Report can not be displayed - The request failed with HTTP status 503: Service Unavailable
Select a Country
  • Report can not be displayed - The request failed with HTTP status 503: Service Unavailable
  • CraigEl
    CraigEl
  • Benji
    Benji
  • sesa177673
    sesa177673
‎2018-09-11 03:45 AM
Last Updated: CraigEl Champion ‎2022-08-08 03:57 AM
When trying to open a report, you get an error message like below:
Msg=DDL creation failed ex=Error creating DropDownddlTopCount The request failed with HTTP status 503: Service Unavailable
Ex=ButtonRunReport The request failed with HTTP status 503: Service Unavailable
Reports server
Cause 1: The Report Server Service is not started
To check if this is the cause, open the report manager. If you get the error below, continue to resolution 1.
Cause 2: The Report Server Service takes too long to generate the report and thus times out
The root cause should also be investigated. It can be a slow network connection, fragmented SQL database, antivirus software or memory limitation that is slowing the request to compile a report down.
Resolution 1
  1. Open "Reporting Services Configuration Manager"
  2. Start the server
Resolution 2
Increase the timeout for the report service
  1. Open Report Manager
  2. Click "Site Settings"
  3. Change the Report Timeout. Default is 1800 which is 30 seconds.
Check that the memory usage for the SQL server is not limited (Microsoft's How to: Set a Fixed Amount of Memory (SQL Server Management Studio))
  1. Open SQL Management Studio
  2. Open the properties for the SQL Server
  3. Click "Memory" and check that the value is default (2147483647)
Reindex and defragment the SQL database e.g. using SBO Reports Agent Config.
Tags (3)
  • 13070
  • found
  • object
100% helpful (1/1)