Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Show raw card data of a badged card in Security Expert

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Show raw card data of a badged card in Security Expert
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5725 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Show raw card data of a badged card in Security Expert

Picard Product_Support
‎2018-09-10 12:45 PM

Last Updated: Guinan AdamSteele Guinan ‎2023-06-22 12:17 AM

Issue

How to show raw card data of a badged card in Security Expert.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert
  • Custom Card Format

Cause

Need to configure a custom card format and need to see the raw bit string to determine this.

Resolution

Displaying a cards raw data is a function that can be set in the Reader expander.

1. Confirm that the Display Card Data When Invalid option is enabled on the Reader tab under Misc Options.

Misc optionsMisc options

Display Card Detail When Invalid:
When enabled, the reader expander will display the actual card data received from the reader when the card number is not known. This can be used to interface with custom third party applications that require their own processing of card information. This option is enabled by default and can be used to add card data to a user when operating Security Expert. When disabled the reader will display the card number not found message.

2. Next, set the Reader format on the Reader tab under Configuration to Any bit (raw).

any bit rawany bit raw

3. Now when badging a card at this reader port it should populate two events. One for the Card Number Raw Data and another for the Facility Code Raw Data.

 

Example:

Read Card Number Raw Data: 46160846
Read Facility Code Raw Data: 436207616

  1. Put the facility code into a Programmer Calculator to convert from Decimal to Binary. This is a 32-bit number.
    00011010000000000000000000000000
  2. Of the 32 bit number take the first 8 Binary digits (in the example this is 0001 1010) and convert this back to decimal.
    00011010 bin = 26 dec
    What you should see in the decimal field is the bit length the card uses.
  3. Now in the Reader Format, it’s an experiment to find out which of the Bit options would correspond to the cards. (In the example above you would need to look through the 26 bit options.)
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (2)
  • Find more articles tagged with:
  • 19366
  • AdamSteele23
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore