Replacement of Satchwell MZF 3-Port Flanged Valve Body due to obsolescence.
  • Replacement of Satchwell MZF 3-Port Flanged Valve Body due to obsolescence.
‎2018-09-10 08:52 AM
Last Updated: Crewman ContentModerator ‎2025-08-11 03:56 AM
Satchwell MZF 3-Port Flanged Valve Body requires replacement.
Field Devices
  • Satchwell 3-Port Plug and Seat Flanged Valve Body MZF
  • MZF3729
  • MZF3779
  • MZF3854
  • MZF3904
  • MZF3958
Obsolescence of Satchwell MZF 3-Port Flanged Valve Body
A number of alternative Schneider Electric 3-Port Flanged Valve Bodies are available to replace existing Satchwell MZF 3-Port Flanged Valve Bodies.
Suggestion 1
Replace Satchwell MZF 3-Port Flanged Valve Body with S-E VG311F 3-Port Flanged Valve Body of appropriate size
N.B.
Existing Satchwell Actuator installed on MZF 3-Port Flanged Valve Body may be retained for installation on replacement Schneider Electric 3-Port Flanged Valve Body.
In such instances a Schneider Electric L9TVG Linkage Kit will additionally be required.
Alternatively an Actuator from the Schneider Electric range of Actuators may be installed on the VG311F 3-Port Flanged Valve Body, in which case no additional Linkage Kit will be required.
Suggestion 2
Replace Satchwell MZF 3-Port Flanged Valve Body with S-E V321 3-Port Flanged Valve Body of appropriate size
N.B.
In such instances a Schneider Electric L8TV Linkage Kit will additionally be required.
Alternatively an Actuator from the Schneider Electric range of Actuators may be installed on the V321 3-Port Flanged Valve Body, in which case no additional Linkage Kit will be required.
IMPORTANT NOTE
It should also be noted that the face to face dimensions both of the Schneider Electric VG311F and V321 3-Port Flanged Valve Bodies differ to that of the Satchwell MZF 3-Port Flanged Valve Body
Similarly, the centre line to bottom of third port dimensions both of the Schneider Electric VG311F and V321 3-Port Flanged Valve Bodies differ to that of the Satchwell MZF 3-Port Flanged Valve Body
As a result alterations to the pipework connected to the MZF 3-Port Flanged Valve Body will be required.
  • Details of the Satchwell MZF 3-Port Flanged Valve Body may be viewed here.
  • Details of the Schneider Electric VG311F 3-Port Flanged Valve Body may be viewed here.
  • Details of the Schneider Electric V321 3-Port Flanged Valve Body may be viewed here.
  • Details of the Schneider Electric L9TVG Linkage Kit may be viewed here.
  • Details of the Schneider Electric L8TV Linkage Kit may be viewed here.
  • Field Devices
Tags (2)
  • 7459
  • GaryMontague22