Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Discovering and Learning b3 bacnet devices in EcoStruxure Building Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Discovering and Learning b3 bacnet devices in EcoStruxure Building Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5791 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Discovering and Learning b3 bacnet devices in EcoStruxure Building Operation

Picard Product_Support
‎2018-09-11 10:11 AM

Issue

How to add b3 devices to EcoStruxure.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation
  • b3
  • BACnet

Cause

List the methods of adding b3 devices to EcoStruxure Building Operation

Resolution

The following information can be found in the EcoStruxure Building Operation - Technical Reference Guide. Use the guide relevant to the release of EBO installed.

 

Discovering b3 BACnet Devices with the Device Discovery View

Using the Device Discovery view to search deployed Automation Servers for b3 BACnet devices. For more information, see section "b3 BACnet Device Overview".

To discover b3 BACnet devices with the Device Discovery view

  1. In WorkStation, click the Device Discovery view.
  2. In the System Tree pane, click the Automation Server to be searched.
  3. In Select device type, click on BACnet devices.
  4. Select the b3 BACnet device you want in the Device result pane.
  5. Map a device by dragging that device from the Device result area and dropping it in the System Tree pane.
  6. When prompted, copy the device only or copy the device and all of its children.
     

Learning b3 BACnet Devices

b3 BACnet devices van be learned and to automatically assign the node IDs and initiate communication with devices on the MS/TP network.

Tip: It is possible to learn b3 devices when the b3 devices and the Automation Server functioning as the BACnet interface are connected and online. If the b3 devices are not physically connected to the network, it is also possible to manually create and configure the devices offline in Workstation. For more information, see section  "b3 BACnet Devices.

To learn b3 BACnet devices

  1. In WorkStation, in the System Tree pane, select the MSTP Network
  2. In WorkStation, on the Actions menu, click b3 devices and Learn
  3. When the b3 BACnet devices are learned, click Close
  4. If necessary, perform a download operation to eliminate any old points and programs stored on the b3 BACnet device.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 16671
  • DavidChild21
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore