Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Error Codes: The Error Sys Var has been incremented or GLB_ELOG_DUP_START

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error Codes: The Error Sys Var has been incremented or GLB_ELOG_DUP_START
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa139513
    sesa139513
  • CraigEl
    CraigEl
  • JohnBoehmer
    JohnBoehmer

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
7648 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error Codes: The Error Sys Var has been incremented or GLB_ELOG_DUP_START

Picard Product_Support
‎2018-09-10 09:05 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:16 PM

Issue

Error Codes:

Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2
1631 E 04/05/2012 10:55:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000

 Error Code Meaning: The Error Sys Var has been incremented

Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2
1632 E 04/05/2012 10:57:30.00 0x00001c0b 0x04dd8500 0x02124e26 0x0000640b 0x00000000

 Error Code Meaning: GLB_ELOG_DUP_START

Product Line

Andover Continuum

Environment

Continuum Site with BCX Controllers and an Error Log

Cause

Crash of BCX and log reveals:

Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2
1629 E 04/05/2012 10:51:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000

Error Code Meaning: The Error Sys Var has been incremented

Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2
1630 E 04/05/2012 10:53:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000

 Error Code Meaning: The Error Sys Var has been incremented

Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2
1631 E 04/05/2012 10:55:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000

 Error Code Meaning: The Error Sys Var has been incremented

Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2
1632 E 04/05/2012 10:57:30.00 0x00001c0b 0x04dd8500 0x02124e26 0x0000640b 0x00000000

 Error Code Meaning: GLB_ELOG_DUP_START

Resolution

It is in the range of “Global System errors” that is usually not good, either faulty controller or need reloading of the O/S. Cold start and update O/S with the latest version supported by the Cyberstation version. Then run it on a test rig with different ID and see if it still crashes, if so will need to be repaired or replaced.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 7800
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore