Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Changing the default port numbers for the Fox, Platform Daemon and HTTP ports in I/A Series G3

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Changing the default port numbers for the Fox, Platform Daemon and HTTP ports in I/A Series G3
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RyanSuar
    RyanSuar
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5239 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Changing the default port numbers for the Fox, Platform Daemon and HTTP ports in I/A Series G3

Picard Product_Support
‎2018-09-06 12:35 PM

Issue

Changing the default port numbers for the Fox, Platform Daemon and HTTP ports in I/A Series G3

Product Line

TAC IA Series

Environment

I/A Series G3 Enterprise Network Server / Enterprise Network Controller

Cause

There is a need to change the default port numbers of the Fox, Platform and HTTP ports used in I/A Series G3.

Below are the descriptions of the ports usage and their default port numbers:

  • TCP port 1911 (Fox port)
    Default port for a station's Fox Service used for Workbench to station and station to station communications
  • TCP port 80 (HTTP port)
    Default port for a station's Web Service used in browser access (Hx, Wb)
  • TCP port 80, 3011 (HTTP and Platform Daemon ports)
    Default ports for Workbench Platform connection

Resolution

The default ports for the Fox and HTTP ports can be changed during the process of creating a new station. Follow the following procedures if the ports need to be changed after the station has been created.

To change the Fox port:

  1. In Workbench, open the station.
  2. Expand 'Config' > 'Drivers'.
  3. Open the Property Sheet of the NiagaraNetwork.
  4. Expand the 'Fox Service' and you can change the port number from the default of 1911.

To change the HTTP:

  1. In Workbench, open the station.
  2. Expand 'Config' > 'Services'.
  3. Open the Property Sheet of the WebService and you can change the Http Port number from the default of 80.

To change the Platform Daemon port:

  1. In Workbench, open the host's Platform.
  2. In the Platform view, go to the Platform Administration.
  3. In the Platform Administration view, click on the 'Change HTTP Port' button to change the default port.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7465
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of