How do I find the IP address of a third party BACnet device?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How do I find the IP address of a third party BACnet device?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4289 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How do I find the IP address of a third party BACnet device?

Picard Product_Support
‎2018-09-10 11:32 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 04:51 AM

Issue

When browsing the IP network using the WorkPlace Commissioning Tool, third party devices are displayed in addition to the I/A Series BACnet devices but no information is known about those devices.

Product Line

TAC I/A Series

Environment

  • WorkPlaceTech Commissioning Tool
  • 3rd party BACnet IP & MS/TP devices

Cause

3rd party BACnet devices are sometimes connected to the IP network without the knowledge of the engineer  programming the I/A Series system.

Resolution

When performing a global browse of the IP network, unknown devices are sometimes displayed in the WorkPlaceTech Commissioning Tool device list display.  Since all data columns are not necessarily displayed, some of the device information may not be able to be directly determined.

Right-click in the column headers and a menu of available data columns will be displayed.

The following columns may be displayed at a minimum to allow identification of the devices on the network as well as the BACnet routing path to those devices:

  •     Instance
  •     Vendor
  •     Model
  •     Router
  •     Network
  •     Address

 

If the device is a BACnet IP device, the "Address" will be displayed as an IP Address and Port. 

For example the address of a BACnet IP device communicating via port 47821 at IP 10.159.34.238

Address   =  10.159.34.238 : 47821

 

If the device is a BACnet MS/TP device under a BACnet IP device, the address is the MAC address of the device on the MSTP bus and the Router is the address of the BACnet IP router to that device in Hexadecimal numbers. 

For example, for MSTP device #4 under BACnet IP Router address, 10.159.34.238 : 47821

10 = 0A, 159 = 9F, 34 = 22, 236 = EC and 47821 = BA CD 

Address   =   4

Router      =   0A-9F-22-EC-BA-CD

 

If the device provides vendor and model information, that information will be displayed in the appropriate columns.

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 12500
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.