Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6645 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node

Picard Product_Support
‎2018-09-07 07:45 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:36 AM

Issue

Using the Xenta 421A, 422A, 451A or 452A I/O modules as a stand alone Lonworks node and all values are reading the default 0.

Product Line

EcoStruxure Building Operation, Field Devices, TAC Vista

Environment

  • Xenta I/O Modules
  • Xenta 400, 421A, 422A, 451A, 452A as stand alone LON nodes

Cause

The Xenta 421A and Xenta 451A as stand alone Lonworks node require the UCPTConfiguration to be set to the necessary integer value for the required input.

Resolution

Please see the supporting documentation for the TAC Xenta 421A/422A and TAC Xenta 451A/452A that gives each nci value for the needed input type.

To configure each input to the correct type please follow these steps:

  1. Navigate to the node in your Lonworks network management software (Lonmaker, NL220, Tridium, Etc.)
  2. Browse / Edit the controller to view all of the inputs, outputs, and configuration properties.
  3. Find the Universal Input module for the input you need to configure, and locate the UCPTConfigInput variable within that module
  4. Set this UCPTConfigInput variable to one of the following:
    1 = 1.8 kohm thermistor
    2 = DI with green indication
    3 = 0-10 vdc
    4 = 0-20 mA
    5 = 10 kohm thermistor
    6 = DI with red indication
    7 = DI with green inverted indication
    8 = DI with red inverted indication

NOTE: This is normally done in Menta when you are using these controllers as I/O modules to a Xenta 401, Xenta 301, Xenta 302 base unit.  The scan time of all inputs is (200ms * number of inputs used).  So if there are 3 inputs, the complete module will have been scanned every 600ms.

Labels (3)
Labels:
  • EcoStruxure Building Operation
  • Field Devices
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4350
  • PeterLarsen21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore