How to set and relinquish a BACnet point from AS Script programming

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to set and relinquish a BACnet point from AS Script programming
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
5372 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to set and relinquish a BACnet point from AS Script programming

Picard Product_Support
‎2018-09-06 09:24 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:51 AM

Issue

How to turn on and release a specific command priority on a BACnet point?

Product Line

EcoStruxure Building Operation

Environment

  • ES AS Bacnet interface
  • Script programming

Cause

Wants an example script program to turn on/ off specific BACnet command priorities in a BACnet device.

Resolution

To control a specific Digital or Analog Output in a BACnet device, from a script program you would use a Numeric Output in the program that has its value set as required by the program.

This Output from the program is then bound to the specific command priority attribute of the point to be controlled.

To release control from that Command Priority the "Relinquish" keyword is used in the program to Null that specific command priority and allow lower commands to take control of the output.

 

Here is an example AS test program that turns on a Digital Output for 4 seconds and then releases it for 4 seconds.

The Numeric Output DOControl should be bound to the required Output Command Priority 2, it is written as a fallthru program.

Notice; the Relinquish command is releasing the output from Command Priority 2 as used in this example.

 

Numeric Output DOControl

DOOnLine:
DOControl = Active

Wait4:
If TS > 4 Then goto DOOffline Else goto Wait4

DOOffline:
Relinquish(DOControl,2)

Wait4More:
If TS > 4 Then goto DOOnline Else goto Wait4More

 

This type of script program can be located in the Application of the BACnet interface and control outputs on 3rd party BACnet products or b3 controllers.

Note: For control of b3 outputs it is often better to put an appropriate control program (Not the above code) within the b3 controller itself, making it more robust in case of comms failure and also reducing communications traffic.

Also check out the Convert Continuum Plain English into SBO Script Quick-Help video on the Exchange.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 17202
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of