Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 16
    • 17
    • 18
    • …
    • 509
  • Next »

Convert Trane BCU (BMTW or BMTX) from BACnet/Ethernet to BACnet/IP for integrating to a Niagara R2 UNC

Issue Is there a way to convert a Trane BCU (BMTW or BMTX) from BACnet/Ethernet to BACnet/IP for integrating to a Niagara R2 UNC? Product Line TAC IA Series Environment Trane BCU (BMTW or BMTX) Niagara R2 UNC Cause There are two components required to change over the BCU from BACnet/Ethernet to BACnet/IP. Resolution A special serial cable is required to download the BCU with the new configuration. Below are the pin outs to make the cable:     Access to the Tracer Summit software. Here are the steps for running the BCUconfig.exe program to change over the BCU from Ethernet to IP: Open Windows Explorer and navigate to C:\Program Files\Tracer Summit\Bin Double-click on BCUconfig.exe Enter the information and select download. Note - This is where you must have the Trane serial cable. The BCU will reset. Now change the Connection type in the Tracer Summit software to IP connection: Open the Tracer Summit software and select Connect. The Site connection Wizard will appear. Select the BACnet/IP radio button. From the Ethernet Configuration window, select the 'open on startup' check box. Select the 'Use BBMD connection' from the BACnet/IP configuration window. Specify the IP address of the BBMD BCU and the UDP port which is the BACnet port. Select Finish.
View full article
Picard Product_Support
‎2018-09-07 12:45 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-26 06:13 AM

Labels:
  • TAC IA Series
5500 Views

Sigma Client reports a "HTTP connection failed" error".

Issue The Sigma Client reports a "HTTP connection failed" error" when an attempt is made to start it. Product Line Satchwell Sigma Environment Satchwell Sigma release 4.05 and later Cause When the Sigma Client is started, attempts are made to make a connection to the Sigma Server, this connection fails and the Client cannot be started. Resolution There are a number of reasons why this error might occur, suggestions are listed below. 1.  Windows XP operating system - ensure that service pack 3 has been installed, and that all the Windows updates have been applied. 2. Windows 7 operating system - only Ultimate and Professional are supported. 3. Sigma Client/Server software must be installed by a Windows user with "Admin" privileges. 4. Windows Firewall must either have been switched off, or has "Exceptions" configured as explained in the Sigma 4.05 SP1 release note. 5. Check that the "SigmaSVR" service has been started. If this service cannot be seen, then this is an indication that the Sigma software has not been install by an "Admin" user, and the software must be reinstalled. 6. Corruption of the Windows "User" files has taken place. Create a new Windows user with "Admin" privileges. Log on to Windows as the new user and test the Sigma Client again. 7. If using a VMware image try rebooting the image. 8. SMART is being used and has a modem connected to the PC for uploading data. Ensure that the modem is fully functional. If not, the HTTP error can be caused. This was seen at Sigma: R4   Release 3.44.14. and Smart Task Manager  3.0.2.20. Added 26-07-2012 9. This may be because a proxy server is being used, eg on school networks. Log on to your PC computer with an administrator account. Open the "Start" menu and click on "Control Panel." Double-click on the icon labeled "Internet Options." Go to the "Connections" tab at the top of the window and then click on "LAN Settings." Make sure the box next to "Bypass proxy server for local addresses" is checked. Hit "OK" twice to confirm the new proxy port settings. Make sure the box next to "Bypass proxy server for local addresses" is checked. Hit "OK" twice to confirm the new proxy port settings. Added 25-09-2012. 10. This issue was reported from a School where Sigma 4.05 SP1 had been operating correctly for several weeks. The issue was traced to the Anti-virus software Sophos, which had received an update prior to the failure. Sophos had quarantined two Sigma dll files. To correct this issue both Sophos and Sigma were uninstalled. A later version of Sophos was installed, and then Sigma was reinstalled, this corrected the problem. Added 01-08-2013 11 - Sigma software installed when connected to a wireless network. The Sigma client will only connect to the server when the wireless connection is made. Uninstall Sigma, disable the wireless, enable the network card, and then reinstall the Sigma software. Added 03-10-2013 12. DELL PC, with firewalls and antivirus disabled and no wireless card fitted. There may be a service or an application running in the background as part of the vendors Windows platform makeup.Restore the same version of Windows, but without (where possible) any of the Vendors applications. Re-install Sigma. Added 16-05-2014 13. Check the port number in c:\sigma\bin\setupsvr.exe, the default is 8080. Added 19-05-2014 14. Flexera license software has been reported as a cause for receiving this error. Flexera license software uses port 8080, (IMADMIN.EXE). Stop Flexera and retry Sigma. Changing Sigma from port 8080 to 8081 could also provide a solution. Added 27-08-2014 15. The SBO PCS (StruxureWare Building Operation Project Configuration Server) also uses port 8080.This needs to be stopped or will conflict with Sigma and produce the HTTP error. Added 02-09-2014 16. Make sure any data is backed up from the installed Sigma system. Uninstall Sigma using Add/remove programs (Win XP) or Programs and features (Win 7). Wait for the Sigma un-install process has completely finish. Delete or rename the C:\Sigma folder to.......for example Sigma1. Re-install Sigma by using a right mouse click on the "SigmaSetup.exe" file and select  A new clean Sigma folder will be created during the install. Once completed reboot the computer. Check the SIgma server is running and run up SIgma. Added 01-10-22014 17. The HTTP error can also caused if the computer name contains extended ASCII or Unicode. For example a computer named "Pást" may fail, if the computer name is changed to "Past" this may correct the HTTP problem. Added 23-11-2021 18. On SE laptops, the McAfee firewall has been updated: Go to McAfee (under hidden icons) > right click 'Quick Settings' > 'Enable Firewall Timed Groups'. This will provide a 1 hour window to run Sigma, in the McAfee pop up window. add a reason e.g. Sigma.
View full article
Picard Product_Support
‎2018-09-07 04:21 AM

Last Updated: Sisko DavidChild Sisko ‎2021-11-23 02:13 AM

Labels:
  • Satchwell BAS & Sigma
5500 Views

Controller is online but downloads to the SP-C are failing

Issue Downloads to the Controller are failing. When reviewing the Download Server Diagnostic Window, numerous Failed to load DAT file error messages are seen. Failed to load DAT file. Path='C:\ProgramData\Schneider Electric\SecurityExpert\Download\5.dat". Error code = 80070002 ***** Invalid Controller (5) version 0 Product Line EcoStruxure Security Expert Environment Security Expert SP-C Cause The Firmware version in the Controller is not compatible with the version of Security Expert being used. Resolution Upgrade the Firmware in the Controller to the latest Firmware build. From the main menu, select Sites | Controllers. Right click on a controller, and select Update Firmware. Click the [...] button and browse to the supplied firmware (.bin) file. Choose which controller(s) to update by selecting the Include option. Only the selected controller(s) will be updated. Click Update to commence the firmware update procedure. The update can take up to 10 minutes per controller to complete. Once complete, the controller is automatically restarted and normal operation resumed.
View full article
Picard Product_Support
‎2018-09-10 10:47 AM

Last Updated: Guinan AdamSteele Guinan ‎2022-02-02 09:47 PM

Labels:
  • EcoStruxure Security Expert
5542 Views

Error Codes: The Error Sys Var has been incremented or GLB_ELOG_DUP_START

Issue Error Codes: Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1631 E 04/05/2012 10:55:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000  Error Code Meaning: The Error Sys Var has been incremented Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1632 E 04/05/2012 10:57:30.00 0x00001c0b 0x04dd8500 0x02124e26 0x0000640b 0x00000000  Error Code Meaning: GLB_ELOG_DUP_START Product Line Andover Continuum Environment Continuum Site with BCX Controllers and an Error Log Cause Crash of BCX and log reveals: Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1629 E 04/05/2012 10:51:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000 Error Code Meaning: The Error Sys Var has been incremented Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1630 E 04/05/2012 10:53:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000  Error Code Meaning: The Error Sys Var has been incremented Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1631 E 04/05/2012 10:55:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000  Error Code Meaning: The Error Sys Var has been incremented Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1632 E 04/05/2012 10:57:30.00 0x00001c0b 0x04dd8500 0x02124e26 0x0000640b 0x00000000  Error Code Meaning: GLB_ELOG_DUP_START Resolution It is in the range of “Global System errors” that is usually not good, either faulty controller or need reloading of the O/S. Cold start and update O/S with the latest version supported by the Cyberstation version. Then run it on a test rig with different ID and see if it still crashes, if so will need to be repaired or replaced.
View full article
Picard Product_Support
‎2018-09-10 09:05 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:16 PM

Labels:
  • Andover Continuum
5539 Views

Configure Time Zone and UTC Offset settings so that time is synchronized across your system

Issue How to properly configure Time Zone and UTC Offset settings in Cyberstations and controllers. Product Line Andover Continuum Environment Continuum Cyberstation Continuum Controllers Cause There are a number of locations for time configuration settings, creating uncertainty as to what needs to be set, and where, to maintain the correct time in all devices. Resolution How to sync controller time with WS time with Server time. Set the correct UTC offset (time zone) in all of the below locations: Confirm Cyberstation(s) PC time zone (UTC offset) and regional settings are correct. [This has no effect on time synchronization but does have an effect on what time alarms and events are written to the database as well as when alarms will be delivered to Cyberstations] Confirm the SQL Server PC time zone (GMT settings) and regional settings are correct. [same as 1 above] In Continuum, the Workstations Device object's Time tab has the correct time zone setting (be aware this is in minutes, ex. GMT+10 = +600 minutes.) In Continuum, the Network folder has a setting for the time zone, this needs to be configured to the time zone the controllers are located. If GMT+10 then this gets set to +600. Note1: To synchronize controller time to Workstations time a program needs to be created in one WS that sets the Date object of the Netcontroller (IP level controller) with the lowest ACCnet ID. This controller will then push any time changes out to all other IP level controllers and down to its subnet controllers (i2’s or b3’s). See Time sync controllers to workstations for details on this. Note2: At 38 minutes past the hour the Netcontroller will push its time down to its subnet (aka Field Bus) controllers. Note3: When time is set in the Netcontroller with a reload of the controller, the UTC settings of the WS doing the reload, and the Network folder the controller is in, are accounted for and the controllers time is set with these UTC settings taken into account. When time is set with a PE program using the WS Date object, this does not take into account the UTC settings of the various locations and just sets the controller Date object to the exact value of the WS Date object. If the controller is in a different time zone than the WS setting its time, then it will now have the wrong time in it. To compensate for this, it is suggested that time offsets must be added to the Time Sync program to accommodate those networks in a different time zone than the WS. Other UTC setting locations and what these settings effect IP level BACnet Device UTC Offset The UTC offset value on the Time tab of the BACnet Device object is only used when the BACnet time synchronization method is being used to set time. This setting then follows the BACnet specification where it needs to be the negative value of the GMT setting. For example, if the BACnet device is in the GMT+10 time zone, then set this offset to -(10*60) = -600. Note4: If using the PE program method, the UTC offset value on the Time tab of the BACnet Device object does not change how time is set in the controllers. However, if the UTC offset value on the Time tab of the BACnet Device object is changed, it will change the current time of the controller to coincide with the new time zone until the time is set again in the controller, or the UTC offset value is removed. UTC offset in controller configuration Time Settings webpage This doesn’t change how the time of the controller is set. It is used to set the time of sent email messages when using the SMTP option on this controller.
View full article
Picard Product_Support
‎2018-09-11 12:00 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:55 PM

Labels:
  • Andover Continuum
5593 Views

Alarm delivery in StruxureWare: Sending Alarms to a Gmail recipient using the ES Email Notification.

Issue An Enterprise Server or Automation Server is unsuccessful at sending email notifications to a Gmail recipient.  Email messages from ES are marked as spam by Gmail SMTP service. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server (AS-P, AS-B or AS) Building Operation Workstation Gmail Cause Unable to successfully configure the ES to send an Alarm Notification to a Gmail recipient. Resolution The following describes how the ES can be set up to use Gmail for Email delivery. 1. Log into the ES; designate the Sender E-mail address and E-mail Host properties. 2. Create a notification on the ES; set the destination E-mail address and type of alarms to be included. 3. Log into destination E-mail account; notice there don’t appear to be any E-mails received. Select the “More” dropdown. 4. Select the “SPAM” folder. 5. Navigate to the E-mail Selection Tab and choose all E-mails from the correct sender. 6. Select the “Not Spam” button and from now on all email notifications will be sent to your inbox! 1. Log into the ES; designate the Sender E-mail address and E-mail Host properties. 2. Create a notification on the ES; set the destination E-mail address and type of alarms to be included. 3. Log into destination E-mail account; notice there don’t appear to be any E-mails received. Select the “More” dropdown. 4. Select the “SPAM” folder. 5. Navigate to the E-mail Selection Tab and choose all E-mails from the correct sender (SxW). 6. Select the “Not Spam” button and from now on all email notifications will be sent to your inbox!
View full article
Picard Product_Support
‎2018-09-10 10:29 PM

Labels:
  • EcoStruxure Building Operation
5555 Views

Web Service addition Script Web Service

Issue Web Service addition Script Web Service Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation site with release 1.2 or later Cause What are Web Services and how to add to my existing StruxureWare Building Operation site. How to add Script Web Service files and how to add to a project or site How to create values from Script Web Service Files How to add values to graphic that uses the values from Script Web Service Resolution Wikipedia: A Web Service is a method of communication between two electronic devices over the web (internet). W3C: A "Web Service" as "a software system designed to support interoperable machine-to-machine interaction over a network." Web Services: 1. are hardware, programming language, and operating system independent 2. Applications written in different programming languages and running on different platforms can seamlessly exchange data over intranet or the internet using Web Services 3. Web Service interfaces are supported in both the AS and ES 4. Like BACnet, Lon, and Modbus, you can create a Web Service interface.      EWS Interface - EcoStruxure Web Services      Script Web Service - Generic Consume via Script      Simple XML Web Service - Rest Generic Consume via Binding Tool (Web Service addition Simple XML Web Service)      SOAP Web Service - SOAP Generic Consume via Binding Tool (Web Service addition SOAP Web Service) This article explains adding Sunrise and Sunset for a particular location data using Script Web Service: -Select New...Interface...Web Service...Script Web Service This first example is for a Calculation program for Results=A+B -Enter the WSDL Service and Endpoint are auto-filled Not necessarily all the time IP Cameras -Script Web Services Interface: -Script Programs can bind to the web service with the "Webservice" declaration. -When the name bound service is typed and a "." is put after it, intellisense drop down will show the available methods WSDL file is brought into the database Drop down methods become available even if the URL of the WSDL is not -The web service capabilities can be used within the code for manipulation, data gathering, or whatever else. -Script Web Services Post and Gets -Script programs can send requests directly to a web service with the SendWebRequest keyword. -The syntax requires 5 specific arguments BaseURL - URL that will be processing the message Method - Method of processing the POST and GET (dictated by URL) Headers - Defines certain parameters that are meaningful to the URL (IsMobileApp:True;IsAndroidClient:True) Content-Type - Defined by the URL Message - What is actually being sent to the URL -Script Web Services - Considerations -Bindings to a web service require a recompile -Display of captured information will get localized   Next, Create a Script Program for Calculations Here is a simple script program which defines the calc and values The below shot is the values A=12, B=3, and the Results of the calculation. Below are the binding for the Script Calc program to the Values The below shot is the binding of the Calc program to the Script Web Service The results are a calculation in which we supply value A and B and the Script Web Service performs the calculation with results of 15.   We can change the value of A to from 12 to a value of 13 which Results in 16 as shown in the shot below.
View full article
Picard Product_Support
‎2018-09-10 01:41 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:39 PM

Labels:
  • EcoStruxure Building Operation
5540 Views

EBO Multi Trend Log Capture in XLSX/Excel format

Issue How to create a proper XLSX/Excel template under Alarm Triggered Notification of EcoStruxure Building Workstation, in order to receive the Multi trend logs report in the XLSX/Excel format. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Workstation Cause Additional information is needed to create a template for presenting multi-trend log information in Excel XLSX format.    Resolution Below screenshot shows where users can select the Report format and XLSX template.   The multi trend log containing four Interval Trend Logs 1 to 4 with their time stamp is shown as below as an example   In order to get the XLSX multi trend log report in XLSX/Excel format upon receiving a trigger, the following XLSX template needs to be used containing two rows: The first header row contains the column headers from the trend log. The second row include the <Multi Log List> command   Here is final report in Excel/XLSX format:  
View full article
Lt. Commander Reza Lt. Commander
‎2021-04-20 08:24 AM

on ‎2021-04-20 08:24 AM

Labels:
  • EcoStruxure Building Operation
5553 Views

Using EBO to replace a SIM-MTECH

Issue Existing SIM-MTECH communicates with a McQuay OPM (Open Protocol Master) and McQuay controllers under it. Can an AS-P replace the SIM-MTECH? Product Line TAC IA Series, EcoStruxure Building Operation Environment I/A Series NW8000 GCM/SIM-MTECH (McQuay OPM) Building Operation Automation Server Premium Cause Replacing obsolete NW8000 GCM/SIM-MTECH with currently supported EBO AS-P Resolution The GCM/SIM-MTECH data base can be converted as a normal GCM through the Transition Tool on the Schenider Electric Exchange TAC I/A Series Transition Portal.  The blocks specifically associated with the OPM integration will not be converted. A third-party hardware device can be used that will allow the AS-P to communicate through the OPM to the McQuay controllers. This will be accomplished by BACNet or Modbus protocol to the AS-P depending on the third parties device selected.  Refer to these 2 documents and websites.  NOTE: These are third party devices and have not been tested or approved by Schneider Electric Product Support. FS-8700-80 McQuay MicroTech Open Protocol Mcquay Gateways
View full article
Picard Product_Support
‎2018-09-10 01:31 AM

Last Updated: Sisko DavidChild Sisko ‎2021-11-26 07:03 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
5551 Views

Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node

Issue Using the Xenta 421A, 422A, 451A or 452A I/O modules as a stand alone Lonworks node and all values are reading the default 0. Product Line EcoStruxure Building Operation, Field Devices, TAC Vista Environment Xenta I/O Modules Xenta 400, 421A, 422A, 451A, 452A as stand alone LON nodes Cause The Xenta 421A and Xenta 451A as stand alone Lonworks node require the UCPTConfiguration to be set to the necessary integer value for the required input. Resolution Please see the supporting documentation for the TAC Xenta 421A/422A and TAC Xenta 451A/452A that gives each nci value for the needed input type. To configure each input to the correct type please follow these steps: Navigate to the node in your Lonworks network management software (Lonmaker, NL220, Tridium, Etc.) Browse / Edit the controller to view all of the inputs, outputs, and configuration properties. Find the Universal Input module for the input you need to configure, and locate the UCPTConfigInput variable within that module Set this UCPTConfigInput variable to one of the following: 1 = 1.8 kohm thermistor 2 = DI with green indication 3 = 0-10 vdc 4 = 0-20 mA 5 = 10 kohm thermistor 6 = DI with red indication 7 = DI with green inverted indication 8 = DI with red inverted indication NOTE: This is normally done in Menta when you are using these controllers as I/O modules to a Xenta 401, Xenta 301, Xenta 302 base unit.  The scan time of all inputs is (200ms * number of inputs used).  So if there are 3 inputs, the complete module will have been scanned every 600ms.
View full article
Picard Product_Support
‎2018-09-07 07:45 PM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
  • TAC Vista
5429 Views

Sigma - Remote Alarm Manager - Commonly used GSM modems.

Issue GSM modems that can be used with the Remote Alarm Manager. Product Line Satchwell BAS & Sigma,Satchwell MicroNet,TAC Vista Environment Remote Alarm Manager. BAS Sigma Micronet Vista  GSM RAM Siemens TC35i Siemens MC52i Multi-Tech MTCBA-G-F4-GB/IE Cinterion MTX-65+G-V53 Cause Not all GSM modems will allow the full functionality of message acceptance in the Remote Alarm Manager. Resolution The following GSM modems are known to provide the full message acceptance of the Remote Alarm Manager. Siemens TC35i GSM modem terminal. In the Remote Alarm Manager configuration select the C35i driver. This modem is now being replaced be the Cinterion (Siemens) MC52i GSM/GPRS Dual band modem terminal, which has not been tested, but appears to be a direct replacement with added functionality. TC35i GSM/GPRS modem terminal data sheet MC52i GSM/GPRS modem terminal data sheet Multi-Tech MultiModem MTCBA-G-F4-GB/IE modem terminal. In the Remote Alarm Manager configuration select the Brodersen UCM 91/92. This modem is still available, but seems expensive and difficult to source. MultiTech MultiModems MTCBA-G-F4 data sheet Cinterion MTX-65+G-V53 modem terminal.In the Remote Alarm Manager configuration, allow the software to locate the modem and use a generic driver. Cinterion MTX-65+G-V53 modem terminal data sheet   Remote Alarm Manger is no longer a support solution, it is recommended transitioning or upgrading to EcoStruxure Building Operation.
View full article
Picard Product_Support
‎2018-09-07 08:44 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 07:54 PM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
5415 Views

Maximum numbers (Scalability and Capacity) EcoStruxure Building Operation

Issue How many objects, users, devices, etc. per device with EcoStruxure Building Operation Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation WorkStation Building Operation WebStation Cause How many objects per device and what are the limits of EcoStruxure Building Operation? Resolution The primary source of these details should be the Architectural Guidelines on WebHelp Topic for the version being used
View full article
Picard Product_Support
‎2018-09-10 05:34 AM

Last Updated: Guinan RandyDavis Guinan ‎2025-01-23 01:03 PM

Labels:
  • EcoStruxure Building Operation
5446 Views

Niagara Station Error Transfer failed. com.tridium.platform.daemon.DaemonResponseException:

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue If the passphrase is incorrect when trying to install a station .bog, the following error message can appear; Transfer failed. com.tridium.platform.daemon.DaemonResponseException: Request to platform daemon at (stationName) failed: bad return code to commit file instance at com.tridium.platform.daemon.DaemonFileUtil.transfer(DaemonFileUtil.java:661) at com.tridium.install.InstallScenario.commit(InstallScenario.java:1444) at com.tridium.platDaemon.ui.stationtransfer.FinalStep.run(FinalStep.java:341) at java.lang.Thread.run(Thread.java:750) Product Line TAC IA Series Environment I/A Series N4 Enterprise Server I/A Series N4 Jace Cause The .bog has not been properly placed in the User Home / Stations for copying into the device or the passphrase is not known. Resolution Always use the Station Copier to install the .bog from the User Home / Stations path If the error message appears, open Workbench and navigate to the "Stations" folder under the "User Home" Expand the station you are attempting to install Double-click the .bog (1) and locate the "Bog File Protection" icon at the top of the page (2) Select the (1) "Force the File to start..." radio button and (2) Update.  Note the information regarding existing passwords. If the message "Cannot display page" occurs when you double click the .bog, open the "Details" and look for missing modules "Cannot load module '......=.....'. Any missing modules will need to be available on the Jace or ES before attempting the force start operation.  
View full article
Guinan RandyDavis Guinan
‎2023-03-14 01:09 PM

on ‎2023-03-14 01:09 PM

Labels:
  • TAC IA Series
5496 Views

Report can not be displayed - The request failed with HTTP status 503: Service Unavailable

Issue When trying to open a report, you get an error message like below: Msg=DDL creation failed ex=Error creating DropDownddlTopCount The request failed with HTTP status 503: Service Unavailable Ex=ButtonRunReport The request failed with HTTP status 503: Service Unavailable   Product Line EcoStruxure Building Operation Environment Reports server Cause Cause 1: The Report Server Service is not started To check if this is the cause, open the report manager. If you get the error below, continue to resolution 1.   Cause 2: The Report Server Service takes too long to generate the report and thus times out The root cause should also be investigated. It can be a slow network connection, fragmented SQL database, antivirus software or memory limitation that is slowing the request to compile a report down. Resolution Resolution 1 Open "Reporting Services Configuration Manager" Start the server   Resolution 2 Increase the timeout for the report service Open Report Manager Click "Site Settings" Change the Report Timeout. Default is 1800 which is 30 seconds.   Check that the memory usage for the SQL server is not limited (Microsoft's How to: Set a Fixed Amount of Memory (SQL Server Management Studio)) Open SQL Management Studio Open the properties for the SQL Server Click "Memory" and check that the value is default (2147483647)   Reindex and defragment the SQL database e.g. using SBO Reports Agent Config.
View full article
Picard Product_Support
‎2018-09-11 03:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:57 AM

Labels:
  • EcoStruxure Building Operation
5484 Views

How to set and relinquish a BACnet point from AS Script programming

Issue How to turn on and release a specific command priority on a BACnet point? Product Line EcoStruxure Building Operation Environment ES AS Bacnet interface Script programming Cause Wants an example script program to turn on/ off specific BACnet command priorities in a BACnet device. Resolution To control a specific Digital or Analog Output in a BACnet device, from a script program you would use a Numeric Output in the program that has its value set as required by the program. This Output from the program is then bound to the specific command priority attribute of the point to be controlled. To release control from that Command Priority the "Relinquish" keyword is used in the program to Null that specific command priority and allow lower commands to take control of the output.   Here is an example AS test program that turns on a Digital Output for 4 seconds and then releases it for 4 seconds. The Numeric Output DOControl should be bound to the required Output Command Priority 2, it is written as a fallthru program. Notice; the Relinquish command is releasing the output from Command Priority 2 as used in this example.   Numeric Output DOControl DOOnLine: DOControl = Active Wait4: If TS > 4 Then goto DOOffline Else goto Wait4 DOOffline: Relinquish(DOControl,2) Wait4More: If TS > 4 Then goto DOOnline Else goto Wait4More   This type of script program can be located in the Application of the BACnet interface and control outputs on 3rd party BACnet products or b3 controllers. Note: For control of b3 outputs it is often better to put an appropriate control program (Not the above code) within the b3 controller itself, making it more robust in case of comms failure and also reducing communications traffic. Also check out the Convert Continuum Plain English into SBO Script Quick-Help video on the Exchange.
View full article
Picard Product_Support
‎2018-09-06 09:24 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:51 AM

Labels:
  • EcoStruxure Building Operation
5406 Views

Logging into CX9900 controller using HyperTerminal

Issue How to log on to CX9900 controller for commissioning or configuring IP settings. Product Line Andover Continuum Environment HyperTerminal CX9900 CX9940 CX9200 CX9400 Cause First generation Continuum controllers do not support web page configuration and must be configured using a terminal emulation program such as HyperTerminal. Resolution Configure HyperTerminal for 9600 baud (or baud that matches default baud configuration for the comm port), 8 data bits, no parity, no flow control. Connect cable to comm3 (or another port configured for autoset) on controller (for information on cable pinout please see PinOuts for the RS-232 Connection of the older 1st Generation CX controllers) On the NetController make sure RS232 is selected, use the MODEM/RS232 override switch to de-select the modem if necessary. Run HyperTerminal and type "window" to have the controller display the log on window Default user/password is acc/acc
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:04 PM

Labels:
  • Andover Continuum
5467 Views

Replacement of Satchwell ZKM series Rotary Actuator due to obsolescence.

Issue Satchwell ZKM series Rotary Actuator requires replacement due to obsolescence. Environment Satchwell ZKM Rotary Actuator installed on Satchwell MBF series Rotary Shoe Valve Body. Satchwell ZKM Rotary Actuator installed on Satchwell MZF series Plug and Seat Valve Body. Cause Obsolescence of Satchwell ZKM series Rotary Actuator Resolution OVERVIEW The Satchwell ZKM Actuator was compatible with both Satchwell MBF series Flanged Rotary Shoe Valve Bodies and Satchwell MZF series Flanged Plug and Seat Valve Bodies, subject to the installation of an appropriate Linkage Kit. Various models of the ZKM Actuator were available, each differing in the number and type of electrical interface provided, enabling the Actuator to be installed in a range of control applications. Interfaces included Transfer Switches, Auxiliary Switches and Feedback Potentiometers, thus resulting in differing wiring connection options between the ZKM Actuator and its associated Controller and other peripherals. Details of the numerous ZKM Actuator variations available may be viewed here. In view of the differing wiring connection options that may be found on site, it is intended to deal only with the most common 6-wire connection option here. Please therefore check the number of wires connected to the ZKM Actuator before proceeding, as this will assist in confirming the suitability of the ZKM Actuator 6-wire connection option replacement suggestion described here.   1. ACTUATOR REPLACEMENT The Actuator comprising a 6 wire electrical connection enabled it to be operated from a Satchwell Z Monotronic or CZT Climatronic Proportional Controller as follows :- Terminal 1 – Open signal Terminal 2 – Close signal Terminal 3 – Common Terminal A – 135 ohm Feedback Potentiometer – winding Terminal B – 135 ohm Feedback Potentiometer – wiper Terminal C – 135 ohm Feedback Potentiometer – winding If all 6 wires are connected then the ZKM Actuator may be replaced either by the Schneider Electric MD20A Actuator or the M800 Actuator, depending on the type of Valve Body to be controlled :- MBF ROTARY SHOE VALVE BODY APPLICATIONS :- MD20A-24 + Linkage Kit LMD-MBF (914-1070-000) Details of the MD20A Actuator may be viewed here Details of the LMD-MBF Linkage Kit may be viewed here N.B. Should the Satchwell ZKM series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E MD20A Actuator as appropriate :- MD-S2 - Two independent SPDT 1mA -- 3(0.5)A, 250 V AC Auxiliary Switches. (914-1061-000) Should the Satchwell ZKM series Actuator include a wired Transfer Switch then the following Accessory should also be installed on the S-E MD20A Actuator as appropriate :- MD-S2 - Two independent SPDT 1mA -- 3(0.5)A, 250 V AC Auxiliary Switches. (914-1061-000) Details of the MD-S2 Auxiliary Switch Kit may be viewed here MZF PLUG AND SEAT VALVE BODY APPLICATIONS :- M800 + Linkage Kit L2SV (880-0124-000) Details of the M800 Actuator may be viewed here Details of the L2SV Linkage Kit may be viewed here N.B. Should the Satchwell ZKM series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :- S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000) Should the Satchwell ZKM series Actuator include a wired Transfer Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :- S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000) Particular care should be taken when selecting an S-E Forta M800 Actuator to replace an existing Satchwell ZKM series Actuator. The S-E Forta M800 Actuator may be used to replace an existing Satchwell ZKM series Actuator but it should be noted that where this is to be connected directly to a Satchwell Controller, an independent Transformer rated to provide the greater level of power required by a single S-E Forta M800 Actuator (50VA) compared to that available at the CZT Controller (10VA) will also be required. (e.g. S-E Transformer Type TR60) Details of the Schneider Electric TR60 Transformer may be viewed here In such installations not only will the ZKM need to be replaced but the associated Proportional Controller will also need to be replaced.   2. PROPORTIONAL CONTROLLER REPLACEMENT The ZKM Actuator was compatible with a number of Satchwell Proportional Controller types including Z Monotronic, CZT Series 1 and CZT Series 3 Z MONTRONIC CONTROLLER APPLICATIONS :- If the Proportional Controller is a Z Monotronic type then this should be replaced by the Satchwell CZT5305 Proportional Controller. The associated Satchwell 3 wire Sensor will also need to be replaced by a S-E 2 wire Sensor compatible with the CZT5305 Details of a compatible Room Temperature Sensor may be viewed here. Details of a compatible Duct Temperature Sensor may be viewed here. Details of a compatible Immersion Temperature Sensor may be viewed here. The replacement Immersion Temperature Sensor may be installed in the existing Immersion Temperature Sensor Pocket with the aid of an Adaptor DWA0001. Details of the DWA0001 Adaptor may be viewed here. Details of the CZT5305 may be viewed here.   CZT CONTROLLER APPLICATIONS :- If the Proportional Controller is a CZT Series 1 or CZT Series 3 type then this should be replaced by the Satchwell CZT5305 Proportional Controller. The associated Satchwell 2 wire Sensor may be retained if desired. Details of the CZT5305 may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 01:48 AM

Labels:
  • Field Devices
5401 Views

How to create a custom lon shadow object in a Niagara G3 station using the Lon Xml Tool.

Issue Working with a 3rd-party lon controller with no existing shadow object available.  Niagara G3 provides the ability to create a shadow object on the jobsite using the Lon Xml Tool. Environment Niagara G3 Cause A shadow object is not available for a specific 3rd-party controller and a dynamic device fails to interface properly.  Resolution The Lon Xml Tool provides the ability to create a Lon Xml file (.lnml) file for a device, using the source .xif file and (if necessary) other resource files, as made available from the device's manufacturer.  Review Appendix A of the Lonworks Integration Guide for Niagara G3.  The Lon Xml Tool is described starting on page A-1.  This section describes the need for custom Lon Xml files as well as an overview of the process and the steps to create one. docLonworks.pdf
View full article
Picard Product_Support
‎2018-09-10 04:54 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:01 AM

Labels:
  • TAC IA Series
5412 Views

"Communication Failed" Alarm occurs when Adding an Automation Server

Issue "Communication Failed" Alarm occurs when Adding an AS. Source: /Server 1/Servers/ASL/System/Server Communications/Models/2deef04c-05d1-41ae-9c3f-f84a9f7e0b41 Alarm "cannot verify lead object" appears even though AS is online. Product Line EcoStruxure Building Operation Environment StruxureWare Alarm Queue Cause The AS is unable to communicate with the ES. The ES may be able to communicate with the AS allowing the user to view and control the AS, but Value Binds will not work. This type of error can also occur as a result of multiple networks being accessed by the same PC.  It is important that if you are using multiple networks that the ES be configured with the IP address for the correct network. Resolution Ensure that no Firewalls are blocking configured ES and AS ports Ensure all devices are on the same Windows Domain In workstation, select the Enterprise server's Communication Tab and verify that the IP address listed for the ES matches the ES PC IP address. Right click on the ES and select Advanced > Repair Server Communication For more information see Creating Windows Firewall rules to allow StruxureWare Building Operation to communicate on the TCP port
View full article
Picard Product_Support
‎2018-09-10 12:54 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:43 AM

Labels:
  • EcoStruxure Building Operation
5449 Views

BACnet Object binding options using priorities

Issue How to bind BACnet Objects with Priority Levels Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation BACnet MPX, RPC, MPC Cause Servers (ES, AS) and other native devices (MPX, RPC) have slightly differing binding options. EcoStruxure Building Operation BACnet binding offers many options and the information below gives an example of how it can be achieved, it is not the only method. Resolution When binding between BACnet objects in EcoStruxure Building Operation (either external or within the device) it is usually better to utilize the BACnet Priority based control, often this facility is not fully exploited. Object Force and Overrides will use set priorities as in the BACnet Interface setting for the site (see System/Interface Manager/BACnet), the defaults are below. The example below shows a simple bind from a BACnet Schedule-value to a BACnet Binary-value Priority 16 (or other priority as required, as binding at Priority 16 can interfere with simple manual overrides). A BACnet datetime_value has no Priority array, so if you bind, for example, from a "BACnet Schedule Next transition" to "BACnet datetime_value Value" the bind to a Priority cannot be achieved, as below. In addition, the MPX & RPC have some constraints that Servers do not have. If you bind "Transfer Value to" an Object Value Property (rather than a Priority) then further bindings "Transfer Value to" binding to a Priority is inhibited. The screenshot below shows the error that is seen. This promotes using Priorities to control BACnet Objects.
View full article
Dave_Shore Schneider Alumni (Retired)
‎2019-04-04 06:53 AM

on ‎2019-04-04 06:53 AM

Labels:
  • EcoStruxure Building Operation
5563 Views
  • « Previous
    • 1
    • …
    • 16
    • 17
    • 18
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of