Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What is pneumatic actuator spring range shift and how can it be eliminated?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is pneumatic actuator spring range shift and how can it be eliminated?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa119747
    sesa119747
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5759 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is pneumatic actuator spring range shift and how can it be eliminated?

Picard Product_Support
‎2018-09-06 02:29 PM

Last Updated: Administrator CraigEl Administrator ‎2023-07-10 07:13 PM

Issue

What is pneumatic actuator spring range shift and how can it be eliminated?

Product Line

Field Devices

Environment

Pneumatic Actuator

Cause

Spring range shift is an inherent feature of all spring return pneumatic actuators without positive positioners. The nominal published spring range of a pneumatic actuator without a positive positioner is the air pressure required to fully stroke the actuator WITH NO EXTERNAL LOAD. In the extend direction against an opposing load as provided by a damper or a valve, the supply air pressure must be increased above the spring range of the actuator to overcome the spring and the opposing force. In the retract direction against an opposing load as provided by a damper or a valve, the supply air pressure must be decreased below the spring range of the actuator so that the spring can overcome the air pressure and the opposing force. Under constant load conditions, the range of the actuator is offset by the amount of air pressure required to provide close-off of the damper or the valve.

Resolution

When is "Spring Range Shift" a concern?

It is a concern when two or more pneumatic controlled devices should be sequenced from one pneumatic signal without an overlap. An example would be a normally open heating valve and a normally closed cooling valve being sequenced from a direct acting thermostat, In this example the spring range of the normally open valve will shift upward and the normally closed valve will shift downward which means the two valves may overlap. Another area of concern is that pneumatic control signal provides proper pressure span to operate the control device and provide "tight" close-off of damper or valve. Examples of limited pressure change would be: pneumatic controllers maximum output which is limited by main air pressure; the low pressure output capability of a pneumatic controller; and electronic to pressure transducer which can have a limited output such as 3 to 15 psig.

 

What can be done to overcome "Spring Range Shift" when sequencing devices?

Sequencing can be accomplished in a pneumatic system by selecting actuators with appropriate spring ranges, utilizing positive positioners (AK-42309-500 or N800-0555) or ratio relays with bias adjustment (2378-501) or controllers with separate outputs for each actuator.

  • Positive positioners on damper and valve actuators provide the versatility of start point and span adjustment plus the availability of full pneumatic power for positioning. This is the ideal way to provide precision sequencing, since variable loading on the actuator will not effect the sequencing.
  • Biased start ratio relays may be used to provide a method of sequencing by amplifying or shifting the pneumatic signal.
  • For applications involving sequencing a pressure to electric (P.E.) switch with a pneumatic actuator, the P.E. can often be adjusted to operate outside the operating range of the actuator.
  • Sometimes larger actuators will help the sequencing problem.
  • Using full actuator stroke to rotate the damper less than 90 degrees increases the force delivered to the damper and therefore reduces control signal change required to control the actuator. Rotating the damper 60 degrees usually provides almost full flow through the damper.
  • If the actuator has an adjustable start point, adjusting the start points can help prevent sequencing problems. Normally open valves or dampers should have start point adjusted to the minimum and normally closed adjusted to the maximum.
  • Sequencing problems can be eliminated by providing controllers with separate outputs for each actuator and do the sequencing in the controller. What can be done to increase the close-off of a damper or valve actuator due to limited or insufficient pneumatic control pressure to the control device? Proper control and close-off of the control device can be accomplished by selecting actuators with appropriate spring ranges, utilizing positive positioners (AK-42309-500 or N800-0555) or ratio relays with bias adjustment ( 2378-501).
  • Positive positioners on damper and valve actuators provide the versatility of start point and span adjustment plus the availability of full pneumatic power for positioning (0 to main air pressure to the actuator).
  • Biased start ratio relay provide a method of amplifying or shifting the pneumatic signal.
  • Selecting larger actuators will increase close-off pressure.
  • Using full actuator stroke to rotate the damper less than 90 degrees increases the force delivered to the damper. Rotating the damper 60 degrees usually provides almost full flow through the damper.
  • If the actuator has an adjustable start point, proper adjustment of the start points will increase close-off. Normally open valves or dampers should have start point adjusted to the minimum and normally closed adjusted to the maximum.
  • Provide electronic to pneumatic transducers with sufficient input span to obtain maximum or sufficient pneumatic output.
Labels (1)
Labels:
  • Field Devices
Tags (2)
  • Find more articles tagged with:
  • 3830
  • CraigEllis23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore