Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

[Dev File] Xenta 5/7/9xx Modbus RTU Integration to Powerlogic PM800 Power Meter

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • [Dev File] Xenta 5/7/9xx Modbus RTU Integration to Powerlogic PM800 Power Meter
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • Anonymous user

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8532 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

[Dev File] Xenta 5/7/9xx Modbus RTU Integration to Powerlogic PM800 Power Meter

Picard Product_Support
‎2018-09-07 03:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:22 PM

Issue

Integration to the Powerlogic PM800 power meter with the Xenta 500 \ Xenta 700 \ Xenta 900 and Modbus RTU

Product Line

TAC Vista

Environment

  • Xenta 511, 527, 701, 711, 721 (5.1.5 up)
  • Xenta 731, 913 (all versions)
  • XBuilder
  • Powerlogic PM800 Power Meter

Cause

Disclaimer: This device template is intended to provide a starting point for an integrator, and is in no way written to be the mandatory points list for your integration effort.

Product Support Services-Dallas has written this device template in an effort to give our customers a starting point and solid example of how to develop a device template for the above product. The integrator will be responsible for any additions or modifications to this device template.

Please report any problems to PSS Dallas at product.support@buildings.schneider-electric.com

Resolution

Please us the following .dev file as a starting point and a guide to the integration. This .dev file contains a set list of registers that PSS assumed would be seen as critical and important to the integration process. If any other data is needed please see this supported document to make the necessary changes.

 

 

To use these files in Xbuilder please follow these steps:

  1. Extract the .dev file from the .zip file in the link above, and place it on your harddrive.
  2. In Xbuilder, right click on the Modbus Master device and chose Add Device
  3. Browse to the needed .dev file and choose Open.
  4. Rename the newly added device to a unique name within the Modbus Master network.
Labels (1)
Labels:
  • TAC Vista
Attachments
[Modbus Ext]PM800.zip
Tags (1)
  • Find more articles tagged with:
  • 4017
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore