Sigma Client reports a "HTTP connection failed" error".

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma Client reports a "HTTP connection failed" error".
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • DavidFisher
    DavidFisher
  • Gary
    Gary
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5299 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma Client reports a "HTTP connection failed" error".

Picard Product_Support
‎2018-09-07 04:21 AM

Last Updated: Sisko DavidChild Sisko ‎2021-11-23 02:13 AM

Issue

The Sigma Client reports a "HTTP connection failed" error" when an attempt is made to start it.

Product Line

Satchwell Sigma

Environment

Satchwell Sigma release 4.05 and later

Cause

When the Sigma Client is started, attempts are made to make a connection to the Sigma Server, this connection fails and the Client cannot be started.

Resolution

There are a number of reasons why this error might occur, suggestions are listed below.

1.  Windows XP operating system - ensure that service pack 3 has been installed, and that all the Windows updates have been applied.

2. Windows 7 operating system - only Ultimate and Professional are supported.

3. Sigma Client/Server software must be installed by a Windows user with "Admin" privileges.

4. Windows Firewall must either have been switched off, or has "Exceptions" configured as explained in the Sigma 4.05 SP1 release note.

5. Check that the "SigmaSVR" service has been started. If this service cannot be seen, then this is an indication that the Sigma software has not been install by an "Admin" user, and the software must be reinstalled.

6. Corruption of the Windows "User" files has taken place. Create a new Windows user with "Admin" privileges. Log on to Windows as the new user and test the Sigma Client again.

7. If using a VMware image try rebooting the image.

8. SMART is being used and has a modem connected to the PC for uploading data. Ensure that the modem is fully functional. If not, the HTTP error can be caused. This was seen at Sigma: R4   Release 3.44.14. and Smart Task Manager  3.0.2.20.

Added 26-07-2012

9. This may be because a proxy server is being used, eg on school networks. Log on to your PC computer with an administrator account. Open the "Start" menu and click on "Control Panel." Double-click on the icon labeled "Internet Options." Go to the "Connections" tab at the top of the window and then click on "LAN Settings." Make sure the box next to "Bypass proxy server for local addresses" is checked. Hit "OK" twice to confirm the new proxy port settings.


Make sure the box next to "Bypass proxy server for local addresses" is checked.
Hit "OK" twice to confirm the new proxy port settings.

Added 25-09-2012.

10. This issue was reported from a School where Sigma 4.05 SP1 had been operating correctly for several weeks. The issue was traced to the Anti-virus software Sophos, which had received an update prior to the failure. Sophos had quarantined two Sigma dll files. To correct this issue both Sophos and Sigma were uninstalled. A later version of Sophos was installed, and then Sigma was reinstalled, this corrected the problem.

Added 01-08-2013

11 - Sigma software installed when connected to a wireless network.

The Sigma client will only connect to the server when the wireless connection is made. Uninstall Sigma, disable the wireless, enable the network card, and then reinstall the Sigma software.

Added 03-10-2013

12. DELL PC, with firewalls and antivirus disabled and no wireless card fitted. There may be a service or an application running in the background as part of the vendors Windows platform makeup.Restore the same version of Windows, but without (where possible) any of the Vendors applications. Re-install Sigma.

Added 16-05-2014

13. Check the port number in c:\sigma\bin\setupsvr.exe, the default is 8080.

Added 19-05-2014

14. Flexera license software has been reported as a cause for receiving this error. Flexera license software uses port 8080, (IMADMIN.EXE). Stop Flexera and retry Sigma. Changing Sigma from port 8080 to 8081 could also provide a solution.

Added 27-08-2014

15. The SBO PCS (StruxureWare Building Operation Project Configuration Server) also uses port 8080.This needs to be stopped or will conflict with Sigma and produce the HTTP error.

Added 02-09-2014

16. Make sure any data is backed up from the installed Sigma system.
Uninstall Sigma using Add/remove programs (Win XP) or Programs and features (Win 7).
Wait for the Sigma un-install process has completely finish.
Delete or rename the C:\Sigma folder to.......for example Sigma1.
Re-install Sigma by using a right mouse click on the "SigmaSetup.exe" file and select 
A new clean Sigma folder will be created during the install.
Once completed reboot the computer.
Check the SIgma server is running and run up SIgma.

Added 01-10-22014

17. The HTTP error can also caused if the computer name contains extended ASCII or Unicode. For example a computer named "Pást" may fail, if the computer name is changed to "Past" this may correct the HTTP problem.

Added 23-11-2021

18. On SE laptops, the McAfee firewall has been updated:

Go to McAfee (under hidden icons) > right click 'Quick Settings' > 'Enable Firewall Timed Groups'.

This will provide a 1 hour window to run Sigma, in the McAfee pop up window. add a reason e.g. Sigma.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (4)
  • Find more articles tagged with:
  • 4400
  • DavidChild19
  • DavidChild21
  • GaryMontague22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of