network Device configuration 1 applies, configuration becomes very simple and no node or distance reductions are called for. The failsafe receivers can typically operate with no added bias resistors. Connect a 120 ohm termination resistor across the + and - data lines at the head end of the bus (typically at the SmartX server). Connect another 120 ohm termination resistor across the + and - data lines on the last node at the far end of the bus. Connect the shield drain wire to earth ground terminal rail in the panel with the SmartX server. This is the only ground connection of the shield for the complete cable segment. Connect the RET/Shield terminal (see the figure below) on the SmartX server to the ground rail in the panel using a 12 AWG (3.31 mm²) to 18 AWG (0.82 mm²) wire. Since the TC900 has a unit load of 1.4 the maximum number of devices that can be placed under each comm port using this configuration is 21 (31.5 / 1.46 = 21.5) Also check out the SmartStruxure-RS485-Controller Unit Load Quick-Help video on the Exchange. Note:  Adding an RS-485 Repeater at this point provides another 32 Units Loads to the Network which can be continued up to the Architectural Maximum defined for the hosting controller.
View full article
Administrator CraigEl Administrator
‎2020-07-14 06:58 PM

Last Updated: Admiral David_Kendrick Admiral ‎2024-11-18 06:56 AM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
4854 Views

System Performance Considerations using a Xenta 555/731 with MicroNet and IAC controllers

Issue The object information received from a MicroNet and IAC controller is based on a request for information from the Xenta. If the local area network receives too many requests, the system will not operate as quickly as expected. It is important to configure the objects with a realistic poll time to avoid issues with slow system response. Product Line Satchwell MicroNet Environment Xenta 500 Xenta 700 Satchwell MicroNet Cause Slow graphic, alarm, updates Resolution Updated June 2019 The MicroNet 50 series range MN350, 450, 550, 650 LCD and Touchscreen have been withdrawn from sale. The IAC 420, 600 and Touchscreen have now also been withdrawn from sale. No direct replacement is offered. Further information on these changes can be found in PA-00495 - Notice of Withdrawal - Satchwell Sigma and PA-00528 - End of Commercialization - Satchwell Sigma. ---------------------------------------------------------------------------------------------------------------------------------------------------------- Network Architecture The size of a MicroNet/Satchnet network within XBuilder is not limited. It is quite possible to have 80 Unifact Pro controllers directly connected on an NCP RS485 network; ARCNET and Satchnet networks with routers can be much larger than this. With such large networks, to achieve acceptable system performance, the number of signals requested and their poll rate must be considered when engineering the Xenta 555. Note that Satchnet networks run four times slower than MicroNet NCP networks. Bandwidth and Performance  Because both MicroNet and Satchnet networks are polled, there is a limited bandwidth available in which to obtain all signal data. This means that it is necessary for the Xenta 555 to request each programmed signal (point) in turn from each controller. There are many factors which deter-mine the performance of a network, however it is generally accepted that certain signal parameters should update more frequently than others. The Xenta 555 has a special dynamic poll scheme that is inherent in the controller and needs no configuration. The polling of any signal depends on the signal type and its poll frequency. Priority is given to signals with the fastest poll rate; therefore some mea-sure of control can be applied to the prioritization of signals. The most important signals should be configured with the fastest poll rate. In the event that a particular signal is referenced more than once, for example, in an alarm, log and web page, that signal appears in the poll scheme once only and is polled at the fastest rate (that is, the fastest of the alarm rate, log rate or web page rate). Typically, the order of engineering priority should be: 1 Alarms 2 Web pages 3 Logs Tip Connection objects should be kept to a minimum because each connection comprises a read signal and a write signal (that is, two operations). Performance example Consider a Xenta 555 ARCNET or NCP network with three web clients showing three web pages (two alarm pages and one values page with 50 signals). The Xenta 555 configuration comprises a total of 480 signals: . 100 alarm signals set with a scan time of four seconds. . 300 logs at a logging interval of one hour. . 30 connection objects at a period of 10 seconds. 50 point signals on a values page with a fixed refresh time of 10 seconds. In this network, the signals will arrive in the alarm pages typically within 60 seconds. Connection objects and signals in values pages will update within 60 seconds. The Xenta 555 polling algorithm computes the optimum poll rate for each signal, therefore if the sum of the poll frequencies exceeds the available bandwidth at any particular time, the lower frequency polls will be delayed. This has the effect of spreading the polls out over the available bandwidth and therefore optimizing performance. Signals on graphics pages and values pages are only polled when the page is being displayed in a web browser, however when a signal is required for logging, alarming or for a connection object, the signals are continuously polled at the configured poll time Web Page Updates Some examples of expected polling rates follow: - In addition to MicroNet network updates, web pages are updated at regularly intervals and this should be considered when analyzing the over-all performance; ten seconds should be considered typical for a web page update. However, polling performance is affected by the number of web clients and the number of web pages. If each web client simultaneously requests a different web page, each with a set of signals not currently being polled (for example, alarms), then the number of polled signals will increase substantially and therefore slow down the rate of web page updates. For this reason it is recommended that the number of web clients is restricted to three for a typical Xenta 555 network as described in the example given earlier. Due to a slightly enhanced Native Communications Protocol (NCP) and Attached Resource Computer Network (ARCnet)  employed by the 50 series controller a small difference between the 100 series and 50 series controller Packets/Min can be seen, these are indicated below. Xenta555 - MNMI NCP Polling 50 Objects 10 Polls/Sec 426 to 595 Packets/Min MN620 526 Packets/Min MN650 567 Packets/Min Xenta555 - MNMI ARCnet Polling 50 Objects 10 Polls/Sec 426 to 595 Packets/Min MN620 484 Packets/Min MN650 495 Packets/Min Xenta555 - SNP 1200 Polling 50 Objects 2.5 Polls/Sec 169 to 174 Packets/Min Xenta555 - SNP 4800 Polling 50 Objects 7.5 Polls/Sec 398 Packets/Min These times are the averages found during testing, these figures will be affected by the following: - 1. The amount of controllers on the LAN (The Xenta 555/731 carries out some background polling an each controller for online and null output status). 2. The controller type has a small bearing on the polling rate per second. 3. Quality of the communications wiring.(poor wiring or incorrect cable specification can cause errors and re-tries) 4. Quality of the controller wiring, particularly with ARCnet installations. (Unscreened inputs ETC can result in noise reaching communications cable causing errors). 5. With the Xenta 731 particularly a high level of Menta programs ETC can cause time delays if the Xenta processor struggles to process all the information in good time. Further information can be found in the TAC Xenta 555 Supplement Manual.
View full article
Picard Product_Support
‎2018-09-10 12:19 AM

Last Updated: Sisko DavidChild Sisko ‎2019-06-19 03:09 AM

Labels:
  • Satchwell MicroNet
  • TAC Vista
4817 Views

Identify the Sigma version or build number installed on a computer

Issue The ability and procedure to identify the version of Sigma software on a system. Product Line Satchwell Sigma Environment Release number: 1, 2, 3, 3.1, 3.3, 3.4, 3.6, 3.7, 3.7 SP2, 3.7 SP3, 3.10, 3.11, 4.00, 4.00 SP2, 4.00 SP4, 4.01, 4.01 SP1, 4.01 SP3, 4.01 SP4, 4.01 SP4a, 4.01 SP5, 4.02, 4.03, 4.03 SP1, 4.04, 4.04 SP1, 4.04 SP2, 4.04 SP3, 4.05, 4.05 SP1, 4.05 SP2, 4.05 SEB, 4.06, 4.07, 4.07 SP1, 4.07 SP2, 4.08 Build number: 1.52, 2.13, 3.12, 3.17, 3.3, 3.31.1, 3.32.10, 3.33.9, 3.33.11, 3.33.13, 3.34.11, 3.34.11, 3.36.11, 3.36.16, 3.36.20, 3.37.08, 3.37.09, 3.37.12, 3.37.13, 3.37.16, 3.37.18, 3.39.09, 3.40.06, 3.40.09, 3.41.14, 3.41.15, 3.41.16, 3.41.18, 3.41.19, 3.42.34, 3.42.43, 3.42.48, 3.43.18, 3.44.14, 3.44.16, 3.44.18, 3 45 48, 3 45 51, 3 45 58, 3.46.57, 3.46.62, 3.46.70, 3.46.72, 3.46.73, 3.46.79, 3.46.80 3.46.81, 3.46.85, 3.46.86, 3.46.89, 3.46.98, 3.46.104, 3.46.105, 3.46.107, 3.46.108, 3.46.110, 3.46.111 Cause Software installed is identified with a build number and not a release number. Resolution To view the Sigma build number, using a Sigma client running locally on the Sigma server, select About System Manager from the Help menu. The displayed window shows the Sigma release and build number Refer to the table below to find the Release No. Sigma Release No. Build No. Software/Firmware File Date   SigmaX   Release 1 1.52 Software/Firmware 22.06.2001 SigmaX 4.5 Release 2 2.13 Software/Firmware 14.02.2002 SigmaX 5.2 Release 2 3.12 Supplement 14.02.2002 SigmaX 5.2 Release 3 3.12 Software 31.07.2002 SigmaX 5.2 Release 3.1 3.17 Software 17.09.2002 SigmaX 5.2 Release 3.3 3.3 Software 30.07.2003 SigmaX 5.2 Release 3.4 3.31.1 Software 03.10.2003 SigmaX 5.2 Release 3.6 3.32.10 Software 19.11.2003 SigmaX 5.2 Release 3.7 3.33.9 Software 22.12.2003 SigmaX 5.2 Release 3.7 SP2 3.33.11 Software 27.01.2004 SigmaX 5.2 Release 3.7 SP3 3.33.13 Software 19.02.2004 SigmaX 5.2 Release 3.10 3.34.11 Software 21.04.2004 SigmaX 5.2 Release 3.11 3.34.11 Supplement 31.08.2004 SigmaX 5.2 Release 4.00 3.36.11 Software 16.12.2005 SigmaX 6.0.1 Release 4.00 SP2 3.36.16 Software 02 03 2006 SigmaX 6.0.1 Release 4.00 SP4 3.36.20 Software 23.05.2006 SigmaX 6.0.1 Release 4.01 3.37.08 Software 07.09.2006 SigmaX 6.0.1 Release 4.01 SP1 3.37.09 Software 26 09 2006 SigmaX 6.0.1 Release 4.01 SP3 3.37.12 Software 20 10 2006 SigmaX 6.0.1 Release 4.01 SP4 3.37.13 Software 13 08 2006 SigmaX 6.0.1 Release 4.01 SP4a 3.37.16 Software 17 11 2006 SigmaX 6.0.1 Release 4.01 SP5 3.37.18 Software 05 01 2007 SigmaX 6.0.1 Release 4.02 3.39.09 Software 26 01 2007 SigmaX 6.0.1 Release 4.03 3.40.06 Software 06 06 2007 SigmaX 6.0.1 Release 4.03 Sp1 3.40.09 Software 09 08 2007 SigmaX 6.0.1 Release 4.04 3.41.14 Software 27.02.2008 SigmaX 6.0.1 Release 4.04 SP1 3.41.15 Software 09.05.2008 SigmaX 6.0.1 Release 4.04 SP2 3.41.16 Software 15 09 2008 SigmaX 6.0.1 Release 4.04 SP3 3.41.18 Software 08 01 2009 SigmaX 6.0.1 Release 4.04 SP4 3.41.19 Software 08 01 2009 SigmaX 6.0.1 Release 4.05 3.42.34 Software 06 11 2009 SigmaX 6.0.1 Release 4.05 SP1 3.42.43 Software 22 03 2010 SigmaX 6.0.2 Release 4.05 SP2 3.42.48 Software 26.08.2010 SigmaX 6.0.2 Release 4.05 SEB 3.43.18 Software 08 12 2010 SigmaX 6.0.2 Release 4.06 3.44.14 Software 01 12 2011 SigmaX 6.0.2 Release 4.06 SP1 3.44.16 Software 01 12 2011 SigmaX 6.0.2 Release 4.06 SP1 3.44.18 Hotfix 01 02 2012 SigmaX 6.0.2 Release 4.07 3 45 48 Software 20 08 2012 SigmaX 7.0.6 Release 4.07 SP1 3 45 51 Service Pack 09 12 2012 SigmaX 7.0.6 Release 4.07 SP2 3 45 58 Service Pack 20 12 2013 SigmaX 7.0.6 Release 4.08 3.46.57 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.62 Hotfix 21.05.2014 SigmaX 7.0.7 Release 4.08 3.46.70 Hotfix 23 07 2014 SigmaX 7.0.7 Release 4.08 3.46.72 Hotfix 04 08 2014 SigmaX 7.0.7 Release 4.08 3.46.73 Hotfix 12 08 2014 SigmaX 7.0.7 Release 4.08 3.46.79 Hotfix 08 10 2014 SigmaX 7.0.7 Release 4.08 (**1) 3.46.80 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.81 Hotfix 17 02 2015 SigmaX 7.0.7 Release 4.08 3.46.85 Hotfix 19 03 2015 SigmaX 7.0.7 Release 4.08 3.46.86 Hotfix 19 03 2015 SigmaX 7.0.7 Release 4.08 (**2) 3.46.89 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.98 Hotfix 14 12 2016 SigmaX 7.0.7 Release 4.08 (**3) 3.46.104 Software 28 02 2017 SigmaX 7.0.9 Release 4.08 3.46.105 Hotfix 10 03 2017 SigmaX 7.0.9 Release 4.08 (**4) 3.46.106 Software 28 03 2017 SigmaX 7.0.9 Release 4.08 3.46.107 Hotfix 08 08 2017 SigmaX 7.0.9 Release 4.08 3.46.108 Hotfix 01 05 2018 SigmaX 7.0.9 Release 4.08 (**5) 3.46.110 Software 13 05 2019 SigmaX 7.0.9 Release 4.08 (**6) 3.46.111 Hotfix 15 11 2019 SigmaX 7.0.9 Release 4.08 (**7) 3.46.131 Software 29 01 2020 SigmaX 7.0.9 Notes:   **1 Sigma build 4.46.57 with StruxureWare Building Operation v1.5 or 1.6 transition support program installed. **2 Sigma build 4.46.57 with StruxureWare Building Operation v1.8 transition support program installed. **3 Sigma build 4.46.57 with StruxureWare Building Operation v1.9 transition support program installed. **4 Sigma build 3.46.57 with StruxureWare Building Operation v2.01 transition support program installed. **5 Sigma build 3.46.57 with StruxureWare Building Operation v3.0.1, v3.0.2 and v3.0.3 transition support program installed.. **6 Sigma build 3.46.57 with StruxureWare Building Operation v3.0.4, v3.1 and v3.2 transition support program installed. **7 Sigma build 3.46.57 with StruxureWare Building Operation v3.2 or later transition support program installed.   Notes: 1. SigmaX version 7.0.9 is now available and can be used on any Sigma version that supported SigmaX version 7.0.6. 2. This information can be downloaded as a PDF file: Sigma Build Numbers 2023 3. When SigmaX 6.0.2 is installed, the build information provided by Sigma (Help > About) can be wrong (later than the actual version). This arises because SigmaX installs a file with Build 3.42.47 in the c:\sigma\bin folder. This is only a problem prior to Sigma Release 4.05 SEB.
View full article
Picard Product_Support
‎2021-01-07 05:36 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2023-04-28 02:32 AM

Labels:
  • Satchwell BAS & Sigma
4895 Views

Cable guide for LonWorks network

Issue Requirements / specifications on cables used in a LonWorks network Environment LonWorks Cable Wire Guide LonMark Cause There are special requirements on cables used for LonWorks networks between Lon devices. Resolution LonMark organisation is recommending cables according to their specification. An example of this is the Belden LonWorks cable guide. Also, Echelon has a Wiring Guideline and Users Guide.
View full article
Picard Product_Support
‎2018-09-10 11:46 AM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
  • TAC Vista
4847 Views

Associate AS BACnet Interface IO points with points on the IO bus

Issue How to associate BACnet IO points created under the BACnet Interface of the Automation Server with IO points on the Automation Server's IO bus. Product Line EcoStruxure Building Operation Environment Building Operation Servers 1.4 and above Building Operation Workstation Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Connect physical IO points to BACnet network controllers. Resolution BACnet Association Tool (EBO V3.0 or higher) BACnet Association Tool will map properties of a central IO point with corresponding properties of a BACnet point. The tool is capable of mapping a single IO point with a single BACnet point, optionally by also creating a BACnet point, and removing the association between IO and BACnet points. To open the BACnet Association Tool, Select the IO Bus or IO Module, BACnet Interface, Application Folder, or the BACnet point, then in the Actions menu, click BACnet Association Tool. Most useful is the ability to associate multiple IO points with their corresponding BACnet points in one operation. The tool can be run from a variety of different container types in the WorkStation Tree view, including an IO point, BACnet Point, CIO Module, or the entire IO Bus (as shown below). For more information refer to WebHelp articles: Creating and Associating BACnet Points to I/O Points (se.com) and Associating or Updating BACnet Point Associations to I/O Points (se.com) NOTE: Please be aware applying the BACnet Association Tool retrospectively, to an already configured site, can remove bindings to outputs.  For example output bindings in Script or Function Block programs.  As shown below, if the tool is used to create a BACnet Associated point for an output already bound to a program (1) the Requested Value will be replaced by the Associated Value of the BACnet point (2). This is due to how the BACnet Association Tool uses the bindings, where the newly created BACnet point should be used instead of the IO point.  The solution is to update the removed program binding (3) to use the BACnet Associated point value (4).   SBO 1.4 to 2.x To associate BACnet IO points created under the BACnet Interface of the Automation Server to points in the IO Bus in SBO 1.4 and above... The association is made via a read reference, so if we think of the two objects as one being the source and the other the destination you configure the association from the destination object so in the case of an output you configure the association from the BACnet object (in this example BO1). In the case of an input, you'd configure the association from the IO Bus input as that would be the destination object, in other words, the recipient of the value. (NOTE: for versions prior to 1.4 see Bacnet and StruxureWare Building Operation Central IO points) Create the points. In this example, we are associating an IO output point named 'Digital Output 1' with a BACnet Binary Output named BO1. From the properties page of the IO Bus point (Digital Output 1 in this example) click on the gear icon to the right of the 'Requested value' field. In the 'Requested value' editor click the navigation icon (...) to the right of the 'Reference' field and navigate to the 'Associated Value' of the BACnet point. Save the configuration changes. Now that the values have been associated setting the BACnet output value (BO1) will drive the IO Bus output (Digital Output 1)  
View full article
Picard Product_Support
‎2018-09-11 12:07 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-20 08:59 AM

Labels:
  • EcoStruxure Building Operation
4809 Views

Alarm code, Fast Run, Setup password for DC1100 and DC1400

Issue Alarm code, configuration code passwords for DC1100 and DC1400 Product Line Field Devices Environment DC1100 controller DC1400 controller Cause Configuration Resolution Passwords are: 0112 for configuration mode 0402 for fast run mode
View full article
Picard Product_Support
‎2018-09-06 02:15 PM

Last Updated: Sisko DavidChild Sisko ‎2019-11-08 03:06 AM

Labels:
  • Field Devices
4880 Views

Replacement I/NET Controller NICAD Battery info

Issue Replacement I/NET Controller NICAD Battery info., I/Net Batteries Product Line TAC INET Environment All I/NET controllers Cause Controller battery has failed, because the battery on the controller is over 5 years old   Resolution The 3 pin version Battery is used for the NPR2000 and the DPU48K (MIP Board) -- part number 3/V80H-SLF (Note this battery has to be order from an outside Vendor and not Schneider Electric). Click here to view a PDF on this part. The 7910, 7920, 7930 7780 & 7940 use the 2 pin version -- part number 3/V80H-LPC (Note this battery has to be ordered from an outside Vendor and not Schneider Electric). Click here to view a PDF on this part. The battery used on the 7700, 7716, 7718, 7728, 7720, 7928, 7793, 7798B, & 7798C (and like controllers) is the Dallas/INET part number 801288-07. This also can be ordered from the Rockford order entry using 01-2100-545 (Old CSI P/N 801288-07). This battery also has an outside Vendor source from Power-Sonic P/N - PCBM-3.6 Click here to view a PDF on this part. For battery testing process see How to test the NiCAD Battery on a Controller
View full article
Picard Product_Support
‎2018-09-10 02:12 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:23 PM

Labels:
  • TAC INET
4841 Views
  • « Previous
    • 1
    • …
    • 17
    • 18
    • 19
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login