Issue
How to log on to CX9900 controller for commissioning or configuring IP settings.
Product Line
Andover Continuum
Environment
- HyperTerminal
- CX9900
- CX9940
- CX9200
- CX9400
Cause
First generation Continuum controllers do not support web page configuration and must be configured using a terminal emulation program such as HyperTerminal.
Resolution
- Configure HyperTerminal for 9600 baud (or baud that matches default baud configuration for the comm port), 8 data bits, no parity, no flow control.
- Connect cable to comm3 (or another port configured for autoset) on controller
(for information on cable pinout please see PinOuts for the RS-232 Connection of the older 1st Generation CX controllers) - On the NetController make sure RS232 is selected, use the MODEM/RS232 override switch to de-select the modem if necessary.
- Run HyperTerminal and type "window" to have the controller display the log on window
- Default user/password is acc/acc