Strange characters are displayed in the display of a VT7000 and SE7000 Series thermostat.
  • Strange characters are displayed in the display of a VT7000 and SE7000 Series thermostat.
  • Ramaaly
    Ramaaly
  • sesa116873_brid
    sesa116873_brid
  • sesa116868
    sesa116868
‎2018-09-06 09:46 AM
Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2022-04-05 08:45 AM
EcoStruxure Building Operation, EcoStruxure Building Expert
  • Building Operation Workstation
  • Building Operation Automation Server
  • SSL SE7000
The thermostat has experienced a brownout condition. Any time the power drops below 16-17Vac for a 1/10 of a second or so it will cause this condition.
The thermostat still updates to the BMS correctly; it’s only its display that’s affected.
Cycling power to the unit will clear the issue. However, if the brown out condition is not addressed, it can happen again. If a repeated brownout issue at the site cannot be corrected, consider powering the controller with an UPS.