Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,847
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1844 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 42
    • 43
    • 44
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Warm and cold starts of Automation Server

Issue Users asked if it is possible to do a warm and cold starts of the Automation Server using the reset button on the physical hardware Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Cause Users may need to do a Warm/Cold start of the Automation Server Resolution From V1.5 and higher, the Warm start of the Automation Server can only be done through the command from the Workstation Software.  From V1.7 and higher, the Cold start of the Automation Server can only be done through the command from the Workstation Software.    Please refer to the following Webhelp for more information: Reset functionalities of the Automation Server    
View full article
Lt. Commander Reza Lt. Commander
‎2022-04-12 01:21 PM

on ‎2022-04-12 01:21 PM

Labels:
  • EcoStruxure Building Operation
1370 Views

Meter Consumption calculation type does not generate log records

Issue On an existing trend log, the calculation type can be set to the “Meter Consumption”, but this does not generate any log records. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Cause The “Set initial meter” under the “Meter Info” tab has been set to false when the trend log was initially created. Resolution The following image demonstrates the issue. The “Is meter log” is false because in the trend log creation process the “Set initial meter” has been set to false. This causes the “Meter Consumption” calculation type does not generate any log records. To resolve this: Create another Trend log with the “Set initial meter” set to true Or Right-click on an existing trend log (with “Is meter log” = false), press manage meter, configure the required settings, and then press save. This will change the “Is meter log” to true  Now, if the calculation type is set to “Meter Consumption” on the trend log, the log records are getting populated.
View full article
Lt. Commander Reza Lt. Commander
‎2022-04-12 01:19 PM

on ‎2022-04-12 01:19 PM

Labels:
  • EcoStruxure Building Operation
921 Views

Heat pump Control with Two stages Auxiliary heating

Issue Unable to use SE8650 to control heat pump with a two Stages Furnace (auxiliary heat) Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Workstation Building Operation Automation Server SSL SE8000 Cause Only one output is available in the SE8650 for Auxiliary heating Resolution A simple solution would be to Wire both Furnace W1 and W2 to the SE8650 W1 terminal, and both will be on at the same time Both furnace stages will be activated as a single stage from the same output Or a more advanced option would be to use a LUA Script to control the second stage of Auxiliary heating. See the below example using the SE8650 UO11 terminal  
View full article
Lt. Commander Ramaaly Lt. Commander
‎2022-04-08 11:10 AM

on ‎2022-04-08 11:10 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
911 Views

Strange characters are displayed in the display of a VT7000 and SE7000 Series thermostat.

Issue Strange characters are displayed in the display of a VT7000 and SE7000 Series thermostat. Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Workstation Building Operation Automation Server SSL SE7000 Cause The thermostat has experienced a brownout condition. Any time the power drops below 16-17Vac for a 1/10 of a second or so it will cause this condition. Resolution The thermostat still updates to the BMS correctly; it’s only its display that’s affected.  Cycling power to the unit will clear the issue. However, if the brown out condition is not addressed, it can happen again. If a repeated brownout issue at the site cannot be corrected, consider powering the controller with an UPS.   
View full article
Picard Product_Support
‎2018-09-06 09:46 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2022-04-05 08:45 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • TAC IA Series
1136 Views

Resolving Programmable Objects with different types of RETURN statements prior to EBO transition

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue SigmaX checks prior to transition into EBO Product Line Satchwell Sigma Environment SigmaX Cause Programmable Object checks required prior to transitioning Sigma to EBO. Resolution Programmable Object checks steps to be taken to check a Sigma database is free of more than one type of RETURN statement is used prior to a transition to EcoStruxure Building Operation (EBO). This video will demonstrate how to use SigmaX to find and create a report of any Programmable Objects that are using more than one type of RETURN statement. This video with SigmaX is the third of three videos, the first SigmaX Quick Help Video will check for Database Errors and the second video will check for Duplicated Names.     When launching the SigmaX application, see the Knowledge Base articles for Side by Side errors and errors regarding missing SigmaX files should they occur.
View full article
Sisko DavidChild Sisko
‎2022-04-05 06:28 AM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
989 Views

Troubleshooting AS configuration issues with IP address

Issue Default IP Address for AS,TCP/IP IPv6, and StruxureWare Building Operation Product Line EcoStruxure Building Operation Environment Building Operation site Cause Attempted to ping AS and got "Request timed out." (AS does not have a default IP address) After going through StruxureWare Building Operation Device Administrator's Open Console which is also referred to as PuTTY(outlined below #1), the configuration has the proper: Hostname DHCP enabled/disabled IP address Subnet mask Default gateway DNS server Domain name Still the ping of the AS IP address receives "Request timed out"  Is this from a Virtual environment? See Resolution 6 below. Resolution Check the following settings: Use Device Administrator to set a static IP address for an Automation Server. Connect the Automation Server to the PC's USB port In Device Administrator, select the Automation Server you want to set the IP address for. On the View menu, click Console which opens console or PuTTY.  See NOTE below if Console icon not shown. If you are prompted to type a login name, default is "admin". Press Enter. If you are prompted to type a password, default is "admin". Press Enter. Type "setip". Press Enter. If you want to change the host name, delete the current host name and type a new host name. Press Enter. Type "no" to use a static IP address. Press Enter. Type the IP address for the Automation Server. Press Enter. Type the subnet mask. Press Enter. Type the default gateway address. Press Enter. Type the DNS server address. Press Enter. Type the domain name. Press Enter. Type "yes" to write the configuration. Press Enter. After the Network settings, "successfully updated" message is displayed, Type "exit" to log off. Press Enter. Rather than connect through a router or switch, plug the Ethernet cable directly into the AS. Ethernet port is AutoSensing (No Crossover Cable required). Adjust IP settings to close proximity IP and Subnet, such as the following example: Computer IP=192.168.1.2 Computer Subnet=255.255.255.0 Automation Server IP=192.168.1.5 Automation Server Subnet=255.255.255.0 Have only one NIC or network card enabled in Network Settings on this computer In Network Settings, uncheck the Internet Protocol Version 6 (TCP/IPv6), which will disable. TCP/IP Version 6 is the latest version of the internet protocol which provides communication across diverse interconnected networks which is not necessary for this configuration. If you are using a virtual environment, exit that virtual environment and attempt the configuration from the real-world environment.  If AS hangs or comes up with the Status light in red: Start Device Administrator and establish a USB connection between the computer and AS. Press the reset button on the AS three times in a row to place it in DFU mode. The AS will disappear from the Device Administrator and re-appear in DFU mode. Perform Upgrade device operation. The AS can be configured using DHCP (Dynamic Host Configuration Protocol) using Device Manager. It is recommended to not use DHCP but rather Static IP addresses. If the IP of the AS/ES changes, then reconfiguration of other AS/ES, or BACnet/IP, Modbus/IP interface needs to be changed also. NOTE: Beginning with StruxureWare Building Operation release 1.4.0, the Device Administrator no longer displays the "Console" icon on its toolbar. You can still access the PuTTY console by holding down the shift key and right-clicking on the automation server. You will have the option to open 'Console'. NOTE: Some network configuration setting changes may be prevented by the connected network. If you have issues getting the AS to save changes, disconnect the AS from the ethernet and use the USB connection only.
View full article
Picard Product_Support
‎2018-09-06 12:03 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-04-04 04:32 PM

Labels:
  • EcoStruxure Building Operation
8645 Views

Bulk Lua4RC upload via BACnet (Mass upload)

Issue Unable to upload the same Lua script to multiple Room Controllers at the same time Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Automation Server Premium SSL SE8000 (all) Cause The alternative method of uploading the script to each of the room controllers using a USB cable Resolution To upload a script to multiple Room Controllers, follow the below steps: (This procedure assumes the BACnet MSTP network is already setup) 1 - Log in to Building Operation Workstation 2 - Right-click on MSTP network and click "Search" 3 - Search for "Lua program 1" or any other Lua program object 4 - Highlight all the Room Controllers that the script will be transferred to then click on the "show/hide property grid" button. 5 - Expand the "Basic" tab and copy the Lua script in the "Description" field then click Save. 6 - The script will be uploaded to each of the Room Controllers one at a time and will be played automatically. Recommendations & Limitations: - Each Lua Program can take up to 460 bytes of text (per script). (Total of 10 Lua programs) - Script must be placed on a single line. Use semicolons ( ; ) as carriage return - Use multiple Lua programs if the 460 bytes limit is exceeded - Encapsulate logic inside the following if statement if the logic is intended to run once: if not init then    ---Script logic here    init = true end For general information about Lua programming for SE8000 Room Controllers, refer to the following guide: Custom Programming Guide for SE8000 Series Room Controllers - Application Guide
View full article
Picard Product_Support
‎2018-09-11 07:13 AM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-04 01:09 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
3931 Views

Unable to access SE7000 series parameters

Issue Unable to access SE7000 parameters as shown in the user interface guide. Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Workstation Building Operation Automation Server SSL SE7000 Cause Parameters to configure SE7000 are inaccessible Resolution To access SE7600 and SE7300, press and hold the middle key until the thermostat display Pswd set? Y/N. To access SE7200, press and hold the override key until the thermostat display Pswd set 0. For SE7200, use override keys to select parameters and use up or down arrows for configuration. For SE7200, use the middle key to select parameters and use up or down arrows for configuration. For SE7600, use YES and NO keys to select parameters and use up or down arrows for configuration.  
View full article
Picard Product_Support
‎2018-09-10 09:47 AM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-04 12:48 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
2892 Views

Converting Continuum b3/i2 Tristate outputs to EBO Multistate outputs

Issue When converting b3/i2 Tristate outputs to EBO Multistate, care must be taken to convert to the appropriate Multistate OR Multistate Pulsed output type Product Line EcoStruxure Building Operation Environment Continuum b3850 Controller Continuum i2850 Controller Cause Continuum Tristate outputs controlling dampers need to be converted to EBO Multistate pulsed  Resolution The tool will convert to Multistate or Multistate Pulsed based on the "Format" property of the Continuum Tristate output.   To have the tool convert to Multistate Pulsed, change the 'Format" property of the Continuum output From $### to #.# or another applicable format that does NOT include the "$"   This can be done in the dump file that is to be used for the conversion.
View full article
Captain AbeMeran Captain
‎2022-04-04 06:34 AM

on ‎2022-04-04 06:34 AM

Labels:
  • EcoStruxure Building Operation
1387 Views

How to create a Windows System Information report (Msinfo32.exe)

Issue Windows System Information may be requested by Technical Support to assist with a reported issue. Product Line All Product Lines Environment Microsoft Windows Operating System Cause Unspecified cause. Resolution Press WINDOWS + R on the keyboard of the Windows system that you wish to obtain the report from. The Windows key is usually located between the CTRL and ALT keys and has a picture of a flag on it. Type Msinfo32.exe and click OK The System Information tool will start. Click on File > Sav When prompted, save the *.nfo file to an accessible location. Email the *.nfo file to your support representative.    Note: This application can also be accessed from Start, All Programs, Accessories, System Tools, and System Information. Using this method will open the System Information for XP and Windows 7, 32 and 64-bit computers. Refer to: Description of Microsoft System Information (Msinfo32.exe) Tool
View full article
Picard Product_Support
‎2018-09-10 01:36 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-04 06:29 AM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Operation
  • TAC Vista
2560 Views

I/A Series Micronet LON controllers (MNL) SNVTs list

Issue I/A Series Micronet LON controllers (MNL) SNVTs list Product Line TAC IA Series Environment I/A Series Micronet LON (MNL) controllers Cause The SNVTs available in an I/A Series MNL controller are not listed on the datasheets.  Resolution The SNVTs list for various MNL controllers' LonMark profiles can be found in the WorkPlace Tech 4.0 Engineering Guide appendix B. 
View full article
Picard Product_Support
‎2018-09-11 06:25 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2022-03-31 09:05 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
2142 Views

Device Administrator fails to connect over IP

Issue Unable to add an Automation Server into the Device Administrator via IP. Error seen - Could not logon to server x.x.x.x This can be caused by providing the wrong password or the password has expired on the server.  If the password has expired, log on to the server using WorkStation and change the password. Product Line EcoStruxure Building Operation Environment Building Operation Device Administrator Building Operation Workstation Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Automation Server Cause Failed attempts of connecting to an AS-P, AS-B, or any IP controller with device admin will trigger the EBO security feature of SSH console lockout. This security feature defaults to 15 minutes and since the device admin uses SSH for communication, it will not allow the connection to an automation server while in this lockout state.  Resolution If a site is experiencing communication issues, then the SSH console lockout could be going into effect before a good connection is established. Reducing the SSH console lockout time period will allow for a connection to be made sooner without waiting out the default setting of 15 minutes. Use Workstation to log in to the server experiencing the issue. Go to Control Panel. Click on "Security settings" under the Security and Communication title. Locate the "SSH Console Lockout" configuration setting and adjust the lockout time to a shorter duration such as 1 second. Click Save. Open Device Administrator and add the Automation Server using IP.
View full article
Administrator Cody_Failinger Administrator
‎2019-12-20 08:14 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-03-31 09:58 PM

Labels:
  • EcoStruxure Building Operation
8818 Views

How to start b3/Infinet program from another b3/Infinet program

Issue As of EBO 4.0.1.86 it is not possible to bind to the "Restart" property of a b3/Infinet Script program Product Line EcoStruxure Building Operation Environment Building Operation - Continuum Interface Cause Unable to bind directly to the "Restart" property of b3 or Infinet Script program. Resolution While the issue may be resolved in a future version of EBO there is a simple workaround. The workaround consists of binding via an intermediate value object.   EXAMPLE: A b3/i2 program (MasterProg) needs to run a second b3/i2 program (SlaveProg).   Create a digital value in the device (ProgReStart), Instead of binding in MasterProg directly to the Restart property of SlaveProg, bind to the value of digital value ProgReStart, then bind the value of ProgReStart to the Restart property of SlaveProg.   Here are the resulting bindings for the intermediate value object (ProgReStart)     The sequence will then be as follows: 1. When MasterProg needs to run SlaveProg, it sets its output binding (bound to the value of ProgReStart) to 1. 2. Upon a change in its value from 0 to 1, ProgReStart will then set the Restart property of SlaveProg to 1 causing it to run.   NOTES 1. Do not use Active/Inactive, it won't work, must use 1/0 instead. 2. MasterProg will need to reset ProgReStart to 0 before running SlaveProg a second time
View full article
Captain AbeMeran Captain
‎2022-03-30 10:52 AM

on ‎2022-03-30 10:52 AM

Labels:
  • EcoStruxure Building Operation
1692 Views

Actions to take when the alarm "Missing response from server" appears in ES

Issue What actions should be taken if the alarm "Missing response from server" appears in the Enterprise Server? Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation 2.0 and later versions Cause ES/EC is waiting for a response from another server(most likely AS/AS-P/AS-B) for more than 120 minutes. Might lead to deadlock and starvation of resources. Can potentially replicate through the system and affect other servers. Examples of problems that could occur are: Values in graphics that reside in a sub server (most likely AS/AS-P or AS-B) are not updating.  Not possible to login to ES/EC Resolution Acknowledge the alarm "Missing response from Server" If not triggered again after 15 minutes then it is not a problem anymore (or at least less likely) If triggered, then continue below In the Alarm view, locate which server the alarm "Missing response from Server" comes from and log in directly to that server. Is the server responding? If not, restart the server. If it is responding, unplug the network cable to the server for a few minutes. Plugin the cable again and acknowledge the alarm. If it triggers again after 15 minutes, then Take 2 core dumps on the server (for investigation of why this problem occurred). Contact your local Product Support contact for instructions on how to do that. Restart the server (should fix the problem)
View full article
Picard Product_Support
‎2018-09-10 07:10 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-03-30 12:15 AM

Labels:
  • EcoStruxure Building Operation
2942 Views

String Bindings between Infinet Controllers

Issue String Bindings between Infinet Controllers fail Product Line EcoStruxure Building Operation Environment Infinet Controllers I2 Controller String Transfer Cause Direct string transfers between Infinet Controllers were possible in Continuum (via an import PE Program), but not in EBO via Script Program Resolution Following a Continuum Conversion, direct string transfers (via an import PE Program) downloads correctly but the Strings do not update. This type of transfer is not seen often, but was possible in Continuum. See the Knowledge Base article Passing InfinityString object between Continuum controllers Details in "Infinet Troubleshooting" in "Technical Reference Guide" from version 4.0.2 Also see WebHelp The workarounds are Bind string values direct (object to object), but this will force an EBO transfer via the ASP, so if the AS is not available the transfer will fail. Also more bandwidth is used. Rewrite the script to avoid using string transfers, by using numerical Objects
View full article
Dave_Shore Schneider Alumni (Retired)
‎2021-03-17 07:38 AM

Last Updated: Sisko DavidChild Sisko ‎2022-03-28 06:45 AM

Labels:
  • EcoStruxure Building Operation
1067 Views

Modbus IP Multiple Queries and Multiple Query Packets (Async) explanation

Issue Details on how Modbus IP Multiple Queries and Multiple Query Packets work Product Line EcoStruxure Building Operation Environment Building Operation SmartX Servers Modbus IP Cause Understanding of how the Modbus synchronous and asynchronous transport layers differ. Resolution By default, the Multiple queries is Disabled, this is the synchronous transport layer. To enable the asynchronous transport layer the Multiple queries must be Enabled within the Modbus TCP Network properties as shown below. Setting to "Enabled" allows multiple queries (packets) to be sent to multiple Modbus devices, thus reducing wait times.  It also enables further settings in the Modbus Device properties "Maximum concurrent queries" and "Multi-query packets".   The maximum concurrent queries and multiple-query packets as shown below are configurations for the Modbus asynchronous transport layer. The Maximum concurrent queries setting is only enabled if the "Multiple queries" is enabled in the Network Properties. When enabled, this allows the "concurrent queries" to be sent as a single packet.     Modbus Synchronous Transport Layer Each Modbus query is sent out one after the other. Before sending out the next query the transport layer waits for a specified period for the previous query. Example Poll Sequence Device No. Objects 1 2 2 1 D=Device, Q=Query, R=Reply D1 Q1 Send D1 R1 Receive  D2 Q1 Send D2 R1 Receive  D1 Q2 Send D1 R2 Receive  If it takes 1 second for the device to reply, then this sequence would take 3 seconds. Modbus Asynchronous Transport Layer With the asynchronous transport layer enabled, the queries are transmitted to multiple devices at the same time. The maximum number of queries that are transmitted to that one device is controlled by the “Maximum concurrent queries” setting. The “Multiple-query packet” specifies whether the queries are transmitted in one TCP frame or not. Simple Example Poll Sequence Device No. Objects Multiple-query packet Maximum concurrent queries 1 2 False 1 2 1 False 1 D=Device, Q=Query, R=Reply D1 Q1 Send D2 Q1 Send D1 Q2 Send D1 R1 Receive  D2 R1 Receive  D1 R2 Receive  If it takes 1 second for the device to reply, then this sequence would take 1 second Complex Example Poll Sequence Device No. Objects Multiple-query packet Maximum concurrent queries 1 10 True 5 2 4 False 2 D=Device, Q=Query, R=Reply D1 Q1, Q2, Q3, Q4, Q5 Send D2 Q1 Send D2 Q2 Send D1 R1, R2, R3, R4, R5 Receive  D2 R1 Receive  D2 R2 Receive  D1 Q6, Q7, Q8, Q9, Q10 Send D2 Q3 Send D2 Q4 Send D1 R6, R7, R8, R9, R10 Receive  D2 R1 Receive  D2 R2 Receive  If it takes 1 second for the device to reply, then this sequence would take 2 seconds   NOTES The use of this feature should be avoided before EBO v3.1, there is also a defect in EBO v3.2 that means v3.2.3.5000 should be used (minimum) Some Modbus devices do not support multiple queries or multiple query packets, so the feature should be tested on an individual basis. (Some devices may even go offline until manually reset) This feature will increase the CPU usage on the EBO server. It should be avoided on EBO Servers that are already heavily loaded This feature also has the ability to reduce the system stability, it is usually better to optimize the use of Modbus Register Groups to increase performance
View full article
Guinan RobertAndriolo Guinan
‎2020-11-11 03:47 AM

Last Updated: Sisko DavidChild Sisko ‎2022-03-23 08:30 AM

Labels:
  • EcoStruxure Building Operation
3040 Views

Discovering Lon Devices in SmartStruxure

Issue How to discover MNL Lon devices or other Lon devices in an SmartStruxure Automation Server. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server Cause Use the below instructions when you need to find all Lon devices on a Lon network. Resolution To discover a LonWorks device In WorkStation, in the System Tree pane, select the server that is connected to the device you want to discover. Click the Device Discovery view. In the Select device type box, select LonWorks. Select the Devices folder. Right click on the Devices folder and take "Scan network for devices" In the Device Discovery view, ensure that the LonWorks device is displayed in the Devices folder. This may take up to 5 seconds. Drag the discovered device to the System Tree pane: Drag to an existing device to associate it with the discovered physical device. Drag to the LonWorks network to create the device.   NOTE: You cannot drag a standard MNL LonWorks device to the System Tree pane if the discovered device is in an unconfigured state For more information, refer to the Creating and Configuring a LonWorks Network with MNL LonWorks Devices [102423].pdf document 
View full article
Picard Product_Support
‎2018-09-11 02:56 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2022-03-17 02:39 AM

Labels:
  • EcoStruxure Building Operation
5363 Views

Prepairing SmartConnector for Flexera license hosting in version 2.5

Issue SmartConnector 2.5 uses the Flexera licensing model. Version 2.4 and below used native licensing. How can the existing license be upgraded for SmartConnector 2.5? Product Line EcoStruxure Building Operation, Flexera Environment Building Operation Enterprise Server Flexera FlexNet Operations Cause SmartConnector 2.5 uses the Flexera licensing model. That means you will license SmartConnector using the License Administrator interface. Prior to version 2.5, SmartConnector licensing used a native licensing model.   Resolution SmartConnector 2.5 will still support the native licensing structure that we have for SmartConnector today for its core license. The way this works is as follows...   There are two parts to SmartConnector licensing.  There is the core, or runtime license which is used to license the web portal and the windows service. There is a second part that licenses the integrations and SmartConnector extensions.  These are licensed separately. When installing SmartConnector for the first time at version 2.5 a single comprehensive license (incorporating the core and integrations licenses) is purchased.  This license is applied using the License Administrator application.   In cases where SmartConnector is being upgraded from a pre-2.5 version, the core license will remain installed as a native license. Your integrations license upgrade would be installed using License Administrator.   Obviously, with SmartConnector you could run lots of different extensions on the same machine. You would still only have one SmartConnector core license but you would license your extensions individually. So you could have many integration licenses running on the Flexera server, while your core license remains in place.
View full article
JohnBoehmer Schneider Alumni (Retired)
‎2022-03-17 08:19 AM

on ‎2022-03-17 08:19 AM

Labels:
  • EcoStruxure Building Operation
1048 Views

How to search for personal and public dashboards

Issue How to find out if a user has created a personal and/or a public dashboard Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Workstation Cause Customers may want to know if there is a personal or public dashboard (or both) under a user Resolution We can search in Workstation to know if a user has created a personal or public dashboard (or both). Enter “Dashboard” on the “Include type” and search over the whole server.   Public dashboards can be created by any user anywhere under the server except under the system tree. In the following example, any results that appear under the “/Server 1/System/Domains” is a personal dashboard since it is tied to the users, and the rest are public dashboards.     Please note that creating a personal dashboard requires a Personal Dashboard License.    How Dashboards Work  Public vs Personal Dashboards  
View full article
Lt. Commander Reza Lt. Commander
‎2022-03-16 03:33 PM

on ‎2022-03-16 03:33 PM

Labels:
  • EcoStruxure Building Operation
1090 Views

Adding Enterprise Server to Enterprise Central fails with Error - Object Does not exist Domain: Data Access

  Issue When adding an Enterprise Server (ES) to Enterprise Central (EC), the process fails with Error - Object Does not exist Domain: Data Access. Details: Modules: Connect Plugin Module Code 73 Trace log shows the following text: nsp.csc.csm.ChangeSetTransaction Rollback due to Data Access Error: Object_Does_Not_Exist (0x40004) in module Connect_Plugin(73), moduleCode=73. "" nsp.csc.cspclient.AddServerCommandPassThrough Execute: Data Access Error: Object_Does_Not_Exist (0x40004) in module Connect_Plugin(73), moduleCode=73. "" nsp.csc.cspclient.ConnectionPool Terminating. GetConnection aborted [IP Address: port#] Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central  Building Operation Enterprise Server  Registered System Cause In this instance, the ES added to the EC is currently registered.  Registered Servers can only be the parent server and therefore cannot be added to a non-registered system or a different system.  Parent servers can only be registered, and any sub-servers inherit this registration from the Parent sever.    Resolution The registration should always be on the parent server. To remove the registration from the ES, the SystemID needs resetting as per the following procedure:  Resetting the System ID Once reset, the system is no longer registered, and adding the ES to the EC will be successful. 
View full article
Guinan RobertAndriolo Guinan
‎2022-03-15 08:23 PM

on ‎2022-03-15 08:23 PM

Labels:
  • EcoStruxure Building Operation
1384 Views
  • « Previous
    • 1
    • …
    • 42
    • 43
    • 44
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of