Issue
Existing SIM-MTECH communicates with a McQuay OPM (Open Protocol Master) and McQuay controllers under it. Can an AS-P replace the SIM-MTECH?
Product Line
TAC IA Series, EcoStruxure Building Operation
Environment
- I/A Series NW8000 GCM/SIM-MTECH (McQuay OPM)
- Building Operation Automation Server Premium
Cause
Replacing obsolete NW8000 GCM/SIM-MTECH with currently supported EBO AS-P
Resolution
The GCM/SIM-MTECH data base can be converted as a normal GCM through the Transition Tool on the Schenider Electric Exchange TAC I/A Series Transition Portal. The blocks specifically associated with the OPM integration will not be converted. A third-party hardware device can be used that will allow the AS-P to communicate through the OPM to the McQuay controllers. This will be accomplished by BACNet or Modbus protocol to the AS-P depending on the third parties device selected. Refer to these 2 documents and websites. NOTE: These are third party devices and have not been tested or approved by Schneider Electric Product Support.