ODBC Connection failure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • ODBC Connection failure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7179 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

ODBC Connection failure

Picard Product_Support
‎2018-09-10 05:09 AM

Issue

Datacard ID Works gives an ODBC error. Examples shown below:

Microsoft SQL Server Login
Connection failed:
SQLState: '01000'
SQL Server Error: 53
[Microsoft][ODBC SQL Server Driver][DBNETLIB]ConnectionOpen (Connect()).
Connection failed:
SQLState: '08001'
SQL Server Error: 17
[Microsoft][ODBC SQL Server Driver][DBNETLIB]SQL Server does not exist or access denied.

Data Source Error
Data source name not found and no default driver specified
State:IM002,Native:0,Origin:[Microsoft][ODBC Driver Manager]

Product Line

TAC INET

Environment

  • I/NET Seven all versions
  • Datacard ID Works video badging software

Cause

The "IDWorksView" driver uses a ODBC Connection to allow the ID Works Software to communicate to the I/NET SQL Database. If for some reason this ODBC gets corrupted, you will get an error anytime you try to run the ID Works software.

Resolution

  1. Go to Start > Control Panel > Administrative Tools
  2. Select Data Sources (ODBC)
  3. Select the System DSN tab
  4. Highlight Seven ODBC SQL Server in the list and hit the Configure button
  5. Make sure the settings are as follows:
    • Name: Seven ODBC
    • Description: ODBC Connection for I/NET Seven
    • Server: (local)
  6. Hit Next
  7. Before you actually login to this window, choose the Client Configuration button and make sure these settings are correct.
    • Network libraries: TCP/IP
    • Connection parameters: Dynamically determine port
  8. Note that the InetThirdParty password changed in I/NET Seven rev 2.4X to PassInetDb3p_SE. If you try to use this in this process it will fail on you. Instead of using the InetThirdParty and the password here, use the Username and Password that you use for the DbCreateEditor. Then select the Next button.
  9. Verify the settings below, then hit Next:
    • Change the default database to: InetDb
  10. Verify the settings below, then hit Finish
    • Perform translation for character data
Labels (1)
Labels:
  • TAC INET
Tags (3)
  • Find more articles tagged with:
  • 6910
  • Datacard
  • ID Works
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of