Installing I/NET Seven on a 64-bit operating system

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Installing I/NET Seven on a 64-bit operating system
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • chris_clerc
    chris_clerc
  • Derrick_Ratliff
    Derrick_Ratliff
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7907 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Installing I/NET Seven on a 64-bit operating system

Picard Product_Support
‎2018-09-10 12:28 PM

Last Updated: Administrator DavidFisher Administrator ‎2023-09-11 01:49 AM

Issue

Initialization errors when starting I/NET Seven 2.42 or higher

Error: "You must install an instance of SQL 2008R2 (64bit) before completing the INET install"

Product Line

TAC INET

Environment

  • I/NET Seven 2.42

  • Windows Server 2008 64-bit

  • Windows 7 64-bit

  • SQL 2008 64-bit

  • Windows 8

Cause

I/NET 64-bit requires specific installation process in order to function on a 64-bit PC

Resolution

Installing SQL

  1. Download SQL2008 R2 Express 64 bit (SQLEXPR_x64_ENU.exe) from this location: http://www.microsoft.com/en-us/download/details.aspx?id=30438
  2. Run SQLEXPR_x64_ENU.exe
  3. In the left hand section, select Installation
  4. In the Right and section, select New SQL Server stand-alone installation of add features to an existing installation.
  5. At the "Setup Support Rules" screen select OK
  6. At the "Product Key" screen, select Next
  7. At the "License Terms" screen, check accept and select "Next"
  8. At the "Setup Support Files" screen, select Install
  9. At the "Setup Support Rules" screen, select Next
  10. At the "Feature Selection" screen select: Database Engine Services, SQL Server Replication, Management Tools - Basic (If Present) and SQL Client Connectivity SDK. Leave the Shared feature directory as default.
  11. At the "Instance Configuration" screen, select the Default instance option, accept the default Instance ID, accept the Instance root directory default settings and select next.
  12. At the "Disk Space Requirements" screen, select Next
  13. At the "Server Configuration" screen, under SQL Server Database Engine set the Account name to NT AUTHORITY/SYSTEM, leave the password field blanks, and set the startup type to automatic. Under SQL Server Browser Service, set the Startup Type to Automatic
  14. At the Database Engine Configuration screen, set the Authentication Mode to "Mixed Mode", Define a strong password (example: @sql2008), in the Specify SQL Server administrators section click "Add Current User". Select Next.
  15. At the "Error and Usage Reporting" screen, select Next
  16. At the "Installation Rules" screen, select Next
  17. At the "Ready to Install" screen, select Install
  18. At the Installation Progress screen, when the setup process is complete, select Next
  19. At the "Complete" screen, select Close.

SQL Configuration:

  1. In the Windows Start Menu, launch the SQL Server Configuration Manager
  2. In the Left hand section of the window, highlight SQL Server Services
  3. Verify that SQL Server Browser and SQL Server are Running
  4. In the left hand section of the window, expand SQL Server Network Configuration and highlight Protocols for MSSQLSERVER
  5. Enable Named pipes and TCP/IP
  6. Close the SQL Server Configuration Manager
  7. Restart the PC

Installing SQL Server 2005 Backward Compatibility

  1. On the I/NET 2.42 or higher installation CD, look in Support\SQLBCM_64Bit and launch the SQLServer2005_BC_x64.msi file
  2. Follow all the prompts on each screen and accept all defaults.

Install I/NET Seven 2.42 or higher

  1. Install I/NET Seven 2.42 or higher using the installation CD
  2. Follow prompts and use defaults
  3. When prompted for the SQL password, select "Windows Authentication"
  4. Restart the PC
  5. Open I/NET Configuration through the start menu.
  6. Modify the default Config profile or create a new profile.
  7. Close I/NET Configuration
  8. Start I/NET

NOTE:

If error occurs during SQL installation stating invoke or begin invoke failed, follow instructions at this link: http://support.microsoft.com/kb/975055

UPDATE: SQL2008 SP1 prevents the invoke failed error. It can be installed with the same instructions as above. Download it at this link: http://www.microsoft.com/en-us/download/details.aspx?id=25052

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 8274
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore