Convert Trane BCU (BMTW or BMTX) from BACnet/Ethernet to BACnet/IP for integrating to a Niagara R2 UNC
  • Convert Trane BCU (BMTW or BMTX) from BACnet/Ethernet to BACnet/IP for integrating to a Niagara R2 UNC
‎2018-09-07 12:45 AM
Last Updated: Administrator DavidFisher Administrator ‎2020-10-26 06:13 AM
Is there a way to convert a Trane BCU (BMTW or BMTX) from BACnet/Ethernet to BACnet/IP for integrating to a Niagara R2 UNC?
TAC IA Series
  • Trane BCU (BMTW or BMTX)
  • Niagara R2 UNC
There are two components required to change over the BCU from BACnet/Ethernet to BACnet/IP.
  1. A special serial cable is required to download the BCU with the new configuration. Below are the pin outs to make the cable:
  2. Access to the Tracer Summit software.
Here are the steps for running the BCUconfig.exe program to change over the BCU from Ethernet to IP:
  1. Open Windows Explorer and navigate to C:\Program Files\Tracer Summit\Bin
  2. Double-click on BCUconfig.exe
  3. Enter the information and select download.
    Note - This is where you must have the Trane serial cable.
    The BCU will reset.
  4. Now change the Connection type in the Tracer Summit software to IP connection:
    1. Open the Tracer Summit software and select Connect.
    2. The Site connection Wizard will appear. Select the BACnet/IP radio button.
    3. From the Ethernet Configuration window, select the 'open on startup' check box.
    4. Select the 'Use BBMD connection' from the BACnet/IP configuration window.
    5. Specify the IP address of the BBMD BCU and the UDP port which is the BACnet port.
    6. Select Finish.