Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Actions to take when the alarm "Missing response from server" appears in ES

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Actions to take when the alarm "Missing response from server" appears in ES
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • Jonas_Brissman
    Jonas_Brissman
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3175 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Actions to take when the alarm "Missing response from server" appears in ES

Picard Product_Support
‎2018-09-10 07:10 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-03-30 12:15 AM

Issue

What actions should be taken if the alarm "Missing response from server" appears in the Enterprise Server?alarm-queue.png

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation 2.0 and later versions

Cause

ES/EC is waiting for a response from another server(most likely AS/AS-P/AS-B) for more than 120 minutes. Might lead to deadlock and starvation of resources. Can potentially replicate through the system and affect other servers.
Examples of problems that could occur are:

  • Values in graphics that reside in a sub server (most likely AS/AS-P or AS-B) are not updating. 
  • Not possible to login to ES/EC

Resolution

  1. Acknowledge the alarm "Missing response from Server"
    1. If not triggered again after 15 minutes then it is not a problem anymore (or at least less likely)
    2. If triggered, then continue below
  2. In the Alarm view, locate which server the alarm "Missing response from Server" comes from and log in directly to that server. Is the server responding?
  3. If not, restart the server. If it is responding, unplug the network cable to the server for a few minutes.
    1. Plugin the cable again and acknowledge the alarm.
    2. If it triggers again after 15 minutes, then
      1. Take 2 core dumps on the server (for investigation of why this problem occurred). Contact your local Product Support contact for instructions on how to do that.
      2. Restart the server (should fix the problem)
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 19836
  • HernanUruena24
  • JonasBrissman19
  • RobertAndriolo22
Was this article helpful? Yes No
0% helpful (0/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore