Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,825
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1849 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 42
    • 43
    • 44
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

"Interval time zone" setting in Trend log

Issue Many users are unsure of the implication of the field "Interval time zone" in the Trend Log configuration window. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation Automation Server Premium Cause The setting "Interval time zone" under the Trend log configuration has caused some users to believe that this setting stores trend data in either "UTC" or "Server local time" Resolution The trend log data is always stored in UTC time, regardless of the option selected under this setting. This setting is intended for preventing problems with Daylight Savings Time (DST) when the logging interval is more frequent than 1 hour. See Interval Trend Log Properties – Basic Tab in EcoStruxure WebHelp. NOTE: When the interval is longer than 1 hour and you want to continue to log that interval after a DST change, use Server Local Time. For example, the log interval is every 24th hour at midnight and you want to continue to log at midnight even after a DST change, so you use Server Local Time. During the DST change in the Spring, the log sample will register after 23 hours. After the DST change in the Autumn, the log sample will register after 25 hours. Interval Time zone 
View full article
Lieutenant JG LocNguyen Lieutenant JG
‎2019-07-11 11:03 AM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-21 12:05 PM

Labels:
  • EcoStruxure Building Operation
1624 Views

Unable to upgrade AS-P to V3.2.x using USB

Issue AS-B/P is unable to upgrade to the EcoStruxure Building Operation V3.2.x from out-of-the-box or DFU mode. When checking the upgrade progress file, you receive the following error: Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause In V3.2.1, the change was made to use IP-over-USB as a way to communicate faster through the USB. Due to this, IPv4 and IPv6 need to be enabled on the connected device running Device Administrator. Resolution Check to make sure IPv6 is enabled on your machine. Open a Command Prompt window and run the "route print -6" command If it only shows two IPv6 addresses then IPv6 is disabled and you will need to enable it To enable IPv6 Open Registry Editor on your Windows Machine Navigate to: HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Services\Tcpip6\Parameters\ Double-click on DisabledComponents to edit Change value from "FF" (IPv6 disabled) to "00" (IPv6 enabled) Note: The Disabled Components registry value does not affect the state of the check box. Therefore, even if the Disabled Components registry key is set to disable IPv6, the check box in the Networking tab for each interface can still be checked. This is the expected behavior. Note: You must restart your computer for these changes to take effect.  
View full article
Commander JonGreen Commander
‎2020-11-24 09:31 AM

Last Updated: Lt. Commander Reza Lt. Commander ‎2022-04-13 07:24 AM

Labels:
  • EcoStruxure Building Operation
10243 Views

WorkPlace Tech and WorkPlace Tech Editor Ribbon Function

Issue The WorkPlace Tech and WorkPlace Editor add-in for the VisioRibbon is available in the toolbar of Visio but all or some of the functions are unavailable. Product Line TAC IA Series, EcoStruxure Building Operation Environment I/A Series WorkPlace Tech 5.9.x, 5.10.4 Building Operation Workstation (WorkPlace Tech Editor) Microsoft Visio 2010, 2013, 2016, 2019 (WorkPlace Tech 5.10.4 only) Cause There may be one or several of these situations causing this behavior depending on a combination of products installed. The Visio installed is an unlicensed product or in its evaluation period and not registered  The Visio installed is not properly updated There is an error in the WPDispatcher.msi Resolution Review the proper area for the Visio you are using to assure the product is registered; Visio 2010 Visio 2013/2016/2019 If the Visio is part of a subscription-based product, it will be noted as such rather than saying the product is activated. Thoroughly read this Knowledge Base Article for the information required to assure your Visio is properly updated. Workplace Tech 5.9.3 / Workplace Tech Editor (EBO) Microsoft Security Updates required for Visio and Office  To correct any possible WorkPlace Tech or Editor (SBO/EBO) dispatcher problems, Follow the path C:\Program Files (x86)\WorkPlace Tech to the WPDispatcher.msi and "right click / Uninstall" Do this for each version of SBO or EBO installed that has Workstation with WorkPlace Tech Editor.  Here is the path C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation X.Y\WorkStation or C:\Program Files (x86)\Schneider Electric StruxureWare\Building Operation X.Y\WorkStation (X.Y will be the version installed i.e 3.1).  Perform the same Uninstall of the WPDispatcher.msi.  The picture below is what will appear if the dispatcher has been removed or was not previously installed.  This message is expected. Open the WorkPlace Tech or the WorkPlaceTech Editor.  The WPDispatcher.msi will run the correct version.
View full article
Guinan RandyDavis Guinan
‎2020-04-23 12:14 PM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
2510 Views

Sigma Transition Issues

Issue Sigma server fails when a Data Import is initiated during a Sigma transition Product Line EcoStruxure Building Operation, Satchwell Sigma Environment Sigma Building Operation Enterprise Server Cause Sigma server fails when an EBO data import is initiated. Resolution It is important that the Sigma Database is checked with the Doctor utility (found in SigmaX) before a Sigma transition into EBO is undertaken. Longtext - Longtext file contains 'mandarin' type characters - probably from previous BAS/Sigma upgrades. If the file contains these, then Longtext has probably not been used in the past or not used currently. Delete the file (located c:\sigma\data), it will self re-create. Shorttext - Shorttext contains an incorrectly formatted entry. Find entry and correct. To find, delete 1 -250, if it continues to fails, the entry in question will be in the range 251 to 500 and keep halving until the entry is found. Index A errors - index contains a looping segment, where the page references itself. Correct index as necessary using SigmaX - Doctor. Index A errors - page is referenced more than once, i.e. the index page can be opened via two (or more) routes. Correct Index as necessary using SigmaX - Doctor. Note: the Index should be checked with SigmaX before a transition. Object corruption - open object in Sigma, if it fails to open, then correct by whatever means that is required, Sigma server will fail at a point during the Data Import. Log Sets - Fail to import log sets. To find, in Sigma, locate the logset.rec in the c:\sigma\data\server...folder file, take a copy. In Sigma, delete 50% of the log sets and try the import again. If it fails, delete another 50% and repeat. Or if it succeeds, then the issue may lie in the 50% of log sets originally deleted, re-instate these using the copied logset.rec file and try again by deleting the other 50% and so forth.
View full article
Picard Product_Support
‎2018-09-06 07:34 AM

Last Updated: Sisko DavidChild Sisko ‎2022-04-13 07:10 AM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
2414 Views

How to get the License Entitlement Certificate

Issue Customers may need a copy of their License Entitlement certificate Product Line EcoStruxure Building Operation Environment Building Operation Licensing Cause Missing Entitlement certificate  Resolution Customers have access to the following link, where they can use the Entitlement ID or Activation ID to login to the Licensing page: License Page information After logging in, select the “List Entitlements” under “Activation & Entitlements” on the top. Tick the checkbox in front of one Activation ID (ACT), select View/View certificate Now, a new page pops up which contains the Entitlement Certificate information. This can be saved or printed.
View full article
Lt. Commander Reza Lt. Commander
‎2022-02-10 03:51 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-12 01:28 PM

Labels:
  • EcoStruxure Building Operation
3727 Views

Warm and cold starts of Automation Server

Issue Users asked if it is possible to do a warm and cold starts of the Automation Server using the reset button on the physical hardware Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Cause Users may need to do a Warm/Cold start of the Automation Server Resolution From V1.5 and higher, the Warm start of the Automation Server can only be done through the command from the Workstation Software.  From V1.7 and higher, the Cold start of the Automation Server can only be done through the command from the Workstation Software.    Please refer to the following Webhelp for more information: Reset functionalities of the Automation Server    
View full article
Lt. Commander Reza Lt. Commander
‎2022-04-12 01:21 PM

on ‎2022-04-12 01:21 PM

Labels:
  • EcoStruxure Building Operation
1394 Views

Meter Consumption calculation type does not generate log records

Issue On an existing trend log, the calculation type can be set to the “Meter Consumption”, but this does not generate any log records. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Cause The “Set initial meter” under the “Meter Info” tab has been set to false when the trend log was initially created. Resolution The following image demonstrates the issue. The “Is meter log” is false because in the trend log creation process the “Set initial meter” has been set to false. This causes the “Meter Consumption” calculation type does not generate any log records. To resolve this: Create another Trend log with the “Set initial meter” set to true Or Right-click on an existing trend log (with “Is meter log” = false), press manage meter, configure the required settings, and then press save. This will change the “Is meter log” to true  Now, if the calculation type is set to “Meter Consumption” on the trend log, the log records are getting populated.
View full article
Lt. Commander Reza Lt. Commander
‎2022-04-12 01:19 PM

on ‎2022-04-12 01:19 PM

Labels:
  • EcoStruxure Building Operation
949 Views

Heat pump Control with Two stages Auxiliary heating

Issue Unable to use SE8650 to control heat pump with a two Stages Furnace (auxiliary heat) Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Workstation Building Operation Automation Server SSL SE8000 Cause Only one output is available in the SE8650 for Auxiliary heating Resolution A simple solution would be to Wire both Furnace W1 and W2 to the SE8650 W1 terminal, and both will be on at the same time Both furnace stages will be activated as a single stage from the same output Or a more advanced option would be to use a LUA Script to control the second stage of Auxiliary heating. See the below example using the SE8650 UO11 terminal  
View full article
Lt. Commander Ramaaly Lt. Commander
‎2022-04-08 11:10 AM

on ‎2022-04-08 11:10 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
946 Views

Strange characters are displayed in the display of a VT7000 and SE7000 Series thermostat.

Issue Strange characters are displayed in the display of a VT7000 and SE7000 Series thermostat. Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Workstation Building Operation Automation Server SSL SE7000 Cause The thermostat has experienced a brownout condition. Any time the power drops below 16-17Vac for a 1/10 of a second or so it will cause this condition. Resolution The thermostat still updates to the BMS correctly; it’s only its display that’s affected.  Cycling power to the unit will clear the issue. However, if the brown out condition is not addressed, it can happen again. If a repeated brownout issue at the site cannot be corrected, consider powering the controller with an UPS.   
View full article
Picard Product_Support
‎2018-09-06 09:46 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2022-04-05 08:45 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • TAC IA Series
1155 Views

Resolving Programmable Objects with different types of RETURN statements prior to EBO transition

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue SigmaX checks prior to transition into EBO Product Line Satchwell Sigma Environment SigmaX Cause Programmable Object checks required prior to transitioning Sigma to EBO. Resolution Programmable Object checks steps to be taken to check a Sigma database is free of more than one type of RETURN statement is used prior to a transition to EcoStruxure Building Operation (EBO). This video will demonstrate how to use SigmaX to find and create a report of any Programmable Objects that are using more than one type of RETURN statement. This video with SigmaX is the third of three videos, the first SigmaX Quick Help Video will check for Database Errors and the second video will check for Duplicated Names.     When launching the SigmaX application, see the Knowledge Base articles for Side by Side errors and errors regarding missing SigmaX files should they occur.
View full article
Sisko DavidChild Sisko
‎2022-04-05 06:28 AM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
1009 Views

Troubleshooting AS configuration issues with IP address

Issue Default IP Address for AS,TCP/IP IPv6, and StruxureWare Building Operation Product Line EcoStruxure Building Operation Environment Building Operation site Cause Attempted to ping AS and got "Request timed out." (AS does not have a default IP address) After going through StruxureWare Building Operation Device Administrator's Open Console which is also referred to as PuTTY(outlined below #1), the configuration has the proper: Hostname DHCP enabled/disabled IP address Subnet mask Default gateway DNS server Domain name Still the ping of the AS IP address receives "Request timed out"  Is this from a Virtual environment? See Resolution 6 below. Resolution Check the following settings: Use Device Administrator to set a static IP address for an Automation Server. Connect the Automation Server to the PC's USB port In Device Administrator, select the Automation Server you want to set the IP address for. On the View menu, click Console which opens console or PuTTY.  See NOTE below if Console icon not shown. If you are prompted to type a login name, default is "admin". Press Enter. If you are prompted to type a password, default is "admin". Press Enter. Type "setip". Press Enter. If you want to change the host name, delete the current host name and type a new host name. Press Enter. Type "no" to use a static IP address. Press Enter. Type the IP address for the Automation Server. Press Enter. Type the subnet mask. Press Enter. Type the default gateway address. Press Enter. Type the DNS server address. Press Enter. Type the domain name. Press Enter. Type "yes" to write the configuration. Press Enter. After the Network settings, "successfully updated" message is displayed, Type "exit" to log off. Press Enter. Rather than connect through a router or switch, plug the Ethernet cable directly into the AS. Ethernet port is AutoSensing (No Crossover Cable required). Adjust IP settings to close proximity IP and Subnet, such as the following example: Computer IP=192.168.1.2 Computer Subnet=255.255.255.0 Automation Server IP=192.168.1.5 Automation Server Subnet=255.255.255.0 Have only one NIC or network card enabled in Network Settings on this computer In Network Settings, uncheck the Internet Protocol Version 6 (TCP/IPv6), which will disable. TCP/IP Version 6 is the latest version of the internet protocol which provides communication across diverse interconnected networks which is not necessary for this configuration. If you are using a virtual environment, exit that virtual environment and attempt the configuration from the real-world environment.  If AS hangs or comes up with the Status light in red: Start Device Administrator and establish a USB connection between the computer and AS. Press the reset button on the AS three times in a row to place it in DFU mode. The AS will disappear from the Device Administrator and re-appear in DFU mode. Perform Upgrade device operation. The AS can be configured using DHCP (Dynamic Host Configuration Protocol) using Device Manager. It is recommended to not use DHCP but rather Static IP addresses. If the IP of the AS/ES changes, then reconfiguration of other AS/ES, or BACnet/IP, Modbus/IP interface needs to be changed also. NOTE: Beginning with StruxureWare Building Operation release 1.4.0, the Device Administrator no longer displays the "Console" icon on its toolbar. You can still access the PuTTY console by holding down the shift key and right-clicking on the automation server. You will have the option to open 'Console'. NOTE: Some network configuration setting changes may be prevented by the connected network. If you have issues getting the AS to save changes, disconnect the AS from the ethernet and use the USB connection only.
View full article
Picard Product_Support
‎2018-09-06 12:03 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-04-04 04:32 PM

Labels:
  • EcoStruxure Building Operation
8725 Views

Bulk Lua4RC upload via BACnet (Mass upload)

Issue Unable to upload the same Lua script to multiple Room Controllers at the same time Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Automation Server Premium SSL SE8000 (all) Cause The alternative method of uploading the script to each of the room controllers using a USB cable Resolution To upload a script to multiple Room Controllers, follow the below steps: (This procedure assumes the BACnet MSTP network is already setup) 1 - Log in to Building Operation Workstation 2 - Right-click on MSTP network and click "Search" 3 - Search for "Lua program 1" or any other Lua program object 4 - Highlight all the Room Controllers that the script will be transferred to then click on the "show/hide property grid" button. 5 - Expand the "Basic" tab and copy the Lua script in the "Description" field then click Save. 6 - The script will be uploaded to each of the Room Controllers one at a time and will be played automatically. Recommendations & Limitations: - Each Lua Program can take up to 460 bytes of text (per script). (Total of 10 Lua programs) - Script must be placed on a single line. Use semicolons ( ; ) as carriage return - Use multiple Lua programs if the 460 bytes limit is exceeded - Encapsulate logic inside the following if statement if the logic is intended to run once: if not init then    ---Script logic here    init = true end For general information about Lua programming for SE8000 Room Controllers, refer to the following guide: Custom Programming Guide for SE8000 Series Room Controllers - Application Guide
View full article
Picard Product_Support
‎2018-09-11 07:13 AM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-04 01:09 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
3985 Views

Unable to access SE7000 series parameters

Issue Unable to access SE7000 parameters as shown in the user interface guide. Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Workstation Building Operation Automation Server SSL SE7000 Cause Parameters to configure SE7000 are inaccessible Resolution To access SE7600 and SE7300, press and hold the middle key until the thermostat display Pswd set? Y/N. To access SE7200, press and hold the override key until the thermostat display Pswd set 0. For SE7200, use override keys to select parameters and use up or down arrows for configuration. For SE7200, use the middle key to select parameters and use up or down arrows for configuration. For SE7600, use YES and NO keys to select parameters and use up or down arrows for configuration.  
View full article
Picard Product_Support
‎2018-09-10 09:47 AM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-04 12:48 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
3039 Views

Converting Continuum b3/i2 Tristate outputs to EBO Multistate outputs

Issue When converting b3/i2 Tristate outputs to EBO Multistate, care must be taken to convert to the appropriate Multistate OR Multistate Pulsed output type Product Line EcoStruxure Building Operation Environment Continuum b3850 Controller Continuum i2850 Controller Cause Continuum Tristate outputs controlling dampers need to be converted to EBO Multistate pulsed  Resolution The tool will convert to Multistate or Multistate Pulsed based on the "Format" property of the Continuum Tristate output.   To have the tool convert to Multistate Pulsed, change the 'Format" property of the Continuum output From $### to #.# or another applicable format that does NOT include the "$"   This can be done in the dump file that is to be used for the conversion.
View full article
Captain AbeMeran Captain
‎2022-04-04 06:34 AM

on ‎2022-04-04 06:34 AM

Labels:
  • EcoStruxure Building Operation
1428 Views

How to create a Windows System Information report (Msinfo32.exe)

Issue Windows System Information may be requested by Technical Support to assist with a reported issue. Product Line All Product Lines Environment Microsoft Windows Operating System Cause Unspecified cause. Resolution Press WINDOWS + R on the keyboard of the Windows system that you wish to obtain the report from. The Windows key is usually located between the CTRL and ALT keys and has a picture of a flag on it. Type Msinfo32.exe and click OK The System Information tool will start. Click on File > Sav When prompted, save the *.nfo file to an accessible location. Email the *.nfo file to your support representative.    Note: This application can also be accessed from Start, All Programs, Accessories, System Tools, and System Information. Using this method will open the System Information for XP and Windows 7, 32 and 64-bit computers. Refer to: Description of Microsoft System Information (Msinfo32.exe) Tool
View full article
Picard Product_Support
‎2018-09-10 01:36 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-04 06:29 AM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Operation
  • TAC Vista
2655 Views

I/A Series Micronet LON controllers (MNL) SNVTs list

Issue I/A Series Micronet LON controllers (MNL) SNVTs list Product Line TAC IA Series Environment I/A Series Micronet LON (MNL) controllers Cause The SNVTs available in an I/A Series MNL controller are not listed on the datasheets.  Resolution The SNVTs list for various MNL controllers' LonMark profiles can be found in the WorkPlace Tech 4.0 Engineering Guide appendix B. 
View full article
Picard Product_Support
‎2018-09-11 06:25 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2022-03-31 09:05 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
2196 Views

Device Administrator fails to connect over IP

Issue Unable to add an Automation Server into the Device Administrator via IP. Error seen - Could not logon to server x.x.x.x This can be caused by providing the wrong password or the password has expired on the server.  If the password has expired, log on to the server using WorkStation and change the password. Product Line EcoStruxure Building Operation Environment Building Operation Device Administrator Building Operation Workstation Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Automation Server Cause Failed attempts of connecting to an AS-P, AS-B, or any IP controller with device admin will trigger the EBO security feature of SSH console lockout. This security feature defaults to 15 minutes and since the device admin uses SSH for communication, it will not allow the connection to an automation server while in this lockout state.  Resolution If a site is experiencing communication issues, then the SSH console lockout could be going into effect before a good connection is established. Reducing the SSH console lockout time period will allow for a connection to be made sooner without waiting out the default setting of 15 minutes. Use Workstation to log in to the server experiencing the issue. Go to Control Panel. Click on "Security settings" under the Security and Communication title. Locate the "SSH Console Lockout" configuration setting and adjust the lockout time to a shorter duration such as 1 second. Click Save. Open Device Administrator and add the Automation Server using IP.
View full article
Administrator Cody_Failinger Administrator
‎2019-12-20 08:14 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-03-31 09:58 PM

Labels:
  • EcoStruxure Building Operation
8984 Views

How to start b3/Infinet program from another b3/Infinet program

Issue As of EBO 4.0.1.86 it is not possible to bind to the "Restart" property of a b3/Infinet Script program Product Line EcoStruxure Building Operation Environment Building Operation - Continuum Interface Cause Unable to bind directly to the "Restart" property of b3 or Infinet Script program. Resolution While the issue may be resolved in a future version of EBO there is a simple workaround. The workaround consists of binding via an intermediate value object.   EXAMPLE: A b3/i2 program (MasterProg) needs to run a second b3/i2 program (SlaveProg).   Create a digital value in the device (ProgReStart), Instead of binding in MasterProg directly to the Restart property of SlaveProg, bind to the value of digital value ProgReStart, then bind the value of ProgReStart to the Restart property of SlaveProg.   Here are the resulting bindings for the intermediate value object (ProgReStart)     The sequence will then be as follows: 1. When MasterProg needs to run SlaveProg, it sets its output binding (bound to the value of ProgReStart) to 1. 2. Upon a change in its value from 0 to 1, ProgReStart will then set the Restart property of SlaveProg to 1 causing it to run.   NOTES 1. Do not use Active/Inactive, it won't work, must use 1/0 instead. 2. MasterProg will need to reset ProgReStart to 0 before running SlaveProg a second time
View full article
Captain AbeMeran Captain
‎2022-03-30 10:52 AM

on ‎2022-03-30 10:52 AM

Labels:
  • EcoStruxure Building Operation
1902 Views

Actions to take when the alarm "Missing response from server" appears in ES

Issue What actions should be taken if the alarm "Missing response from server" appears in the Enterprise Server? Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation 2.0 and later versions Cause ES/EC is waiting for a response from another server(most likely AS/AS-P/AS-B) for more than 120 minutes. Might lead to deadlock and starvation of resources. Can potentially replicate through the system and affect other servers. Examples of problems that could occur are: Values in graphics that reside in a sub server (most likely AS/AS-P or AS-B) are not updating.  Not possible to login to ES/EC Resolution Acknowledge the alarm "Missing response from Server" If not triggered again after 15 minutes then it is not a problem anymore (or at least less likely) If triggered, then continue below In the Alarm view, locate which server the alarm "Missing response from Server" comes from and log in directly to that server. Is the server responding? If not, restart the server. If it is responding, unplug the network cable to the server for a few minutes. Plugin the cable again and acknowledge the alarm. If it triggers again after 15 minutes, then Take 2 core dumps on the server (for investigation of why this problem occurred). Contact your local Product Support contact for instructions on how to do that. Restart the server (should fix the problem)
View full article
Picard Product_Support
‎2018-09-10 07:10 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-03-30 12:15 AM

Labels:
  • EcoStruxure Building Operation
2993 Views

String Bindings between Infinet Controllers

Issue String Bindings between Infinet Controllers fail Product Line EcoStruxure Building Operation Environment Infinet Controllers I2 Controller String Transfer Cause Direct string transfers between Infinet Controllers were possible in Continuum (via an import PE Program), but not in EBO via Script Program Resolution Following a Continuum Conversion, direct string transfers (via an import PE Program) downloads correctly but the Strings do not update. This type of transfer is not seen often, but was possible in Continuum. See the Knowledge Base article Passing InfinityString object between Continuum controllers Details in "Infinet Troubleshooting" in "Technical Reference Guide" from version 4.0.2 Also see WebHelp The workarounds are Bind string values direct (object to object), but this will force an EBO transfer via the ASP, so if the AS is not available the transfer will fail. Also more bandwidth is used. Rewrite the script to avoid using string transfers, by using numerical Objects
View full article
Dave_Shore Schneider Alumni (Retired)
‎2021-03-17 07:38 AM

Last Updated: Sisko DavidChild Sisko ‎2022-03-28 06:45 AM

Labels:
  • EcoStruxure Building Operation
1082 Views
  • « Previous
    • 1
    • …
    • 42
    • 43
    • 44
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of