Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

It is normal for a BACnet network port's Poll Service 'Busy Time' property to be greater than 100%?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • It is normal for a BACnet network port's Poll Service 'Busy Time' property to be greater than 100%?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • RobertAndriolo
    RobertAndriolo
  • RyanSuar
    RyanSuar
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3360 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

It is normal for a BACnet network port's Poll Service 'Busy Time' property to be greater than 100%?

Picard Product_Support
‎2018-09-11 04:29 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:57 AM

Issue

It is normal for a BACnet network port's Poll Service 'Busy Time' property to be greater than 100%?

Eg:

Product Line

I/A Series

Environment

G3 BACnet

Cause

The Poll Service is a common component for typical field bus drivers including BACnet. 

The Niagara Ax Drivers Guide defines the Poll Service's Busy Time property as:

Displays a percentage of time spent by the poll thread actually polling points, across all poll buckets. Includes (in parentheses) a ratio of “(time spent polling/total time since statistics were restarted)”. Given a small amount of time is spent transitioning between poll buckets, and with the thread sleeping to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%. However, any percentage above 95% indicates that the poll thread is basically spending all of its time actually polling. 

Resolution

In the case of the Poll Service for a BACnet network port, because two threads are used for polling, it is possible to see a Busy Time approaching 200%. In this case, divide the Busy Time in half to get an average busy time for each thread.

In the case of the Poll Service for a Bacnet network port, because two threads are used for
polling, it is possible to see a Busy Time approaching 200%. In this case, divide the Busy Time in half
to get an average busy time for each thread.
actually polling.
However, any percentage above 95% indicates that the poll thread is basically spending all of its time
actually polling.
to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%.
However, any percentage above 95% indicates that the poll thread is basically spending all of its time
actually polling
to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%.
However, any percentage above 95% indicates that the poll thread is basically spending all of its time
actually polling.
Given a small amount of time is spent transitioning between poll buckets, and with the thread sleeping
to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%.
However, any percentage above 95% indicates that the poll thread is basically spending all of its time
actually polling.
Includes (in parentheses) a ratio of “(time spent polling/total time since statistics were restarted)”.
Given a small amount of time is spent transitioning between poll buckets, and with the thread sleeping
to evenly space out polling messages, it is unlikely to ever see Busy Time reach exactly 100%.
However, any percentage above 95% indicates that the poll thread is basically spending all of its time
actually polling.
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 13850
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore