How to move a CyberStation installation when replacing the workstation PC on a single user system.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to move a CyberStation installation when replacing the workstation PC on a single user system.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • Chris_Asbury
    Chris_Asbury
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2679 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to move a CyberStation installation when replacing the workstation PC on a single user system.

Picard Product_Support
‎2018-09-06 01:56 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-22 12:18 AM

Issue

What is the procedure on transferring Continuum from one PC to another PC?

Product Line

Andover Continuum

Environment

  • CyberStation
  • SQL

Cause

Workstation hardware needs to be upgraded or replaced altogether

Resolution

Collect information from the existing machine

  • Collect all IP address, DNS server and Windows Server IP information from the existing workstation.
  • Run Continuum Database Initialization on the existing machine.
  • Select Workstation and record the following information.
    • Workstation Name
    • Folder Name
    • Device Node ID
    • Network ID
    • Data Source Name
    • Database Name
    • User Login ID
    • Server Name.
  • Verify that correct Database Passwords are known for both Andover97 user and sa accounts
  • Start Continuum and run PinPoint.
    • From the View menu select Options
    • Record the folder path indicated under Graphics (Pin Files) and archive these files. 
    • Record the folder path indicated under Background and archive these files. 
  • If any customization has been done to the menu pages (i.e. hot spot) then the User Profile folder( C:\Program File\Continuum\UserProfile) should also be archived.
  • Backup the Continuum Database
  • Move the database backup and the contents of the archived folders described above to a secure external drive or a network folder (not on the workstation itself).

Install CyberStation on the new machine

  • Before removing the existing machine from the network, start the new Workstation without connecting it to the network.
  • Configure the IP Address, DNS server and Windows Server IP address collected from the existing machine.
  • Install CyberStation on the new Workstation PC Note: Do not forget to disable all Virus Protection and Firewalls. 
  • When prompted run Database Initialization
    • Use the information collected on the existing machine to initialize the StandAlone Database.
    • Use the information collected on the existing machine to initialize the WorkStation.
  • Start Continuum and verify that the CyberStation operates normally.

Copy data collected from the existing workstation onto the new workstation.

  • Copy Database backup file to the Backup folder under C:\Program Files\Microsoft SQL Server\
  • Copy contents of the archived Graphics folder to the same folder on the new workstation PC.
  • Copy contents of the archived Background folder to the same folder on the new workstation PC.
  • Copy contents of the archived User Profile folder to the same folder on the new workstation PC.
  • Run PinPoint
    • From the View Menu select Options
    • Under Graphics (Pin Files) enter the folder path to where the Graphics files have just been copied (see above).
    • Under Background enter the folder path to where the background image files (see above).
    • Select the Check button and verify that a failure notice (a red "X") does not appear beside any item.
  • Close PinPoint

Restore the Continuum Database.

  • On the new workstation, run SQL Server Management Studio Express.
  • Navigate to the Continuum Database.
  • Right click on the Continuum Database, select Restore
  • Browse to the folder where the existing Database backup file was copied to. 
  • When the restore has completed successfully. Change the DB Owner:
    • Right clicking on the Continuum database
    • Selecting new query.
    • In the query window type SP_ChangeDBOwner Andover97
    • From the tool bar select Execute.
    • The result window should return............Command(s) completed successfully
    • Reset the passwords for Andover97 and SA
      1. Open Security from the main tree,
      2. Select Logins.
      3. Right click on Andover97 and select properties
      4. enter and retype new strong password password, retype the correct password.
      5. Repeat for SA password.
    • Now restart the PC.
  • Run Database Initialization
  • Under StandAlone, update the database.
  • Re-Launch Continuum CyberStation and verify that CyberStation is working properly.
  • Shut down the new workstation.

Swap the workstations

  • Shutdown the existing workstation and remove it from the network.
  • Connect the new workstation to the network
  • Start the computer.
  • Launch Continuum and verify all functions are operating as expected.
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 4951
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore