Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Sigma Transition Issues

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma Transition Issues
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2928 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma Transition Issues

Product_Support
‎2018-09-06 07:34 AM

Last Updated: CraigEl Champion ‎2025-11-04 04:50 PM

Issue

Sigma server fails when a Data Import is initiated during a Sigma transition into EcoStruxure Building Operation (EBO).

Product Line

EcoStruxure Building Operation, Satchwell Sigma

Environment

  • Satchwell Sigma
  • Building Operation Enterprise Server

Cause

The failure typically occurs due to data integrity issues within the Sigma database. These issues must be resolved before initiating the transition.

Resolution

Before transitioning Sigma into EBO, run the SigmaX Doctor utility to validate and clean the database. Address the following common issues:

1. Longtext File Issues

  • Symptoms: Contains 'Mandarin'-type characters, likely from previous BAS/Sigma upgrades.
  • Action:
    • Delete the longtext file located at C:\sigma\data.
    • The file will auto-recreate if needed.

2. Shorttext File Issues

  • Symptoms: Contains incorrectly formatted entries.
  • Action:
    • Use a binary search method to locate the faulty entry:
      • Delete entries 1–250. If the issue persists, check entries 251–500.
      • Continue halving the range until the problematic entry is found and corrected.

3. Index A Errors

  • Types:
    • Looping Segment: Page references itself.
    • Multiple References: Page can be accessed via multiple routes.
  • Action:
    • Use SigmaX Doctor to correct the index structure.

4. Object Corruption

  • Symptoms: Object fails to open in Sigma.
  • Action:
    • Open the object in Sigma and correct it using appropriate methods.
    • If unresolved, the server will fail during Data Import.

5. Log Sets Import Failure

  • Symptoms: Log sets fail to import.
  • Action:
    • Locate logset.rec in C:\sigma\data\server...folder.
    • Make a backup copy.
    • Delete 50% of log sets and retry the import.
      • If it fails, delete another 50%.
      • If it succeeds, the issue lies in the deleted portion.
    • Use the backup to reinstate and isolate the problematic log sets.

⚠️ Important Notice

Sigma is not supported in EBO 2022 and later.
To continue supporting Sigma devices, you can implement a multi-version system:

  • Keep Enterprise Servers with Sigma devices on Building Operation 3.2.
  • Add a Building Operation 2022 or later Enterprise Central
  • Upgrade the rest of the system to Building Operation 2022 or later.

You will not be able to upgrade EcoStruxure Building Operation servers that contain unsupported protocols, objects, or devices. Attempting to do so will result in failed upgrades or loss of functionality.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
Tags (5)
  • Find more articles tagged with:
  • 19517
  • CraigEllis25
  • DavidChild19
  • DavidChild20
  • DavidChild22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore