Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

STR-150 Manual Configuration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • STR-150 Manual Configuration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8297 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

STR-150 Manual Configuration

Product_Support
‎2018-09-07 06:20 AM

Last Updated: ContentModerator Explorer ‎2025-09-25 02:57 AM

Issue

How to change the STR-150 temperature display, setpoint adjustment range, etc.

Product Line

TAC Vista

Environment

  • STR-150
  • STR Sensor

Cause

The communication between the STR-150 and the TAC Xenta 121/122 device is one way, space temperature and setpoints are sent from the sensor to the controller. Therefore some STR-150 functions (for example, the setpoint adjustment) can not be configured though Zbuilder, but needs to be done manually in the STR 150 device.

Resolution

Buttons on the thermostat:

Increase Button

Decrease Button

Bypass button

Fan button

Wrench symbol

 

Steps of changing the STR-150 configuration are listed below:

  1. Enter Configuration:
    1. Push the fan and bypass button simultaneously for 2 seconds to enter P0
    2. In P0, hold down the bypass button and push the fan button three times to enter configuration mode.
      NOTE: the wrench symbol is lit when the STR-150 is in configuration mode.
       
  2. In configuration mode:
    1. Press the fan button repeatedly until reaches desired parameters (refer to the configuration table below).
      NOTE: the two digits farthest to the left on the display show the parameters, while the two digits farthest to the right show the value
    2. Use increase button or decrease button to change the value.
       
  3. Exit configuration mode:
    1. Push the fan and bypass button simultaneously for 2 seconds. Or, the timeout will exit configuration mode if idle.
       

Configuration Options:

Parameter

Function

Value/Range

Default value

P0

Software Version

-

-

P1

°C or °F temperature display

1=°C, 2=°F

1=°C

P2

Reference temperature (Reftemp)

15-30°C / 60-90°F

22°C / 72°F

P3

Setpoint or room temp.

1=Setpt, 2=Room

1=Setpt

P4

Timeout

5-90 seconds

10 seconds

P5

Fan Settings

0=No fan

1=On/Off fan

2=Two-speed fan

3=Three-speed fan

3=Three-speed fan

P6

Room temperature and setpoint display resolution

0.1 or 0.5 °C

0.2 or 1.0 °F

0.5 °C or 0.2 °F

P7

Max adjustable setpoint span above or below Reftemp (P2).

+/- 0 - +/- 5°C

+/- 0 - +/- 10°F

+/- 3° or +/- 6°F

P8

Bypass button and occupancy indication When = 2, no bypass command is sent  to the controller

1= Symbol on, off

Or flashing

2=Symbol always off

Default 1=on, off

Or flashing

P9

Setpoint as Absolute or Offset value

1=Absolute
2=Offset

1=Absolute

 

Click here to read STR-150 user's manual.

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4623
  • MikaelKrantz22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore