Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,845
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 7
    • 8
    • 9
    • …
    • 508
  • Next »

Replacement of Satchwell MZF 3-Port Flanged Valve Body due to obsolescence.

Issue Satchwell MZF 3-Port Flanged Valve Body requires replacement. Product Line Field Devices Environment Satchwell 3-Port Plug and Seat Flanged Valve Body MZF MZF3729 MZF3779 MZF3854 MZF3904 MZF3958 Cause Obsolescence of Satchwell MZF 3-Port Flanged Valve Body Resolution A number of alternative Schneider Electric 3-Port Flanged Valve Bodies are available to replace existing Satchwell MZF 3-Port Flanged Valve Bodies. Suggestion 1 Replace Satchwell MZF 3-Port Flanged Valve Body with S-E VG311F 3-Port Flanged Valve Body of appropriate size N.B. Existing Satchwell Actuator installed on MZF 3-Port Flanged Valve Body may be retained for installation on replacement Schneider Electric 3-Port Flanged Valve Body. In such instances a Schneider Electric L9TVG Linkage Kit will additionally be required. Alternatively an Actuator from the Schneider Electric range of Actuators may be installed on the VG311F 3-Port Flanged Valve Body, in which case no additional Linkage Kit will be required. Suggestion 2 Replace Satchwell MZF 3-Port Flanged Valve Body with S-E V321 3-Port Flanged Valve Body of appropriate size N.B. Existing Satchwell Actuator installed on MZF 3-Port Flanged Valve Body may be retained for installation on replacement Schneider Electric 3-Port Flanged Valve Body. In such instances a Schneider Electric L8TV Linkage Kit will additionally be required. Alternatively an Actuator from the Schneider Electric range of Actuators may be installed on the V321 3-Port Flanged Valve Body, in which case no additional Linkage Kit will be required. IMPORTANT NOTE It should also be noted that the face to face dimensions both of the Schneider Electric VG311F and V321 3-Port Flanged Valve Bodies differ to that of the Satchwell MZF 3-Port Flanged Valve Body Similarly, the centre line to bottom of third port dimensions both of the Schneider Electric VG311F and V321 3-Port Flanged Valve Bodies differ to that of the Satchwell MZF 3-Port Flanged Valve Body As a result alterations to the pipework connected to the MZF 3-Port Flanged Valve Body will be required. Details of the Satchwell MZF 3-Port Flanged Valve Body may be viewed here. Details of the Schneider Electric VG311F 3-Port Flanged Valve Body may be viewed here. Details of the Schneider Electric V321 3-Port Flanged Valve Body may be viewed here. Details of the Schneider Electric L9TVG Linkage Kit may be viewed here. Details of the Schneider Electric L8TV Linkage Kit may be viewed here. 
View full article
Picard Product_Support
‎2018-09-10 08:52 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-22 06:52 PM

Labels:
  • Field Devices
7488 Views

Documentation on the MSC-MPC Microsmart controller and its associated modules

Issue Documentation on the MSC-MPC Microsmart controller and its associated modules. Product Line TAC I/A Series Environment Microsmart controller MSC-MPC MPC-4AO MPC-8AI MPC-2PO MPC-SSR MPC-4CO Cause Obsolete controller Resolution Click here to view the installation instructions on the MSC-MPC. Click each associated module part number below to view its installation instructions: MPC-4AO MPC-8AI MPC-2PO MPC-SSR MPC-4CO
View full article
Picard Product_Support
‎2018-09-10 03:48 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-24 07:50 AM

Labels:
  • TAC IA Series
7417 Views

Modbus basics

Issue Understanding and Troubleshooting Modbus Product Line EcoStruxure Building Operation, TAC IA Series, Other  Environment All Modbus environments. Cause Modicon first introduced Modbus in 1979. Modbus is an open standard,and it is the most widely used in the industrial environment. Modbus is publicly available and,due to its simplicity, many manufacturers use Modbus as a solution for integration in their own products. Many commercial products and systems support the Modbus RTU and Modbus TCP protocols. For further information, visit the Modbus website at http://www.modbus.org. Resolution For a brief understanding on Modbus and how to troubleshoot Modbus, refer to the Modbus Troubleshooting PDF
View full article
Picard Product_Support
‎2018-09-10 05:07 AM

Last Updated: Lt. Commander mroche1 Lt. Commander ‎2021-08-23 02:28 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC Vista
7360 Views

Cannot edit the graphic because the Graphics Editor has lost connection with the server

Issue When attempting to edit a graphic on an SBO/EBO ES or AS the Graphics Editor, Function Block Editor or Script Editor reports it has lost connection. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server Premium Cause A second instance of the workstation is running on the same computer The firewall is blocking the connection. The password was recently changed during the same session Workstation is connected via HTTPS but there is no valid certificate Resolution Solution 1 If using Remote Desktop (RDP) to access the SBO/EBO ES remotely, a second instance of the workstation could be initiated. Close the workstation on both the remote connection and at the SBO/EBO ES. Then open the workstation either at the SBO/EBO ES or via remote connection, not both.   Solution 2 Check if the firewall has been enabled while logged in to the SBO/EBO ES or AS, and disable the firewall Here is an example for McAfee   Solution 3 Make sure the network information (such as gateway) for the PC is entered correctly.   Solution 4 If you just changed the password of the logged in user, log out and in again   Solution 5 Workstation is connected via HTTPS but there is no valid certificate. Ensure that certificates are installed and trusted on the workstation/server so that no certificate warnings are received or use HTTP to connect to the server.   Solution 6 Update the Certificate Revocation List as described in First time a TGML graphic is opened after logging in it takes a long time for the graphic to load.
View full article
Picard Product_Support
‎2018-09-11 07:51 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-13 05:17 PM

Labels:
  • EcoStruxure Building Operation
7374 Views

StruxureWare Building Operation LNS plug-in support

Issue LNS plug-ins are needed in order to configure certain application specific controllers. Product Line EcoStruxure Building Operation Environment Workstation Open LNS Server Cause Many application specific controllers can be configured through Workstation but this can be very time consuming. Starting with Version 1.4.0, SmartStruxure is now able to support LNS plug-ins. Key points and features Click SBO v1.4 Activation Key for OpenLNS Server - SmartStruxure solution - PA-00285 to download the StruxureWare Building Operation v1.4 - Activation key for OpenLNS Server product announcement. Echelon OpenLNS Server must be installed on the computer that plug-ins will be used. LNS Server plug-ins can be used at the workstation to configure TAC Xenta devices using TAC STR 350 plug-in 5.1.9 or later. (earlier versions won't work) LNS Server plug-ins can be used at the workstation to configure TAC Xenta devices using TAC 100 plug-in 5.1.9 or later. (earlier versions won't work) LNS Server plug-ins can be used at the workstation to configure third party LON devices. The LNS plug-in capability will only work if the device does not require to be online to configure. If the manufacturer's plug-in requires active communication with the device then the plug-in implementation will not work. StruxureWare Building Operation database is automatically updated to any changes created with the plug-in. Resolution For LNS plug-ins to work in SmartStruxure, Echelon OpenLNS Server must be purchased and installed on the computer where plug-ins will be used. Purchasing Echelon OpenLNS Server An activation key must be purchased in order to install Echelon OpenLNS Server. The activation key is available to purchase through Schneider Electric using the part number SXWSWLNSX00001. The activation key can be purchased through standard product ordering procedures. After ordering, the activation key will be sent to you via email within a few days. Installing Echelon OpenLNS Server WARNING: You can not install OpenLNS Server on the same computer as TurboLNS without upgrading Turbo to Open. You will now be converting any TurboLNS databases to OpenLNS if they are opened on this computer. Once you have purchased the OpenLNS activation key and received it via email from Schneider Electric then you can now install Echelon OpenLNS. Double click on the executable to start the OpenLNS install wizard. Click Next. Select 'I accept the terms in the license agreement' and click Next. Fill out the information and enter you activation key. Click Next. Click Install. Click Next. Click Finish. NOTE - At step 7 above, if the PC is not connected to the internet, the registration may require an email to be send manually to Echelon to register the licence code.  Uninstalling Echelon OpenLNS Server Make sure you reference the OpenLNS Server License Guide here for information on how to return the OpenLNS license in order to use it again.   Registering LNS Plug-ins Note: Before registering LNS plug-ins, they must be installed on the computer first. If working with TAC Vista Xenta 100 and TAC STR 350 controllers, the plug-ins must be version 5.1.9 or greater. ZBuilder is included in the TAC Vista 100 download. These can be downloaded off of the Extranet in the same place as the SmartStruxure software. See LNS plugins for SmartStruxure 1.4 are not included in the release, but downloaded separately for more information. In SmartStruxure Workstation, go to the Control Panel. Click on 'LNS Plug-in Registration'. In the 'Available LNS Plug-ins' field, select the plug-ins you want to register and then click the right arrow to move to the 'Registered LNS Plug-ins" field. Click the save icon on the System tab. Note: If registering the TAC Xenta 100 plug-in, you will be prompted to select the devices you want to register. Then click OK.   Using the LNS Plug-ins Note: All changes made in the LNS plug-ins are offline configuration changes. The LNS plug-in support in SmartStruxure will not support devices that are required to be online for plug-in use.  Right click on the controller, click Configure... The LNS server is checked for a matching device template and the current device configuration is saved to the LNS server. Click Next. Double click on the plug-in listed in the window. This will launch the LNS plug-in. Make configuration changes to the controller and then save or exit the plug-in. Click Next. Click Next. The configuration changes that have been made will be listed in the window while they are being saved to the LNS server. Click Finish. Now the configuration changes that were made in the LNS server need to be downloaded to the controller. Right click on the controller in Workstation and select 'Download device configuration'.
View full article
Picard Product_Support
‎2018-09-11 12:53 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:37 PM

Labels:
  • EcoStruxure Building Operation
7378 Views

Capturing a photo using "Logitech HD Pro Webcam C920"

Issue Blank window while capturing a photo using "Logitech HD Pro Webcam C920". Product Line EcoStruxure Security Expert Environment Security Expert Cause While capturing a user photo using "Logitech HD Pro Webcam C920", it shows up as an image source (in the drop-down along with Topaz). When selected however, the screen is blank. Resolution With this webcam, you need LWS software by Logitech installed on your machine. G Hub has replaced LWS however it seems like G Hub is not currently functional with the integration. Find more information about the  "LWS280" driver HERE.  The driver can be downloaded from the attachment.
View full article
Commander Sampath_Konda Commander
‎2019-11-14 08:13 AM

Last Updated: Kirk AdamSteele Kirk ‎2023-06-21 11:54 PM

Labels:
  • EcoStruxure Security Expert
7289 Views

STR-150 Manual Configuration

Issue How to change the STR-150 temperature display, setpoint adjustment range, etc. Product Line TAC Vista Environment STR-150 STR Sensor Cause The communication between the STR-150 and the TAC Xenta 121/122 device is one way, space temperature and setpoints are sent from the sensor to the controller. Therefore some STR-150 functions (for example, the setpoint adjustment) can not be configured though Zbuilder, but needs to be done manually in the STR 150 device. Resolution Buttons on the thermostat: Increase Button Decrease Button Bypass button Fan button Wrench symbol   Steps of changing the STR-150 configuration are listed below: Enter Configuration: Push the fan and bypass button simultaneously for 2 seconds to enter P0 In P0, hold down the bypass button and push the fan button three times to enter configuration mode. NOTE: the wrench symbol is lit when the STR-150 is in configuration mode.   In configuration mode: Press the fan button repeatedly until reaches desired parameters (refer to the configuration table below). NOTE: the two digits farthest to the left on the display show the parameters, while the two digits farthest to the right show the value Use increase button or decrease button to change the value.   Exit configuration mode: Push the fan and bypass button simultaneously for 2 seconds. Or, the timeout will exit configuration mode if idle.   Configuration Options: Parameter Function Value/Range Default value P0 Software Version - - P1 °C or °F temperature display 1=°C, 2=°F 1=°C P2 Reference temperature (Reftemp) 15-30°C / 60-90°F 22°C / 72°F P3 Setpoint or room temp. 1=Setpt, 2=Room 1=Setpt P4 Timeout 5-90 seconds 10 seconds P5 Fan Settings 0=No fan 1=On/Off fan 2=Two-speed fan 3=Three-speed fan 3=Three-speed fan P6 Room temperature and setpoint display resolution 0.1 or 0.5 °C 0.2 or 1.0 °F 0.5 °C or 0.2 °F P7 Max adjustable setpoint span above or below Reftemp (P2). +/- 0 - +/- 5°C +/- 0 - +/- 10°F +/- 3° or +/- 6°F P8 Bypass button and occupancy indication When = 2, no bypass command is sent  to the controller 1= Symbol on, off Or flashing 2=Symbol always off Default 1=on, off Or flashing P9 Setpoint as Absolute or Offset value 1=Absolute 2=Offset 1=Absolute   Click here to read STR-150 user's manual.
View full article
Picard Product_Support
‎2018-09-07 06:20 AM

Last Updated: Kirk MikaelKrantz Kirk ‎2022-10-12 01:00 AM

Labels:
  • TAC Vista
7230 Views

Setup External Log Storage using MSSQL

Issue How to setup and configure External Log Storage in EcoStruxure Building Operation (EBO) when using Microsoft SQL Server as external log storage. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Building Operation Enterprise Server Building Operation Enterprise Central Cause You use External Log Storage feature to store historical data from EcoStruxure BMS. The amount of stored data is limited only by the equipment you use, and not by the capacities of the feature. The External Log Storage feature uses an external database administered by either a combination of TimescaleDB and PostgreSQL software, or Microsoft SQL server. Resolution Please see the below video demonstrating how to: Create a database and user account in Microsoft SQL (MSSQL) Server using Microsoft Server Management Studio. Configure the External Log storage connection between EBO and MSSQL server in EBO. Also please note the following: In the video the "Host address" in EBO is set to the IP address or DNS name\SQLserver instance like this: localhost\SQLEXPRESS. If the SQL server is not located on the same computer as the EBO server only use the IP address or DNS name and no instance on "Host address". The video demonstrates using the version 5 script when configuring the database in the MSSQL server, search External Log Storage - MSSQL Installation Script  to download the appropriate EBO version script. For the example query to manage user permissions download User Rights Script or see attached script.txt. If using MSSQL Express rather than the full MSSQL version it may be necessary to consult External log storage not working with SQL Server Express.    
View full article
Janeway Jonas_Brissman Janeway
‎2023-03-02 05:58 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-10-11 05:47 AM

Labels:
  • EcoStruxure Building Operation
7276 Views

ISO certificate for Schneider Electric Industries SAS Building Business

Issue ISO 9001 certificate for Schneider Electric Buildings Product Line EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices,Other, TAC INET, TAC Vista Environment Management Certification Certificate for the Design and Manufacture of Building Management System Controllers, Devices and Electronic Systems Cause ISO9001 certificates are sometimes requested for different projects. Resolution Download the ISO 9001:2015 certificate here.
View full article
Picard Product_Support
‎2018-09-07 02:09 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-30 10:52 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • TAC INET
  • TAC Vista
7294 Views

BACnet device can't be discovered due to duplicate name

Issue BACnet device can't be discovered but instead shows up under the 'Unconfigured devices' in the server's hardware folder. Product Line EcoStruxure Building Operation Environment WorkStation Enterprise Server - ES Automation Server - AS Cause A BACnet device name must be unique. Devices with duplicate BACnet names can't be discovered. In the screen shot below a device by the name AbesbCX already exists under Network1, when performing a device discovery on Network1 a second device with the same name is found, Since StruxureWare already has a device with the same name it adds the device to the list of unconfigurable devices. NOTE: “The <<N>> means the device was discovered on a directly connected network (such as the local IP network, or a directly connected MSTP bus).  The 2 indicates it was “port” 2, (port numbers are really an internal detail) The server's Trace Log shows the following information, which includes the device's ID. The entry gives the reason as duplicate device name. Resolution 1.8.1 and above BACnet device name duplication is allowed, the duplicates will still land in the unconfigured folder and the system alarm will be generated BUT you can drag the duplicate device from the unconfigured folder to the desired network. When finished, manually delete the device from the unconfigured/non-conformant folder. Alternatively, you can also  warm start the server to force the unconfigured/non-conformant devices list to be updated. Note that the devices with duplicate names will still stay in the unconfigured/non-conformant folder until the name conflict is resolved. 1.7.2 and below A workaround is to create the device manually and specify a BACnet name during the create process. When manually creating the device you need to know the Device ID, you can get the id from the information in the trace log as shown above. SmartStruxure will send a message to the device to change its name to the specified BACnet name. The entry in the unconfigured devices folder should automatically update after a few minutes, you can also re-start the server to force the unconfigured devices list to be updated, the entry for AbesBCX should be gone now that the devices has been manually configured.
View full article
Picard Product_Support
‎2018-09-07 08:51 AM

Labels:
  • EcoStruxure Building Operation
7193 Views

How to create custom reports in Building Operation WebReports

Issue How to create custom reports in Building Operation WebReports Product Line EcoStruxure Building Operation Environment Building Operation WebReports up to version 3.2.  Note: WebReports is no longer included in Building Operation 2022 and above. Cause Custom reports are typically created by modifying another report and then saving these changes. Typically used are the factory-supplied reports as the base for a new report then enter the filtering criteria that are required to be used in the new report. Assign a unique name to the custom report and save the new report as a dashboard or prompted report.  There may be a need to create a report not based on any of the standard reports provided in these Report Packs, this article covers this process. Resolution To create a non-factory-supplied report within WebReports it is necessary to use an editor.  Since WebReports use Microsoft Reporting Services it is recommended to download the Microsoft SQL Server 2008 R2 Report Builder 3.0 or MS MSQL Server 2012 Report Builder.  This is a free tool provided by Microsoft that provides an intuitive report authoring environment for business and power users. This download provides a stand-alone installer for Report Builder 3.0.  Please note that Product Support does NOT provide support for Report Builder.  After downloading and installing the Report Builder application, the steps are as follows:  Each of these steps is also located on the Building Management System WebHelp site, a link for each of these steps is provided for additional reference and guidance. Start Report Builder and create a new blank report, see Creating a Basic Report for the steps.  After Creating the report create a data source that connects this report to StruxureWareReportsDB, see Creating a Data Source for these steps Then create the Data set, so add to the report which tables, views, stored procedures, and fields from the StruxureWareReportsDB are required to use in your report, see Creating a Dataset for these steps. This data can then be added to the custom report as required.  See Setting Up a Report for an example of setting up a report. See Adding an Image to a Report  on how to add images to the report  The new report now must be deployed to the Reports Server where it can be accessible to WebReports. To complete this procedure use SQL Server Reporting Services Report Manager. See Deploying a New Report to the Reports Server to view these steps in detail.  Finally, the report must be synchronized in WebReports to be deployed and therefore appear in the WebReports Reports Tree. Use WebReports with a Web browser to complete this procedure.  See Synchronizing WebReports with a New Report for the steps to complete this. Once all these steps have been completed successfully the new Report should be visible in the tree - the placement of these reports will depend on where they have been uploaded in step 5 above.  See the image below:
View full article
Picard Product_Support
‎2018-09-06 11:58 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-06-07 12:00 AM

Labels:
  • EcoStruxure Building Operation
7169 Views

Installing I/NET Seven on a 64-bit operating system

Issue Initialization errors when starting I/NET Seven 2.42 or higher Error: "You must install an instance of SQL 2008R2 (64bit) before completing the INET install" Product Line TAC INET Environment I/NET Seven 2.42 Windows Server 2008 64-bit Windows 7 64-bit SQL 2008 64-bit Windows 8 Cause I/NET 64-bit requires specific installation process in order to function on a 64-bit PC Resolution Installing SQL Download SQL2008 R2 Express 64 bit (SQLEXPR_x64_ENU.exe) from this location: http://www.microsoft.com/en-us/download/details.aspx?id=30438 Run SQLEXPR_x64_ENU.exe In the left hand section, select Installation In the Right and section, select New SQL Server stand-alone installation of add features to an existing installation. At the "Setup Support Rules" screen select OK At the "Product Key" screen, select Next At the "License Terms" screen, check accept and select "Next" At the "Setup Support Files" screen, select Install At the "Setup Support Rules" screen, select Next At the "Feature Selection" screen select: Database Engine Services, SQL Server Replication, Management Tools - Basic (If Present) and SQL Client Connectivity SDK. Leave the Shared feature directory as default. At the "Instance Configuration" screen, select the Default instance option, accept the default Instance ID, accept the Instance root directory default settings and select next. At the "Disk Space Requirements" screen, select Next At the "Server Configuration" screen, under SQL Server Database Engine set the Account name to NT AUTHORITY/SYSTEM, leave the password field blanks, and set the startup type to automatic. Under SQL Server Browser Service, set the Startup Type to Automatic At the Database Engine Configuration screen, set the Authentication Mode to "Mixed Mode", Define a strong password (example: @sql2008), in the Specify SQL Server administrators section click "Add Current User". Select Next. At the "Error and Usage Reporting" screen, select Next At the "Installation Rules" screen, select Next At the "Ready to Install" screen, select Install At the Installation Progress screen, when the setup process is complete, select Next At the "Complete" screen, select Close. SQL Configuration: In the Windows Start Menu, launch the SQL Server Configuration Manager In the Left hand section of the window, highlight SQL Server Services Verify that SQL Server Browser and SQL Server are Running In the left hand section of the window, expand SQL Server Network Configuration and highlight Protocols for MSSQLSERVER Enable Named pipes and TCP/IP Close the SQL Server Configuration Manager Restart the PC Installing SQL Server 2005 Backward Compatibility On the I/NET 2.42 or higher installation CD, look in Support\SQLBCM_64Bit and launch the SQLServer2005_BC_x64.msi file Follow all the prompts on each screen and accept all defaults. Install I/NET Seven 2.42 or higher Install I/NET Seven 2.42 or higher using the installation CD Follow prompts and use defaults When prompted for the SQL password, select "Windows Authentication" Restart the PC Open I/NET Configuration through the start menu. Modify the default Config profile or create a new profile. Close I/NET Configuration Start I/NET NOTE: If error occurs during SQL installation stating invoke or begin invoke failed, follow instructions at this link: http://support.microsoft.com/kb/975055 UPDATE: SQL2008 SP1 prevents the invoke failed error. It can be installed with the same instructions as above. Download it at this link: http://www.microsoft.com/en-us/download/details.aspx?id=25052
View full article
Picard Product_Support
‎2018-09-10 12:28 PM

Last Updated: Administrator DavidFisher Administrator ‎2023-09-11 01:49 AM

Labels:
  • TAC INET
7174 Views

ODBC Connection failure

Issue Datacard ID Works gives an ODBC error. Examples shown below: Microsoft SQL Server Login Connection failed: SQLState: '01000' SQL Server Error: 53 [Microsoft][ODBC SQL Server Driver][DBNETLIB]ConnectionOpen (Connect()). Connection failed: SQLState: '08001' SQL Server Error: 17 [Microsoft][ODBC SQL Server Driver][DBNETLIB]SQL Server does not exist or access denied. Data Source Error Data source name not found and no default driver specified State:IM002,Native:0,Origin:[Microsoft][ODBC Driver Manager] Product Line TAC INET Environment I/NET Seven all versions Datacard ID Works video badging software Cause The "IDWorksView" driver uses a ODBC Connection to allow the ID Works Software to communicate to the I/NET SQL Database. If for some reason this ODBC gets corrupted, you will get an error anytime you try to run the ID Works software. Resolution Go to Start > Control Panel > Administrative Tools Select Data Sources (ODBC) Select the System DSN tab Highlight Seven ODBC SQL Server in the list and hit the Configure button Make sure the settings are as follows: Name: Seven ODBC Description: ODBC Connection for I/NET Seven Server: (local) Hit Next Before you actually login to this window, choose the Client Configuration button and make sure these settings are correct. Network libraries: TCP/IP Connection parameters: Dynamically determine port Note that the InetThirdParty password changed in I/NET Seven rev 2.4X to PassInetDb3p_SE. If you try to use this in this process it will fail on you. Instead of using the InetThirdParty and the password here, use the Username and Password that you use for the DbCreateEditor. Then select the Next button. Verify the settings below, then hit Next: Change the default database to: InetDb Verify the settings below, then hit Finish Perform translation for character data
View full article
Picard Product_Support
‎2018-09-10 05:09 AM

Labels:
  • TAC INET
7124 Views

License Features list for version 3.0 and 4.0 Product names

Issue Is there a quick reference I can search to find out what features are included in a particular license When manually adding my Product during offline embedded license workflow, how do I know which Features is included and in what quantity?  Product Line EcoStruxure Building Operation Environment Building Operation EBO 2022 v4.03 and lower  Embedded Offline Licensing Offline Activation of Licenses Workflow Cause Currently, no information lists features for each Product name listed in the Part Number Summary for EBO 2022.  A documentation defect (QC 49762) has been raised, which should resolve this.  This article has been created to assist somewhat during this process while waiting for this to be corrected.  The recommendation, if possible, is to perform license activation online to avoid having to enter this detail.   Resolution Important Note: This information is no longer valid for EBO 2022 (Maintenance Release 4.0.4) and EBO 2023 and greater.  The details below are still provided for reference only and are not needed for these later versions.   Attached are two documents that provide version 3.0 and 4.0 License details.  The documents contain all searchable details, including: Product Name Features Part Numbers     Additional details required for Device Administrator "Feature Name" offline entry:   SpaceLogic Server license details Feature Name (seen in Device Admin) License name (seen in Features document) Description / Comments Automation Server server.as.base   SmartDrivers smartdriver.license   SNMP Notifications server.alarms.snmp   Personal Dashboard client.dashboard   TimescaleDB server.timescale   MQTT Publish/Subscribe server.mqtt.rw Enables EBO, as MQTT Client, to publish data on an MQTT Broker and to subscribe to the same data. Serial Modbus server.modbus.rtu Allows SmartX server serial communication - Modbus RTU Serial MS/TP server.bacnet.mstp Allows SmartX server serial communication - MSTP ES Connection server.connect.to.es Allows SmartX server to be hosted by an Enterprise Server Server I/O server.io Allows SmartX server to use IO Field Devices server.device.as Allows SmartX server to host one field device SAML Authentication server.as.auth.saml   Zoning client.zoning Enables use of zoning tools BACnet IP server.bacnet.ip Allows SmartX Server to communicate using BACnet IP Software Assurance software.assurance         Feature Name (Automatically included with bundle licenses)   client.webstation Allows Webstation to log on to an AS   server.cloud.customer Cloud connectivity - Checked by Cloud SMS (Production)   server.as.scalable Included in the license that allows SpaceLogic servers upgrades. i.e. Standalone to Standard etc.   Example: Product Name: ASP-NL Bundle upgrade - Full to ASP Full    Search the document for the product name in the attached document. In this case, the version 4 document.  Below is the result seen in the document: From this, the associated Features and Quantity are shown. In Device Administrator, then add the respective features and quantities when adding the product manually to the Entitlement. Use the above table to correlate between Feature Name and License Name. The example shown below:  
View full article
Guinan RobertAndriolo Guinan
‎2022-06-08 08:57 PM

Labels:
  • EcoStruxure Building Operation
7160 Views

What is the recommended BACnet Network ID number scheme to be used for Automation Server's Primary IP (eth1)

Issue Many campuses are configured with 1 BACnet Network ID number for Primary IP that is unique per building whether or not they are in the same IP subnet or multiple (with BBMDs). Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Cause When reviewing the Technical Reference Guide and searching "BACnet and IP Routing", it does not clearly explain the configuration and it also does not extend to multi-building systems using BBMDs. Resolution BACnet network numbers are assigned at BACnet routers, with a Range of 1-65,534 (where 65535 is reserved for broadcasts). Routed networks are assigned unique network numbers and can only have 1 router per network. Routed networks are usually BACnet MSTP, BACnet Ethernet, and Secondary IP networks. Standard practice is to have primary IP networks consisting of IP routers/devices in the same IP subnet or across multiple IP subnets joined by a BBMD and/or foreign device configuration uses the default BACnet network number 1.
View full article
Commander JonGreen Commander
‎2020-09-09 11:54 AM

Last Updated: Sisko DavidChild Sisko ‎2022-02-10 07:43 AM

Labels:
  • EcoStruxure Building Operation
7186 Views

Changing the IP address of Automation Server

Issue How to change the IP address of the Automation Server and ensure proper communication. Product Line EcoStruxure Building Operation Environment Enterprise Server Automation Server Building Operation Device Administrator Building Operation Workstation Cause At times the IP address information for an Automation Server must be changed after being added to an Enterprise Server to accommodate changes in IP network design, correction of incorrect data, or any other reason. Changing the IP address needs to be done in the proper method to avoid artifacts and confusion after the change. Resolution To avoid complications, follow this process to modify the IP address of an Automation Server that is already communicating with an Enterprise Server. In the Building Operation Device Administrator connect the AS controller via USB or IP.  WebHelp Topic Connect to SmartX Servers Right-click on the AS and select Network Settings Modify the IP address settings to the new values Additionally, this can be changed through PuTTY with the "setip" command. Power Cycle the Automation Server (If a power cycle is not completed the AS will still have invalid data for network settings despite the physical network interface running with the new settings) Start Building Operation Workstation and log in to the Enterprise Server Select the Enterprise Server and open the Communication Tab Highlight the Automation Server that needs to be changed and modify the address field for the IP address of the device. (The Communications settings tab is enabled by selecting the Show/Hide tick icon). Click the Save button The Enterprise Server should now automatically establish communication with the AS, but if you want to speed this process you can right-click the Enterprise Server and select the "Advanced\Repair Server Communication" option. IMPORTANT: As of 1.41 if the IP address is changed on a server that is configured with a BACnet interface, the IP address and possibly the broadcast address of the IP Network under the BACnet interface must be updated manually. (see below)
View full article
Picard Product_Support
‎2018-09-10 11:32 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-11-22 06:37 PM

Labels:
  • EcoStruxure Building Operation
7085 Views

What versions of Visio are required for WorkPlace Tech?

Issue What versions of Visio are required for WorkPlace Tech? Product Line TAC IA Series Environment WorkPlace Tech Microsoft Office Visio (32-bit version only on WPT versions 5.10 and earlier ) Microsoft Office Visio (64-bit version only on WPT versions 5.11 and later) Cause Software requirement - Microsoft Office Visio must be installed on the computer before beginning the installation of WorkPlace Tech. Resolution Below is a list of the WorkPlace Tech revisions and compatible Microsoft Visio versions.  The "Pro" versions are not required.  The "standard" versions of Microsoft Visio are typically recommended.  Only the 32-bit versions of Visio are supported in WPT 5.10 and earlier and only 64-bit versions are supported in WPT 5.11 and later. WPT Visio 3.1 Visio 5 Technical Plus 3.2 2000 SP1 4.0 2000 SP1, 2002 SP1 5.0 2002 SP1, 2003 SP1 5.1 2002 SP1, 2003 SP1 5.2 2002 SP2, 2003 SP1 or SP2 5.3 2002 SP2, 2003 SP1 or SP2 5.4 2002 SP2, 2003 SP1 or SP2 5.5 2002 SP2, 2003 SP1 or SP2 5.6 2002 SP2, 2003 SP1 or SP2 5.7 2003 SP3, 2007 SP1 5.8.0 to 5.8.5 ** 2003 SP3, 2007 SP1 or SP2, 2010 SP1 5.8.6 2007 SP1 or SP2, 2010 SP1 5.8.7 2007 SP3, 2010 SP2 5.9.1 to 5.9.4 2010 SP2, 2013 SP1, 2016 5.10.0 to 5.10.4 2016, 2019, 2021 Office (Visio) 365 Subscription Plans 5.11 2019 64-bit, 2021 64-bit, Office (Visio) 365 Subscription Plans 64-bit ** Microsoft Office Visio 2003 with Service Pack 3 (officially supported for WorkPlace Tech 5.8.0 and 5.8.1, no known issues with 5.8.2 through 5.8.5)
View full article
Picard Product_Support
‎2020-12-15 09:38 AM

Last Updated: Administrator CraigEl Administrator ‎2024-07-08 04:48 PM

Labels:
  • TAC IA Series
7028 Views

The difference between getTarget() and getCurrentTarget() in TGML Scripting

Issue Every item shown in the Objects window of the TGML editor can be considered a Node. In the figure shown below, this relatively simple TGML page has 14 nodes. Nodes are hierarchical with parent and children nodes. One important concept when scripting in TGML is finding the desired node. Examples of this are: Changing the color of a rectangle when a bound signal is offline Writing a new value to a text box every time the database value updates Opening a new page when the user left clicks on a component Product Line EcoStruxure Building Operation, TAC Vista Environment StruxureWare Building Operation TAC Vista TGML Graphics Editor Cause Within a script, there are two functions that will pinpoint a specific node, but have very different applications. These are: getTarget() getCurrentTarget() An example function of how to use these functions is: function click(evt){ target = evt.getTarget(); } Resolution getTarget() - returns where an event is coming from getCurrentTarget() - returns the parent of the script Both examples below chart the differences between the two functions using the screen capture below. If the bind object in the figure above changes its value, here is what getTarget() and getCurrentTarget() would each return if they were a part of each script (A, B, C). Script getTarget() getCurrentTarget() A Bind Component B Bind Rectangle C Bind Bind If the user clicks on the rectangle in the figure above, here is what getTarget() and getCurrentTarget() would each return if they were a part of each script (A, B, C). Script getTarget() getCurrentTarget() A Rectangle Component B Rectangle Rectangle C N/A N/A Also check out the JavaScript Essentials - Programs and Statements Quick-Help video on the Exchange.
View full article
Picard Product_Support
‎2018-09-11 03:05 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:34 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
7026 Views

Where can I obtain standard Plain English example functions?

Issue Where are example Plain English programs and functions stored for typical BMS applications? Product Line Andover Continuum Environment Plain English (PE) Functions and programs. ACSM, PID, Optimiser, ISM, First Aid. Standards Bacnet Optimiser Cause It is always easier to write your Plain English programs starting from documented examples rather than a blank page. What is available? Resolution The following link is to a .zip file containing various BMS standard modules originally developed by the UK Application engineers for Infinity SX8000 and were known as the Infinity Standard Modules (ISM's), they were then updated to Andover Controls Standard Modules (ACSM's) for Continuum. These modules are example functions or building blocks that can by used globally by application engineers to provide the control and monitoring appropriate for your own buildings. Link: Click here. In addition to these functions other examples are in the online help for the corresponding Plain English keywords, and other applications can be found on the Forums; see Sample PE functions and programs for further details. For Smart Sensor examples see Example programs for Smart Sensors TTS-SD-LCD-1 and TTS-SD-LED-1 for details. For example Security programs see the Download Center link, Click Here.
View full article
Picard Product_Support
‎2018-09-10 11:48 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:42 PM

Labels:
  • Andover Continuum
7006 Views

Replacement of Satchwell AR Series 7 Rotary Actuator by Schneider Electric MD Series Rotary Actuator due to obsolescence. (Actuator Wiring)

Issue Satchwell AR Series 7 Rotary Actuator requires replacement Product Line Field Devices Environment Satchwell AR Series 7 Rotary Actuators installed on Air Dampers, Satchwell MB Series or MBF Series Rotary Shoe Valve Bodies. Actuator types :- ARE ARM ARX ARMS Cause Obsolescence of Satchwell AR Series 7 Rotary Actuators Resolution Replace Satchwell AR Series 7 Rotary Actuators with appropriate Schneider Electric MD Series Rotary Actuators and wire as follows :- Satchwell AR Series 7 Rotary Actuators installed on Air Dampers. ARE ARE Series 7 Wire Number 2 = MD20A-24 Wire Number 2 ARE Series 7 Wire Number 3 = MD20A-24 Wire Number 3 ARE Series 7 Wire Number 1 = MD20A-24 Wire Number 1 ARE Series 7 Wire Number 5 = MD20A-24 Wire Number 5 ARX ARX Series 7 Wire Number 3 = MD20B-24 Wire Number 3 ARX Series 7 Wire Number 2 = MD20B-24 Wire Number 2 ARX Series 7 Wire Number 1 = MD20B-24 Wire Number 1 ARM ARM Series 7 Wire Number 3 = MD20B-230 Wire Number 3 ARM Series 7 Wire Number 2 = MD20B-230 Wire Number 2 ARM Series 7 Wire Number 1 = MD20B-230 Wire Number 1 ARM Series 7 Wire EARTH = MD20B-230 NO EARTH REQUIRED ARMS ARMS Series 76021Term 3 (Open) = MD10SR-TS Blue G ARMS Series 7602 Term 2 (L1) = MD10SR-TS Not used *1 ARMS Series 7602 Term 1 (N) = MD10SR-TS Brown GO ARMS Series 7602 Wire EARTH = MD10SR-TS NO EARTH REQUIRED ARMS Series 7603 Wire Number 2 = MD10SR-T Blue G ARMS Series 7603 Wire Number 1 = MD10SR-T Brown GO ARMS Series 7604 Wire Number 2 = MD10SR-TS Blue G ARMS Series 7604 Wire Number 1 = MD10SR-TS Brown GO *1 Disconnect from the supply, label, and make safe at the supply and actuator.   N.B. Should the Satchwell AR Series 7 Actuator (not applicable to ARMS) include a wired Auxiliary Switch then the following Accessory should also be wired on the Schneider Electric MD Actuator as follows:- MD – S1 One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch AR COMMON Wire Number S1 = MD-S1 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S1 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S1 N/C contact Wire Number S2 MD – S2 Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches AR COMMON Wire Number S1 = MD-S2 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S2 N/C contact Wire Number S2 AR COMMON Wire Number S4 = MD-S2 COMMON Wire Number S4 AR N/O contact Wire Number S6 = MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Number S5 = MD-S2 N/C contact Wire Number S5   Satchwell AR Series 7 Rotary Actuators installed on Satchwell MB Series Screwed Rotary Shoe Valve Bodies. ARE ARE Series 7 Wire Number 2 = MD10A-24 Wire Number 2 ARE Series 7 Wire Number 3 = MD10A-24 Wire Number 3 ARE Series 7 Wire Number 1 = MD10A-24 Wire Number 1 ARE Series 7 Wire Number 5 = MD10A-24 Wire Number 5 ARX ARX Series 7 Wire Number 3 = MD10B-24 Wire Number 3 ARX Series 7 Wire Number 2 = MD10B-24 Wire Number 2 ARX Series 7 Wire Number 1 = MD10B-24 Wire Number 1 ARM ARM Series 7 Wire Number 3 = MD10B-230 Wire Number 3 ARM Series 7 Wire Number 2 = MD10B-230 Wire Number 2 ARM Series 7 Wire Number 1 = MD10B-230 Wire Number 1 ARM Series 7 Wire EARTH = MD10B-230 NO EARTH REQUIRED N.B. Should the Satchwell AR 7 Series Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the Schneider Electric MD Actuator as follows :- MD – S1 One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch AR COMMON Wire Number S1 = MD-S1 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S1 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S1 N/C contact Wire Number S2 MD – S2 Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches AR COMMON Wire Number S1 = MD-S2 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S2 N/C contact Wire Number S2 AR COMMON Wire Number S4 = MD-S2 COMMON Wire Number S4 AR N/O contact Wire Number S6 = MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Number S5 = MD-S2 N/C contact Wire Number S5   Satchwell AR Series 7 Rotary Actuators installed on Satchwell MBF Series Flanged Rotary Shoe Valve Bodies ARE ARE Series 7 Wire Number 2 = MD20A-24 Wire Number 2 ARE Series 7 Wire Number 3 = MD20A-24 Wire Number 3 ARE Series 7 Wire Number 1 = MD20A-24 Wire Number 1 ARE Series 7 Wire Number 5 = MD20A-24 Wire Number 5 ARX ARX Series 7 Wire Number 3 = MD20B-24 Wire Number 3 ARX Series 7 Wire Number 2 = MD20B-24 Wire Number 2 ARX Series 7 Wire Number 1 = MD20B-24 Wire Number 1 ARM ARM Series 7 Wire Number 3 = MD20B-230 Wire Number 3 ARM Series 7 Wire Number 2 = MD20B-230 Wire Number 2 ARM Series 7 Wire Number 1 = MD20B-230 Wire Number 1 ARM Series 7 Wire EARTH = MD20B-230 NO EARTH REQUIRED N.B. Should the Satchwell AR Series 7 Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the Schneider Electric MD Actuator as follows :- MD – S1 One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch AR COMMON Wire Number S1 = MD-S1 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S1 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S1 N/C contact Wire Number S2 MD – S2 Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches AR COMMON Wire Number S1 = MD-S2 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S2 N/C contact Wire Number S2 AR COMMON Wire Number S4 = MD-S2 COMMON Wire Number S4 AR N/O contact Wire Number S6 = MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Number S5 = MD-S2 N/C contact Wire Number S5   Product Information. For details of AR Series 7 ARM ARX ARE please see here For details of AR Series 7602 and 7603 please see here. For details of the MD10 SR Damper Actuator please see here. For details of MD10A please see here For details of MD10B please see here For details of MD20A please see here For details of MD20B please see here For details of MD-S1 please see here For details of MD-S2 please see here
View full article
Picard Product_Support
‎2018-09-10 12:23 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2023-09-29 02:57 AM

Labels:
  • Field Devices
7094 Views
  • « Previous
    • 1
    • …
    • 7
    • 8
    • 9
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of