Replacement of Satchwell ZKM series Rotary Actuator due to obsolescence.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacement of Satchwell ZKM series Rotary Actuator due to obsolescence.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7220 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacement of Satchwell ZKM series Rotary Actuator due to obsolescence.

Picard Product_Support
‎2018-09-10 01:48 AM

Issue

Satchwell ZKM series Rotary Actuator requires replacement due to obsolescence.

Environment

  • Satchwell ZKM Rotary Actuator installed on Satchwell MBF series Rotary Shoe Valve Body.
  • Satchwell ZKM Rotary Actuator installed on Satchwell MZF series Plug and Seat Valve Body.

Cause

Obsolescence of Satchwell ZKM series Rotary Actuator

Resolution

OVERVIEW

The Satchwell ZKM Actuator was compatible with both Satchwell MBF series Flanged Rotary Shoe Valve Bodies and Satchwell MZF series Flanged Plug and Seat Valve Bodies, subject to the installation of an appropriate Linkage Kit.

Various models of the ZKM Actuator were available, each differing in the number and type of electrical interface provided, enabling the Actuator to be installed in a range of control applications.

Interfaces included Transfer Switches, Auxiliary Switches and Feedback Potentiometers, thus resulting in differing wiring connection options between the ZKM Actuator and its associated Controller and other peripherals.

Details of the numerous ZKM Actuator variations available may be viewed here.

In view of the differing wiring connection options that may be found on site, it is intended to deal only with the most common 6-wire connection option here.

Please therefore check the number of wires connected to the ZKM Actuator before proceeding, as this will assist in confirming the suitability of the ZKM Actuator 6-wire connection option replacement suggestion described here.

 

1. ACTUATOR REPLACEMENT

The Actuator comprising a 6 wire electrical connection enabled it to be operated from a Satchwell Z Monotronic or CZT Climatronic Proportional Controller as follows :-

Terminal 1 – Open signal

Terminal 2 – Close signal

Terminal 3 – Common

Terminal A – 135 ohm Feedback Potentiometer – winding

Terminal B – 135 ohm Feedback Potentiometer – wiper

Terminal C – 135 ohm Feedback Potentiometer – winding

If all 6 wires are connected then the ZKM Actuator may be replaced either by the Schneider Electric MD20A Actuator or the M800 Actuator, depending on the type of Valve Body to be controlled :-

MBF ROTARY SHOE VALVE BODY APPLICATIONS :-

MD20A-24 + Linkage Kit LMD-MBF (914-1070-000)

Details of the MD20A Actuator may be viewed here

Details of the LMD-MBF Linkage Kit may be viewed here

N.B.

Should the Satchwell ZKM series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E MD20A Actuator as appropriate :-

MD-S2 - Two independent SPDT 1mA -- 3(0.5)A, 250 V AC Auxiliary Switches. (914-1061-000)

Should the Satchwell ZKM series Actuator include a wired Transfer Switch then the following Accessory should also be installed on the S-E MD20A Actuator as appropriate :-

MD-S2 - Two independent SPDT 1mA -- 3(0.5)A, 250 V AC Auxiliary Switches. (914-1061-000)

Details of the MD-S2 Auxiliary Switch Kit may be viewed here

MZF PLUG AND SEAT VALVE BODY APPLICATIONS :-

M800 + Linkage Kit L2SV (880-0124-000)

Details of the M800 Actuator may be viewed here

Details of the L2SV Linkage Kit may be viewed here

N.B.

Should the Satchwell ZKM series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :-

S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000)

Should the Satchwell ZKM series Actuator include a wired Transfer Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :-

S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000)

Particular care should be taken when selecting an S-E Forta M800 Actuator to replace an existing Satchwell ZKM series Actuator.

The S-E Forta M800 Actuator may be used to replace an existing Satchwell ZKM series Actuator but it should be noted that where this is to be connected directly to a Satchwell Controller, an independent Transformer rated to provide the greater level of power required by a single S-E Forta M800 Actuator (50VA) compared to that available at the CZT Controller (10VA) will also be required. (e.g. S-E Transformer Type TR60)

Details of the Schneider Electric TR60 Transformer may be viewed here

In such installations not only will the ZKM need to be replaced but the associated Proportional Controller will also need to be replaced.

 

2. PROPORTIONAL CONTROLLER REPLACEMENT

The ZKM Actuator was compatible with a number of Satchwell Proportional Controller types including Z Monotronic, CZT Series 1 and CZT Series 3

Z MONTRONIC CONTROLLER APPLICATIONS :-

If the Proportional Controller is a Z Monotronic type then this should be replaced by the Satchwell CZT5305 Proportional Controller.

The associated Satchwell 3 wire Sensor will also need to be replaced by a S-E 2 wire Sensor compatible with the CZT5305

Details of a compatible Room Temperature Sensor may be viewed here.

Details of a compatible Duct Temperature Sensor may be viewed here.

Details of a compatible Immersion Temperature Sensor may be viewed here.

The replacement Immersion Temperature Sensor may be installed in the existing Immersion Temperature Sensor Pocket with the aid of an Adaptor DWA0001.

Details of the DWA0001 Adaptor may be viewed here.

Details of the CZT5305 may be viewed here.

 

CZT CONTROLLER APPLICATIONS :-

If the Proportional Controller is a CZT Series 1 or CZT Series 3 type then this should be replaced by the Satchwell CZT5305 Proportional Controller.

The associated Satchwell 2 wire Sensor may be retained if desired.

Details of the CZT5305 may be viewed here.

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (1)
  • Find more articles tagged with:
  • 6124
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore