Device Administrator fails to connect over IP

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Device Administrator fails to connect over IP
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Cody_Failinger
    Cody_Failinger
  • RobertAndriolo
    RobertAndriolo
  • Jonas_Brissman
    Jonas_Brissman

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
4 Likes
10078 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Device Administrator fails to connect over IP

Administrator Cody_Failinger Administrator
‎2019-12-20 08:14 AM

Last Updated: Picard RobertAndriolo Picard ‎2022-03-31 09:58 PM

Issue

Unable to add an Automation Server into the Device Administrator via IP.

Error seen -

Could not logon to server x.x.x.x

This can be caused by providing the wrong password or the password has expired on the server.  If the password has expired, log on to the server using WorkStation and change the password.

DeviceAdminError.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Device Administrator
  • Building Operation Workstation
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Building Operation Automation Server

Cause

Failed attempts of connecting to an AS-P, AS-B, or any IP controller with device admin will trigger the EBO security feature of SSH console lockout. This security feature defaults to 15 minutes and since the device admin uses SSH for communication, it will not allow the connection to an automation server while in this lockout state. 

Resolution

If a site is experiencing communication issues, then the SSH console lockout could be going into effect before a good connection is established. Reducing the SSH console lockout time period will allow for a connection to be made sooner without waiting out the default setting of 15 minutes.

  1. Use Workstation to log in to the server experiencing the issue.
  2. Go to Control Panel.
  3. Click on "Security settings" under the Security and Communication title.
  4. Locate the "SSH Console Lockout" configuration setting and adjust the lockout time to a shorter duration such as 1 second.
    SSH Console Lockout.png
  5. Click Save.
  6. Open Device Administrator and add the Automation Server using IP.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • CodyFailinger19
  • JonasBrissman21
  • RobertAndriolo22
Was this article helpful? Yes No
74% helpful (14/19)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore