Valid access events are not logging or showing in the active event view but Invalid events show

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Valid access events are not logging or showing in the active event view but Invalid events show
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2480 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Valid access events are not logging or showing in the active event view but Invalid events show

Picard Product_Support
‎2018-09-10 05:23 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-06-20 07:31 AM

Issue

On a working system, valid access events no longer show in the active event view and are no longer visible in the accessevent table within the Database.   However, invalid events continue to work normally. 

Product Line

Andover Continuum

Environment

  • Access Events
  • Logging

Cause

An incomplete object may have been added to the Continuum Database recently that is interfering with queries running against that database.

Resolution

Try the following steps to troubleshoot the issue

  1. Does the issue happen on multiple CyberStations?
  2. Ensure all the event types are selected in the active event view that is being used on the door(s).
  3. Perform a CyberStation Teach

    It is best to contact PSS and work with them at this point with the following procedures.
     
  4. Verify that access events are being sent from the controller to the CyberStation using Wireshark.
  5. Verify that the issue follows the Database by loading the database in a test environment to see if the issue still happens. 
  6. On the TEST database, use SQL Management Studio:
    1.  SQL Query: set acdbversion=0  (execute the query)
    2.  Update database: launch Database Initialization Server/Stand Alone
  7. Enter sa password and update database
  8. Restore database or locate incomplete object
    1. The quickest fix would be to revert to a known good database. Once restored, the events in the controllers would be downloaded to the database.
    2. Finding the object in the database that has caused the issue can be very challenging. Check to see if there was a controller recently added and if the issue began to happen after that. If for some reason a controller had been added and it wasn't completed normally then it could cause this issue.
    3. Check to see if there is a controller in the InfinityController table with an objectidhi or objectidlo with a zero value. If so, delete that controller and see if the valid access events start coming in.

It may also be necessary to use the SQL profiler to view the entries that are being made into the database. See the following link  below for  more information. http://msdn.microsoft.com/en-us/library/ms181091.aspx

 

NOTE:

Turning off the Primary and Secondary Access Server will cause the access events to buffer in the controllers, so that these events will be inserted into the database once valid access event logging has been restored. After turning off the primary and secondary, check the Access Log infinity system variable on the controllers. If they are non zero values, then events are buffering. There is a limited amount of access events that can be stored in the controllers before loss of data occurs.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 7059
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of