Automatically Running Continuum Standard Reports using Windows10

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Automatically Running Continuum Standard Reports using Windows10
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • RobertAndriolo
    RobertAndriolo
  • David_Kendrick
    David_Kendrick
  • Dave_Shore
    Dave_Shore
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3262 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Automatically Running Continuum Standard Reports using Windows10

Picard Product_Support
‎2018-09-10 03:52 AM

Last Updated: Picard RobertAndriolo Picard ‎2023-06-14 06:53 PM

Issue

A method is needed to automatically schedule and run Continuum standard reports

Product Line

Andover Continuum

Environment

  • Cyberstation
  • Windows10

Cause

Sites want Continuum Report to run automatically 

Resolution

Scheduling Automatic Reports

Using a special Continuum application, ReportCmdLine,  and Microsoft Windows Scheduler, reports may be run automatically on a regular basis at a specific time. When the report runs automatically, it can also automatically be emailed to one or more recipients and/or saved to a file.

 

CyberStation must be running when using the ReportCmdLine application.

To set up and run a report automatically, perform the following procedure:

 

    1. If the report should also email when it runs automatically, check the Output report to email address checkbox on the Output tab, and enter email address recipients.

      Likewise, if the report should save to file when it runs automatically, check the Output report to file in path checkbox and enter the file's path.

       

    2. From Start> Run> control (type this command and Enter)

      This will open up Windows control panel

      Double-click Administrative Tools> Task Scheduler

    3. Click Create Basic Task, Name: ReportCmdLine (or whatever name is needed), Next
      CreateBasicTask.png
    4. Select how often the task will be run, Next
      TaskTrigger.png
    5. Specify the start date and how often the task should recur, Next
      DailyRecur.png
    6. Select which action to be performed, Next
      Action.png
    7. Enter the ReportCmdLine executable path and command line options
      • /o - ObjectName
        Enter the path name of the Report object to run automatically. It is recommended to use a  full path instead of just the name of the object file.
      • /u - UserName
        Enter the CyberStation User Name
      • /t -Type
        Enter an integer to specify the type of distribution:
        • 0 — Save to a file
        • 1 — Email
        • 2 — Save to a file and email
      1. In the Program/script field, enter the command syntax as follows:

        “C:\Program Files (x86)\Continuum\ReportCmdLine.exe” /o ObjectName /u UserName /t Type
        Note: Make sure the command option parameters are set outside the quotes surrounding the path and executable

      2. Example with the Continuum objects specified:

        “C:\Program Files (x86)\Continuum\ReportCmdLine.exe” /o DailyRpt /u acc /t Type 0

      3. If the ObjectName or UserName contains a space, then place quotes around those items:

        “C:\Program Files (x86)\Continuum\ReportCmdLine.exe” /o “Object Name” /u “User Name” /t Type 0

      4. Parameter Descriptions
      5. The email recipients and file path are specified on the Output tab
        StartProgram-Script.png
      6. After clicking Next, click Yes to accept the command and arguments
        Program-Arguments Yes-No.png
    8. Click Finish to create the Task
      SummaryFinish.png

 

See the following link for additional information on setting up a Scheduled Task in Windows10: 
https://www.windowscentral.com/how-create-automated-task-using-task-scheduler-windows-10 

 

Note: If having problems getting the report to run, try typing the report command from step 7 into a DOS prompt. This will give immediate feedback to make sure the command is getting executed. Doing this prior to using the command in Task Scheduler will help to get the command set up correctly.

 

For additional information, see Continuum Help (F1) in the Reports> Scheduling Automatic Reports section.

Labels (1)
Labels:
  • Andover Continuum
Tags (10)
  • Find more articles tagged with:
  • 6528
  • AlanWood22
  • automatic
  • command line
  • DavidKendrick23
  • email
  • reportcmdline
  • reports
  • RobertAndriolo23
  • schedule
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore