Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

BACnet device can't be discovered due to duplicate name

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet device can't be discovered due to duplicate name
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • Cody_Failinger
    Cody_Failinger
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7710 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet device can't be discovered due to duplicate name

Picard Product_Support
‎2018-09-07 08:51 AM

Issue

BACnet device can't be discovered but instead shows up under the 'Unconfigured devices' in the server's hardware folder.

Product Line

EcoStruxure Building Operation

Environment

  • WorkStation
  • Enterprise Server - ES
  • Automation Server - AS

Cause

A BACnet device name must be unique. Devices with duplicate BACnet names can't be discovered.

In the screen shot below a device by the name AbesbCX already exists under Network1, when performing a device discovery on Network1 a second device with the same name is found, Since StruxureWare already has a device with the same name it adds the device to the list of unconfigurable devices.

NOTE:

“The <<N>> means the device was discovered on a directly connected network (such as the local IP network, or a directly connected MSTP bus).  The 2 indicates it was “port” 2, (port numbers are really an internal detail)

The server's Trace Log shows the following information, which includes the device's ID. The entry gives the reason as duplicate device name.

Resolution

1.8.1 and above

BACnet device name duplication is allowed, the duplicates will still land in the unconfigured folder and the system alarm will be generated BUT you can drag the duplicate device from the unconfigured folder to the desired network.

When finished, manually delete the device from the unconfigured/non-conformant folder. Alternatively, you can also  warm start the server to force the unconfigured/non-conformant devices list to be updated.

Note that the devices with duplicate names will still stay in the unconfigured/non-conformant folder until the name conflict is resolved.

1.7.2 and below

A workaround is to create the device manually and specify a BACnet name during the create process. When manually creating the device you need to know the Device ID, you can get the id from the information in the trace log as shown above.

SmartStruxure will send a message to the device to change its name to the specified BACnet name.

The entry in the unconfigured devices folder should automatically update after a few minutes, you can also re-start the server to force the unconfigured devices list to be updated, the entry for AbesBCX should be gone now that the devices has been manually configured.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 1.4.1.2009
  • 14717
  • CraigEllis20
  • defect23885
  • hotfix
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore