Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,826
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 54
    • 55
    • 56
    • …
    • 509
  • Next »

Error generated when deleting Services in SP-C-Web

Issue An error is generated when trying to delete an unused Service in the SP-C-Web. Product Line EcoStruxure Security Expert Environment SP-C-Web Services Cause When using the Security Expert Client/Server and an SP-C it is possible to delete an unused/unwanted Service quite easily.       However when trying to do the same in an SP-C-Web via its web browser the following error is generated.           Resolution The SP-C-Web is fundamentally different to an SP-C with a Client/Server system.   As such deletion of Services from an SP-C-Web is not supported.  It is instead recommended to either stop the unwanted Service entirely or leave it running but without association to any Areas.
View full article
Admiral David_Kendrick Admiral
‎2023-06-27 12:05 AM

on ‎2023-06-27 12:05 AM

Labels:
  • EcoStruxure Security Expert
1209 Views

Smart Card Reader cable specification for Wiegand and RS-485 connections

Issue Where do I find the cable specifications for Wiegand and RS485 connections to the Smart Card Reader? Product Line EcoStruxure Security Expert Environment Security Expert Smart Card Readers SX-DRD-SB SX-RD-MB Cause The sample cable specification links and CAT5e / CAT6 support is missing from the Card Reader With BLE Security Expert - Installation Guide. Resolution Smart Card Reader Wiegand Cable The cable specifications are: 22 AWG alpha 5196 or 5198 18 AWG alpha 5386 or 5388 Maximum cable distance of 150m (492ft) Smart Card Reader RS-485 Cable The cable specification for RS-485 connections (including when those connections are encrypted) are: Belden 9842 or equivalent 24 AWG twisted pair with characteristic impedance of 120ohm Maximum total length of cable is max 900m (3000ft) CAT5e / CAT6 are also supported for data transmission when using ground in the same cable (to a maximum length 100m (328ft))
View full article
Picard Product_Support
‎2018-09-10 10:09 AM

Last Updated: Guinan AdamSteele Guinan ‎2023-06-26 12:07 AM

Labels:
  • EcoStruxure Security Expert
6756 Views

How to move a CyberStation installation when replacing the workstation PC on a single user system.

Issue What is the procedure on transferring Continuum from one PC to another PC? Product Line Andover Continuum Environment CyberStation SQL Cause Workstation hardware needs to be upgraded or replaced altogether Resolution Collect information from the existing machine Collect all IP address, DNS server and Windows Server IP information from the existing workstation. Run Continuum Database Initialization on the existing machine. Select Workstation and record the following information. Workstation Name Folder Name Device Node ID Network ID Data Source Name Database Name User Login ID Server Name. Verify that correct Database Passwords are known for both Andover97 user and sa accounts Start Continuum and run PinPoint. From the View menu select Options Record the folder path indicated under Graphics (Pin Files) and archive these files.  Record the folder path indicated under Background and archive these files.  If any customization has been done to the menu pages (i.e. hot spot) then the User Profile folder( C:\Program File\Continuum\UserProfile) should also be archived. Backup the Continuum Database Move the database backup and the contents of the archived folders described above to a secure external drive or a network folder (not on the workstation itself). Install CyberStation on the new machine Before removing the existing machine from the network, start the new Workstation without connecting it to the network. Configure the IP Address, DNS server and Windows Server IP address collected from the existing machine. Install CyberStation on the new Workstation PC Note: Do not forget to disable all Virus Protection and Firewalls.  When prompted run Database Initialization Use the information collected on the existing machine to initialize the StandAlone Database. Use the information collected on the existing machine to initialize the WorkStation. Start Continuum and verify that the CyberStation operates normally. Copy data collected from the existing workstation onto the new workstation. Copy Database backup file to the Backup folder under C:\Program Files\Microsoft SQL Server\ Copy contents of the archived Graphics folder to the same folder on the new workstation PC. Copy contents of the archived Background folder to the same folder on the new workstation PC. Copy contents of the archived User Profile folder to the same folder on the new workstation PC. Run PinPoint From the View Menu select Options Under Graphics (Pin Files) enter the folder path to where the Graphics files have just been copied (see above). Under Background enter the folder path to where the background image files (see above). Select the Check button and verify that a failure notice (a red "X") does not appear beside any item. Close PinPoint Restore the Continuum Database. On the new workstation, run SQL Server Management Studio Express. Navigate to the Continuum Database. Right click on the Continuum Database, select Restore Browse to the folder where the existing Database backup file was copied to.  When the restore has completed successfully. Change the DB Owner: Right clicking on the Continuum database Selecting new query. In the query window type SP_ChangeDBOwner Andover97 From the tool bar select Execute. The result window should return............Command(s) completed successfully Reset the passwords for Andover97 and SA Open Security from the main tree, Select Logins. Right click on Andover97 and select properties enter and retype new strong password password, retype the correct password. Repeat for SA password. Now restart the PC. Run Database Initialization Under StandAlone, update the database. Re-Launch Continuum CyberStation and verify that CyberStation is working properly. Shut down the new workstation. Swap the workstations Shutdown the existing workstation and remove it from the network. Connect the new workstation to the network Start the computer. Launch Continuum and verify all functions are operating as expected.
View full article
Picard Product_Support
‎2018-09-06 01:56 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-22 12:18 AM

Labels:
  • Andover Continuum
2418 Views

Show raw card data of a badged card in Security Expert

Issue How to show raw card data of a badged card in Security Expert. Product Line EcoStruxure Security Expert Environment Security Expert Custom Card Format Cause Need to configure a custom card format and need to see the raw bit string to determine this. Resolution Displaying a cards raw data is a function that can be set in the Reader expander. 1. Confirm that the Display Card Data When Invalid option is enabled on the Reader tab under Misc Options. Misc options Display Card Detail When Invalid: When enabled, the reader expander will display the actual card data received from the reader when the card number is not known. This can be used to interface with custom third party applications that require their own processing of card information. This option is enabled by default and can be used to add card data to a user when operating Security Expert. When disabled the reader will display the card number not found message. 2. Next, set the Reader format on the Reader tab under Configuration to Any bit (raw). any bit raw 3. Now when badging a card at this reader port it should populate two events. One for the Card Number Raw Data and another for the Facility Code Raw Data.   Example: Read Card Number Raw Data: 46160846 Read Facility Code Raw Data: 436207616 Put the facility code into a Programmer Calculator to convert from Decimal to Binary. This is a 32-bit number. 00011010000000000000000000000000 Of the 32 bit number take the first 8 Binary digits (in the example this is 0001 1010) and convert this back to decimal. 00011010 bin = 26 dec What you should see in the decimal field is the bit length the card uses. Now in the Reader Format, it’s an experiment to find out which of the Bit options would correspond to the cards. (In the example above you would need to look through the 26 bit options.)
View full article
Picard Product_Support
‎2018-09-10 12:45 PM

Last Updated: Guinan AdamSteele Guinan ‎2023-06-22 12:17 AM

Labels:
  • EcoStruxure Security Expert
5318 Views

How do I find the IP address of a third party BACnet device?

Issue When browsing the IP network using the WorkPlace Commissioning Tool, third party devices are displayed in addition to the I/A Series BACnet devices but no information is known about those devices. Product Line TAC I/A Series Environment WorkPlaceTech Commissioning Tool 3rd party BACnet IP & MS/TP devices Cause 3rd party BACnet devices are sometimes connected to the IP network without the knowledge of the engineer  programming the I/A Series system. Resolution When performing a global browse of the IP network, unknown devices are sometimes displayed in the WorkPlaceTech Commissioning Tool device list display.  Since all data columns are not necessarily displayed, some of the device information may not be able to be directly determined. Right-click in the column headers and a menu of available data columns will be displayed. The following columns may be displayed at a minimum to allow identification of the devices on the network as well as the BACnet routing path to those devices:     Instance     Vendor     Model     Router     Network     Address   If the device is a BACnet IP device, the "Address" will be displayed as an IP Address and Port.  For example the address of a BACnet IP device communicating via port 47821 at IP 10.159.34.238 Address   =  10.159.34.238 : 47821   If the device is a BACnet MS/TP device under a BACnet IP device, the address is the MAC address of the device on the MSTP bus and the Router is the address of the BACnet IP router to that device in Hexadecimal numbers.  For example, for MSTP device #4 under BACnet IP Router address, 10.159.34.238 : 47821 10 = 0A, 159 = 9F, 34 = 22, 236 = EC and 47821 = BA CD  Address   =   4 Router      =   0A-9F-22-EC-BA-CD   If the device provides vendor and model information, that information will be displayed in the appropriate columns.
View full article
Picard Product_Support
‎2018-09-10 11:32 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:51 AM

Labels:
  • TAC IA Series
4102 Views

BACnet error message when trying to use WriteProperty to a 3rd Party BACnet device

Issue When trying to use WriteProperty to a 3rd Party BACnet device the following error is generated : "An attempt has been made to write to a property defined as inaccessible through the BACnet protocol write service" Product Line Andover Continuum Environment BACnet  Cause The error can be seen when using WriteProperty OR when attempting to Manually Command a BACnet Point on a 3rd Party Device Resolution The property that is being commanded, is not available to be written to in the 3rd party device. Many properties and object classes cannot be written to on BACnet devices, this is often defined in the devices PIC Statement which has hopefully also been BTL Tested. Some BACnet devices allow writing to be enabled/ disabled, but this must be set up on the 3rd Party device itself depending on the site requirements.  An example of this is in the Jace unit where there is a regular BACnet user that has no write capabilities from 3rd party devices, so to allow this requires a tick a box for "Super user".
View full article
Picard Product_Support
‎2018-09-11 03:53 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:54 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
3519 Views

It is normal for a BACnet network port's Poll Service 'Busy Time' property to be greater than 100%?

Issue It is normal for a BACnet network port's Poll Service 'Busy Time' property to be greater than 100%? Eg: Product Line I/A Series Environment G3 BACnet Cause The Poll Service is a common component for typical field bus drivers including BACnet.  The Niagara Ax Drivers Guide defines the Poll Service's Busy Time property as: Displays a percentage of time spent by the poll thread actually polling points, across all poll buckets. Includes (in parentheses) a ratio of “(time spent polling/total time since statistics were restarted)”. Given a small amount of time is spent transitioning between poll buckets, and with the thread sleeping to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%. However, any percentage above 95% indicates that the poll thread is basically spending all of its time actually polling.  Resolution In the case of the Poll Service for a BACnet network port, because two threads are used for polling, it is possible to see a Busy Time approaching 200%. In this case, divide the Busy Time in half to get an average busy time for each thread. In the case of the Poll Service for a Bacnet network port, because two threads are used for polling, it is possible to see a Busy Time approaching 200%. In this case, divide the Busy Time in half to get an average busy time for each thread. actually polling. However, any percentage above 95% indicates that the poll thread is basically spending all of its time actually polling. to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%. However, any percentage above 95% indicates that the poll thread is basically spending all of its time actually polling to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%. However, any percentage above 95% indicates that the poll thread is basically spending all of its time actually polling. Given a small amount of time is spent transitioning between poll buckets, and with the thread sleeping to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%. However, any percentage above 95% indicates that the poll thread is basically spending all of its time actually polling. Includes (in parentheses) a ratio of “(time spent polling/total time since statistics were restarted)”. Given a small amount of time is spent transitioning between poll buckets, and with the thread sleeping to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%. However, any percentage above 95% indicates that the poll thread is basically spending all of its time actually polling.
View full article
Picard Product_Support
‎2018-09-11 04:29 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:57 AM

Labels:
  • TAC IA Series
3131 Views

How to capture localhost traffic with Wireshark to help troubleshoot EWS communication issues.

Issue When the EWS is installed on the same machine using the service then all packets will be going to the localhost and will not hit the NIC so will not be captured in a Wireshark packet capture. Product Line EcoStruxure Building Operation, EcoStruxure Security Expert Environment Security Expert Building Operation Enterprise Server Building Operation Automation Servers (AS-P, AS-B) Cause Packets sent between services on the same machine (like SOAP and EWS) do not hit the NIC and therefore cannot be captured with the default configuration of Wireshark using the WinPcap packet sniffing library.  Resolution Replace WinPcap with Npcap to emulate a loopback NIC for packet capture. Go to https://nmap.org/npcap/ for details on the library. Download the library installer from https://nmap.org/npcap/#download Uninstall WinPcap. Install Npcap. Npcap will then create an adapter named Npcap Loopback Adapter. In Wireshark choose this adapter to capture, loopback traffic will be the seen the same way as other non-loopback adapters. This can be tested by typing in commands like "ping 127.0.0.1" (IPv4)  or "ping ::1" (IPv6).
View full article
Picard Product_Support
‎2018-09-10 09:07 AM

Last Updated: Guinan AdamSteele Guinan ‎2023-06-21 11:47 PM

Labels:
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
12320 Views

How to trigger an output with Access Denied events

Issue Need to activate an Output when access is denied to a User at a Door. Product Line Security Expert Environment EcoStruxure Security Expert Cause In the Door object, there is a facility for triggering Outputs on Pre Alarm, Door Left Open, and Door Forced Open but nothing for when a User is denied access. Resolution There were new Door commands added to SP-C firmware 2.08.1018 and newer to add this functionality. AccessDeniedTime = # has been added to the Door commands which will specify the duration in seconds that an output or output group will be activated for when access to the door has been denied. This must also be paired with one of the following 2 commands in order for the functionality to occur. AccessDeniedOutput = # has been added to the Door commands which will specify the output that will be activated when access to the door has been denied. The # will be the database ID of the output/output group. AccessDeniedOutputGroup = # has been added to the Door commands which will specify the output group that will be activated when access to the door has been denied. The # will be the database ID of the output group. As an example, if you wanted the Output with an Id = 3 to turn on for 5 seconds when access is denied at the Door, the following lines would need to be added to the Door object in the Commands section. AccessDeniedTime = 5 AccessDeniedOutput = 3 Door Command - Access Denied Output  
View full article
Guinan AdamSteele Guinan
‎2020-09-18 12:03 AM

Labels:
  • EcoStruxure Security Expert
1797 Views

Associate AS BACnet Interface IO points with points on the IO bus

Issue How to associate BACnet IO points created under the BACnet Interface of the Automation Server with IO points on the Automation Server's IO bus. Product Line EcoStruxure Building Operation Environment Building Operation Servers 1.4 and above Building Operation Workstation Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Connect physical IO points to BACnet network controllers. Resolution BACnet Association Tool (EBO V3.0 or higher) BACnet Association Tool will map properties of a central IO point with corresponding properties of a BACnet point. The tool is capable of mapping a single IO point with a single BACnet point, optionally by also creating a BACnet point, and removing the association between IO and BACnet points. To open the BACnet Association Tool, Select the IO Bus or IO Module, BACnet Interface, Application Folder, or the BACnet point, then in the Actions menu, click BACnet Association Tool. Most useful is the ability to associate multiple IO points with their corresponding BACnet points in one operation. The tool can be run from a variety of different container types in the WorkStation Tree view, including an IO point, BACnet Point, CIO Module, or the entire IO Bus (as shown below). For more information refer to WebHelp articles: Creating and Associating BACnet Points to I/O Points (se.com) and Associating or Updating BACnet Point Associations to I/O Points (se.com) NOTE: Please be aware applying the BACnet Association Tool retrospectively, to an already configured site, can remove bindings to outputs.  For example output bindings in Script or Function Block programs.  As shown below, if the tool is used to create a BACnet Associated point for an output already bound to a program (1) the Requested Value will be replaced by the Associated Value of the BACnet point (2). This is due to how the BACnet Association Tool uses the bindings, where the newly created BACnet point should be used instead of the IO point.  The solution is to update the removed program binding (3) to use the BACnet Associated point value (4).   SBO 1.4 to 2.x To associate BACnet IO points created under the BACnet Interface of the Automation Server to points in the IO Bus in SBO 1.4 and above... The association is made via a read reference, so if we think of the two objects as one being the source and the other the destination you configure the association from the destination object so in the case of an output you configure the association from the BACnet object (in this example BO1). In the case of an input, you'd configure the association from the IO Bus input as that would be the destination object, in other words, the recipient of the value. (NOTE: for versions prior to 1.4 see Bacnet and StruxureWare Building Operation Central IO points) Create the points. In this example, we are associating an IO output point named 'Digital Output 1' with a BACnet Binary Output named BO1. From the properties page of the IO Bus point (Digital Output 1 in this example) click on the gear icon to the right of the 'Requested value' field. In the 'Requested value' editor click the navigation icon (...) to the right of the 'Reference' field and navigate to the 'Associated Value' of the BACnet point. Save the configuration changes. Now that the values have been associated setting the BACnet output value (BO1) will drive the IO Bus output (Digital Output 1)  
View full article
Picard Product_Support
‎2018-09-11 12:07 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-20 08:59 AM

Labels:
  • EcoStruxure Building Operation
5022 Views

No beep when presenting a card in front of an HID reader

Issue When swiping a card in front of the reader, there should be a beep indicating that the reader has read the card. There is no beep. Product Line EcoStruxure Security Expert, Andover Continuum, TAC I/NET Environment Access Control HID Reader Cause There are 3 possible reasons for this issue: The beeper is disabled through a default configuration when the card is shipped The beeper has failed The Reader and Card represent incompatible technologies such as an 125Khz Prox Reader trying to read a 13.56MHz IClass Card Resolution Ensure Reader and Card both support a common technology (125Khz/13.56Mhz etc..) Short the Beeper wire (yellow) and the GND wire (Black) with the reader powered On If there is a beep, that indicates that the beeper can work but is disabled. Ask the manufacturer to send a configuration card to enable the beeper (use 3 seconds after reader power is on) If shorting the beeper produces no sound, the beeper has failed. Send the reader to repair and replace it with a new one.
View full article
Picard Product_Support
‎2018-09-06 09:56 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:50 AM

Labels:
  • Andover Continuum
  • EcoStruxure Security Expert
  • TAC INET
4141 Views

Error performing Continuum Database Initialization

Issue When performing Continuum Database Initialization from a CyberStation workstation, the workstation cannot connect to the SQL Server with the following error message: "Microsoft SQL Server Login Connection failed or server not available or access denied" Product Line Andover Continuum Environment LAN workstations Single User workstations Cause Possible Invalid Server Name is being used in Continuum Database Initialization:   For Continuum LAN systems, the Server Name attribute of Continuum Continuum Database Initialization includes invalid characters.  For Continuum Single User systems, the Server Name attribute of Continuum Continuum Database Initialization does not include the \SQLExpress attribute after the Computer name.  Resolution For Continuum LAN systems, type the correct computer name of the SQL Server in the Server Name attribute field of Continuum Database Initialization screen such as "MyDBServer". Check that the required strong password is being used, such as "ABCabc123" For Continuum Single User systems, add the qualifier "\SQLExpress" at the end of the computer name in the Server Name attribute field of Continuum Database Initialization screen such as "MySUServer\SQLExpress" . Restart the SQL Server  Service and/or SQL Agent Service Check that the Windows Firewall on the Windows Server PC is turned off. Check Connection with sa Admin account on MS Management Studio and via ODBC.
View full article
Picard Product_Support
‎2018-09-06 01:15 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:46 AM

Labels:
  • Andover Continuum
2926 Views

Valid access events are not logging or showing in the active event view but Invalid events show

Issue On a working system, valid access events no longer show in the active event view and are no longer visible in the accessevent table within the Database.   However, invalid events continue to work normally.  Product Line Andover Continuum Environment Access Events Logging Cause An incomplete object may have been added to the Continuum Database recently that is interfering with queries running against that database. Resolution Try the following steps to troubleshoot the issue Does the issue happen on multiple CyberStations? Ensure all the event types are selected in the active event view that is being used on the door(s). Perform a CyberStation Teach It is best to contact PSS and work with them at this point with the following procedures.   Verify that access events are being sent from the controller to the CyberStation using Wireshark. Verify that the issue follows the Database by loading the database in a test environment to see if the issue still happens.  On the TEST database, use SQL Management Studio:  SQL Query: set acdbversion=0  (execute the query)  Update database: launch Database Initialization Server/Stand Alone Enter sa password and update database Restore database or locate incomplete object The quickest fix would be to revert to a known good database. Once restored, the events in the controllers would be downloaded to the database. Finding the object in the database that has caused the issue can be very challenging. Check to see if there was a controller recently added and if the issue began to happen after that. If for some reason a controller had been added and it wasn't completed normally then it could cause this issue. Check to see if there is a controller in the InfinityController table with an objectidhi or objectidlo with a zero value. If so, delete that controller and see if the valid access events start coming in. It may also be necessary to use the SQL profiler to view the entries that are being made into the database. See the following link  below for  more information. http://msdn.microsoft.com/en-us/library/ms181091.aspx   NOTE: Turning off the Primary and Secondary Access Server will cause the access events to buffer in the controllers, so that these events will be inserted into the database once valid access event logging has been restored. After turning off the primary and secondary, check the Access Log infinity system variable on the controllers. If they are non zero values, then events are buffering. There is a limited amount of access events that can be stored in the controllers before loss of data occurs.
View full article
Picard Product_Support
‎2018-09-10 05:23 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 07:31 AM

Labels:
  • Andover Continuum
2500 Views

HID Corporate 1000 Cards

Issue Support for HID Corporate 1000 Product Line TAC I/NET Environment HID Corporate 1000 35-bit Wiegand Cause Desire for higher security HID Corporate 1000 Cards Resolution I/NET will work with Corporate 1000 cards, but there are several things to check and go over concerning this type of setup.   Below is a link to the HID Corporate 1000 information page and FAQs https://www.hidglobal.com/access-control/corporate-1000-program   One other consideration is the site will have to go to a Large Number format for the Corporate 1000 format.  The site requesting Corporate 1000 card certification will need to be verified, and though this is not an expense, it will take time.     Note: I/NET will not allow two variations of Wiegand in the same controller. In the door parameters, set up a single Reader type, such as Wiegand 26. 
View full article
Picard Product_Support
‎2018-09-10 04:56 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:23 AM

Labels:
  • TAC INET
2522 Views

Unable to Initialize Continuum Database after installing new SQL instance

Issue After installing a new SQL server and installing CyberStation on a workstation PC, Database Initialization is unable to connect to the database. Product Line Andover Continuum Environment SQL Database Initialization Cause The Database has not been assigned with a correct owner. Resolution In SQL Server Management Studio, highlight ContinuumDB. Right Click on ContinuumDB. Select "New Query" In the query field type SP_ChangeDBOwner 'Andover97' Run the query Once the query returns Success, it should be possible to Initialize the Database successfully.
View full article
Picard Product_Support
‎2018-09-06 12:43 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:08 AM

Labels:
  • Andover Continuum
2708 Views

7790A LIU Information

Issue 7790A LAN Interface Unit and Information. Why is the 7790A not shown in my Network Configuration Product Line TAC I/NET Environment I/NET Seven Software v2.45 7790A LAN Interface Unit (LIU) 7791A Door Processing Interface (DPI) 7792A Micro Regulator Interface (MRI) 7793A Micro Control Interface (MCI) Cause Information about the 7790A LAN Interface Unit or LIU Confusion is usually with the Hardware Model when purchasing. Once installed and configured for one of the three common options above, firmware (software) is downloaded to the hardware device (7790A) to become one of the three indicated interfaces, DPI, MRI, and MCI. In the later release of I/NET Seven Software only supports the 7793 MCI.  Resolution Refer to TCON109 attached for further information.    The 7793 has two channels and will handle 32 devices on each channel if addressed correctly. This gives a total of 64 SCU units on a single 7793. The 7790A can be addressed using the HHC to a 7790, 7791, 7792, 7793, 7797.  The 7790A replaces the 7797A-C as of January 1, 2013. The original 7791 was primarily for Access Control. The original 7792 was primarily for HVAC. The 7793 is a combination for both and the most popular of the 7790 series. To clarify, when purchasing a 7790A, you would address as a 7793, then put up to 32 SCUs on each of the channels giving you a total capacity of 64 SCUs.     For access control, the model 7798C has more memory but only one Channel, which means it can handle up to a maximum of 32 SCU controllers and the recommended interface for larger access control sites.  
View full article
Picard Product_Support
‎2018-09-11 01:26 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-06-19 04:49 PM

Labels:
  • TAC INET
3894 Views

Continuum Compatibility with Video Expert

  Issue Continuum compatibility with Video Expert Product Line Andover Continuum Environment Andover Continuum Video Expert Cause Video Expert is not listed as a video integration for Continuum on the Video compatibility matrix. Is there any way to accomplish the integration? Resolution Continuum and a Video Expert integration is not supported natively (by R&D) like the other Pelco integrations. For Example Digital Sentry and Endura.   The Center of Excellence(CoE) team has a number of add-ons/pay-for Continuum integrations including Video Expert.    However, the Video Expert add-on integration has not been updated since 2018, so the integration is no longer compatible with the current version of Video Expert.   Unfortunately, with Continuum end-of-life approaching the CoE team are no longer upgrading any legacy integration software versions. Link to Continuum Video Compatibility Matrix Article: https://community.se.com/t5/Building-Automation-Knowledge/Continuum-Video-Integration-Compatibility-Matrix-and-Supported/ta-p/531  
View full article
Admiral Alan_Wood Admiral
‎2023-06-15 05:54 PM

on ‎2023-06-15 05:54 PM

Labels:
  • Andover Continuum
1319 Views

Automatically Running Continuum Standard Reports using Windows10

Issue A method is needed to automatically schedule and run Continuum standard reports Product Line Andover Continuum Environment Cyberstation Windows10 Cause Sites want Continuum Report to run automatically  Resolution Scheduling Automatic Reports Using a special Continuum application, ReportCmdLine,  and Microsoft Windows Scheduler, reports may be run automatically on a regular basis at a specific time. When the report runs automatically, it can also automatically be emailed to one or more recipients and/or saved to a file.   CyberStation must be running when using the ReportCmdLine application. To set up and run a report automatically, perform the following procedure:   If the report should also email when it runs automatically, check the Output report to email address checkbox on the Output tab, and enter email address recipients. Likewise, if the report should save to file when it runs automatically, check the Output report to file in path checkbox and enter the file's path.   From Start> Run> control (type this command and Enter) This will open up Windows control panel Double-click Administrative Tools> Task Scheduler Click Create Basic Task, Name: ReportCmdLine (or whatever name is needed), Next Select how often the task will be run, Next Specify the start date and how often the task should recur, Next Select which action to be performed, Next Enter the ReportCmdLine executable path and command line options /o - ObjectName Enter the path name of the Report object to run automatically. It is recommended to use a  full path instead of just the name of the object file. /u - UserName Enter the CyberStation User Name /t -Type Enter an integer to specify the type of distribution: 0 — Save to a file 1 — Email 2 — Save to a file and email In the Program/script field, enter the command syntax as follows: “C:\Program Files (x86)\Continuum\ReportCmdLine.exe” /o ObjectName /u UserName /t Type Note: Make sure the command option parameters are set outside the quotes surrounding the path and executable Example with the Continuum objects specified: “C:\Program Files (x86)\Continuum\ReportCmdLine.exe” /o DailyRpt /u acc /t Type 0 If the ObjectName or UserName contains a space, then place quotes around those items: “C:\Program Files (x86)\Continuum\ReportCmdLine.exe” /o “Object Name” /u “User Name” /t Type 0 Parameter Descriptions The email recipients and file path are specified on the Output tab After clicking Next, click Yes to accept the command and arguments Click Finish to create the Task   See the following link for additional information on setting up a Scheduled Task in Windows10:  https://www.windowscentral.com/how-create-automated-task-using-task-scheduler-windows-10    Note: If having problems getting the report to run, try typing the report command from step 7 into a DOS prompt. This will give immediate feedback to make sure the command is getting executed. Doing this prior to using the command in Task Scheduler will help to get the command set up correctly.   For additional information, see Continuum Help (F1) in the Reports> Scheduling Automatic Reports section.
View full article
Picard Product_Support
‎2018-09-10 03:52 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-06-14 06:53 PM

Labels:
  • Andover Continuum
2809 Views

Showing SpaceLogic IP controllers (MP-x/RP-x) IP changes pending flag in search list view

Issue How to configure search object to display SpaceLogic controllers IP settings "Changes pending" in the search's list view Product Line EcoStruxure Building Operation Environment Space Logic IP controllers  Cause Confusion when attempting to find the appropriate type to include in the search  Resolution The IP settings "Changes pending" property is not a property of the device but rather a property of the IP Network Port as seen in the screen shot below  
View full article
Captain AbeMeran Captain
‎2023-06-13 11:12 AM

on ‎2023-06-13 11:12 AM

Labels:
  • EcoStruxure Building Operation
1050 Views

MNB firmware version may not be correctly reported in EBO and Building Advisor Portal

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed correctly. Before beginning these steps, ensure all necessary data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue MNB firmware may not match the version reported in EBO and Building Advisor Portal. Product Line EcoStruxure Building Operation, EcoStruxure Building Advisor Environment I/A Series MNB I/A Series WorkPlace Tech Building Operation Workstation Building Operation Building Advisor EBO Health Module Cause MNB firmware is upgraded via the WorkPlaceTech Commissioning Tool independent of EBO, and EBO reports firmware to Building Advisor Portal for use in BMS Health Module. Example cases where controllers are upgraded after adding to EBO are: MNB controllers added with factory default firmware version MNB controllers transitioned into EBO with existing older firmware version MNB controller that was upgraded to the latest was replaced with MNB Controller at factory default firmware version Resolution Create a Saved Search to identify all MNB controllers in the system Create New Search Enter * in Object Name Field Click ... button next to Include Types: and add all the MNB controller models Right-click on Column Header and select Add/Remove columns to select Firmware revision and Model name, and remove Description Save the search and select a location and name it Run the search to identify all the MNB controllers Sort by Firmware Revision to find older versions. MNB-1000 will end in 01.5xx and all other MNB ASC models will end in 01.4xx Update firmware version from the controller(s) Select one or more MNB controllers Right-click and select Device -> Upload Configuration. *WARNING*: Ensure you do NOT select Download Configuration  Now EBO is reporting the correct firmware in the controller and will upload this information to Building Advisor Portal, if cloud connectivity is established. Upgrade any MNB controller firmware with WorkplaceTech Commission Tool to the latest version and perform Steps 2 and 3 to keep EBO updated.
View full article
Picard David_Purser Picard
‎2023-06-09 06:50 PM

Last Updated: Guinan RandyDavis Guinan ‎2023-06-12 12:48 PM

Labels:
  • EcoStruxure Building Advisor
  • EcoStruxure Building Operation
1550 Views
  • « Previous
    • 1
    • …
    • 54
    • 55
    • 56
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of