Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,841
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 11
    • 12
    • 13
    • …
    • 507
  • Next »

SMTP Email Alarm Configuration in Continuum 2.0 and 2.03

Issue Instructions are needed to configure the new SMTP configuration. Product Line Andover Continuum Environment Continuum Non-Microsoft Exchange/Outlook SMTP Email Cause Configuration for the SMTP Configuration for email alarming in Continuum 2.00 through 2.03 Resolution In Cyberstation 2.0 and above, you no longer need Microsoft Outlook and Exchange to send email alarm notifications. Other SMTP servers can be used on the network and other email clients can be used also to send email alarm notifications directly to an intended recipient. Note: Public SMTP servers such as Gmail SMTP and Yahoo SMTP do not currently work with this solution as they require SSL or certain unsupported port combinations. The connections these servers establish cause connection issues within the SMTP application. Private SMTP (In-house) servers can be set up and used.   Steps to Configure SMTP Email Alarming   Open and Event Notification Navigate to the Actions Tab Select which events to receive email alarms Select the Delivery Tab Click the Add Recipient button to open the recipient configuration Browse for the recipient Cyberstation by click the ellipsis Select the recipient Cyberstation Select the SMTP Configuration button in the Recipient Configuration window Fill in the Server Configuration fields in the SMTP Configuration window Specify the SMTP Server address, port and login information Fill in the Email Configuration Specify the sender's email address - this is the email address the email will be sent from and it is also the email address that failed emails will be sent to    Type in a Subject line if needed or the default Continuum email subject line will be used Alarm Option Settings - Fill in the RetryCount and Retry Time fields  Retry Count - once you pass this value the email is dropped. The maximum Retry Count is 10  Retry Time -  field is in minutes. The maximum is 1440 minutes (24 hours) Adding an email address to the recipient list Click the Display Master List to open the SMTP Master Email Configuration Dialog Place a check in the check box to add an email address from the existing Master List to the Event Notification's recipient list and then click OK Adding or deleting email addresses from the Master Email list Open the SMTPMasterEmail Event Notification in the templates folder In the opened SMTPMasterEmail Event Notification click the Display Master List button Click the Add Recipient or Delete Recipient button depending on what is needed After selecting Add Recipient supply the email address in the recipient field and click Add Recipient After selecting Delete Recipient, select the address to highlight it and then click the Delete Recipient button. Multiple Selection is supported To deliver email notifications to the added email address, select the check box next to it Testing to ensure email address recipients receive emails Select the address you wish to test and click the Test Selected button Successful email to SMTP Server test will display a pop-up Failed email to SMTP server test will display a pop-up to the Sender's email address Final address configuration Recipients Configuration Options Place a checkmark next to the option needed Ex. Primary or Backup  SMTP Email A checkmark next to Repeat. Repeat will function as if it were an Outlook email alarm and send until the alarm is acknowledged. Known issues: In order for BACnet controllers to use the new SMTP feature, the following hotfix from the following link is needed.  CyberStation v2.00 (Only) SMTP Emailing & BACnet Alarms - Hotfix 2.03 contains the hotfix listed above   For additional information, see the Cyberstation Help, search for SMTP.
View full article
Picard Product_Support
‎2018-09-11 09:08 AM

Last Updated: Administrator CraigEl Administrator ‎2022-11-07 03:27 PM

Labels:
  • Andover Continuum
6108 Views

Configuring EBO SMTP settings to use a Google SMTP server

Issue Need to configure SMTP settings to use a Google SMTP server Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause There is no SMTP settings configured by default Resolution Note: As of May 30, 2022 please also consult Less secure apps & your Google Account 
View full article
Commander JonGreen Commander
‎2020-01-24 08:22 AM

Last Updated: Sisko GavinHe Sisko ‎2023-02-27 07:01 AM

Labels:
  • EcoStruxure Building Operation
6166 Views

How to reset the backup to flash circuit breaker on i2/b3 devices

Issue After 2000 backups an attempt to perform a backup to flash results in the error 'Flash backup for this controller has been disabled.' Product Line EcoStruxure Building Operation, Andover Continuum Environment b3 controller i2 controller Cause Flash memory has a limited write count; Controllers implement a flash circuit breaker that trips after 2000 backup operations in order to protect the flash device from damage. Resolution (Applies to all b3 and i2 controllers) EcoStruxure Building Operation In EBO, a command has been added that will re-enable backup to flash after the circuit breaker has been tripped (2000 backups) From Workstation, in the object tree, right-click the i2/b3 device. From the context menu select, DEVICE->ENABLE BACKUP TO FLASH     Andover Continuum From CyberStation command line set the ACCStatusBackup system variable of the device to ACCBackupEnable. NOTE: The flash circuit breaker CANNOT be reset from Script/Plain English.  This is by design as it was deemed too risky to allow resetting it programmatically.  A poorly written program could very quickly cause damage to the flash device.
View full article
Picard Product_Support
‎2020-09-22 09:25 AM

Last Updated: Sisko GavinHe Sisko ‎2024-04-25 02:42 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
6087 Views

How to read the LED Indicator lights on a Xenta controller

Issue Solid red light Blinking red light Blinking green light Product Line TAC Vista Environment Xenta Programmable Controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Cause The indicator lights on the face of the Xenta controllers can help explain the state of the controller with different actions.  Resolution There are two LED indicators – one red and one green on the Xenta programmable controllers.   The red service diode is primarily an error indication. It also lights up if the Service pin is activated. A solid red light usually indicates that the hardware has failed.  Please see a few simple steps to deactivate the solid red light below. Use a reset dongle to wipe the controller then reinstall the firmware and menta program. If the controller is the group master you might try to assign a different controller to group master.  This method has not been proven but has worked before during internal testing. NOTE: The hardware may need to be replaced if the solid red light continues after these steps. If the red indicator light is blinking once per second this will indicate a non-configured node. If the controller has been commissioned you might try to decommission the controller and try again. If the red indicator light is off this would indicate that it has been commissioned and added properly to the network.  You should not see the red indicator light if the controller is working properly. The green status diode blinks once per second to indicate that the program is running properly.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-22 01:48 AM

Labels:
  • TAC Vista
6077 Views

What Continuum products have been discontinued?

Issue Where to find a statement of discontinued products if needed. Product Line Andover Continuum Environment Obsoleted Continuum Controllers DCX250 DCX 250, Netcontroller CX9000, CX9400 Infinity products Cause Which products are no longer available? Resolution The following link details all products that were discontinued in 2007/ 2008: 2007/ 2008 Discontinued Products Also the DCX250 was obsoleted in 2011 see Product Announcement Discontinuation of Infinity 01-0008-300 (DCX 250) Also see Display options now the DCX250 is no longer available for DCX250 alternatives.  Search for all discontinuation announcements on The Exchange.
View full article
Picard Product_Support
‎2018-09-10 06:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:37 PM

Labels:
  • Andover Continuum
6082 Views

Building Operation Report Server SQL Database Full

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue SQL Database is full, or the partition the SQL is installed is full Product Line EcoStruxure Building Operation Environment Building Operation Report Server Cause If a site is using SQL Express 2008, the limit is 10 GB. If using the full version(s), it is unlimited. If the database or the partition where the Reports Server resides is full, here are some steps to reduce the SQL table volume and offer a short-term solution. Resolution Before continuing, make sure there is a good backup of the database. Using SQL Server Management Studio, highlight the StruxureWareReportsDB and select New Query Use the following Script in that Query: SELECT t.NAME AS TableName, s.Name AS SchemaName, p.rows AS RowCounts, SUM(a.total_pages) * 8 AS TotalSpaceKB, SUM(a.used_pages) * 8 AS UsedSpaceKB, (SUM(a.total_pages) - SUM(a.used_pages)) * 8 AS UnusedSpaceKB FROM sys.tables t INNER JOIN sys.indexes i ON t.OBJECT_ID = i.object_id INNER JOIN sys.partitions p ON i.object_id = p.OBJECT_ID AND i.index_id = p.index_id INNER JOIN sys.allocation_units a ON p.partition_id = a.container_id LEFT OUTER JOIN sys.schemas s ON t.schema_id = s.schema_id WHERE t.NAME NOT LIKE 'dt%' AND t.is_ms_shipped = 0 AND i.OBJECT_ID > 255 GROUP BY t.Name, s.Name, p.Rows ORDER BY t.Name Select Execute to run that Query as shown in the screen capture below: The Results show each of the tables and the size of those tables as shown in the screen capture below: Purely for example purposes, a script to reduce the number of Events would be delete from tbEvents where DATEDIFF(day, datetimestamp, getdate()) > 180 To gain back the space after deleting rows, right-click on StruxureWareReportsdb > Tasks > Shrink > Database
View full article
Picard Product_Support
‎2018-09-11 02:54 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2024-03-24 06:14 PM

Labels:
  • EcoStruxure Building Operation
6062 Views

BACnet COV subscription system COV Settings

Issue BACnet COV subscription system Product Line EcoStruxure Building Operation Environment BACnet Settings COV subscriptions v1.7 and earlier Cause A site will have a problem with the amount of traffic because of misconfigured COV Increments. The problem is that Building Operation, the  ES and AS resubscribes to values every 10 seconds and one by one. So for example: hh:mm:ss 00:00:00 Value1 00:00:10 Value2 00:00:20 Value3 00:00:30 Value4 ... 05:00:00 Value1800 If you have more than 1800 subscriptions the ES or AS is not able to do all subscriptions in 5 hours.   5 hours is used because Building Operation subscribes to the values with a lifetime of 5 hours.   Resolution BACnet COV subscription system is not influenced by the requested transfer rate in the edit bindings system (Subscriptions using BACnet). That is used in the case where the external device does not support COV, and read-property must be used instead. The design in 1.4 and 1.5 simply did not anticipate such large numbers of COV subscriptions. Workaround: 1.Exit Workstation 2. Stop the Enterprise Server Edit using notepad the server.properties file located in "C:\Program Files\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\etc\ Find at the bottom: # Set GenericConsume communication defaults Add the two following lines: NspServer.BACnetPlugIn.COVSubscriptionLifetime entry = 28800 NspServer.BACnetPlugIn.COVTimerPeriod entry = 5 Save your changes and close the server.properties file. This changes the default values from 5 hours to 8 hours and 10 seconds to 5 seconds. NOTE From version 1.8 the BACnet Interface manager (/Server 1/System/Interface Manager/BACnet) provides access to these settings (COV subscription lifetime (default 8 hours) and Server COV renew rate(default 5 seconds)) The settings will be controlled via the Enterprise Server if connected.
View full article
Picard Product_Support
‎2018-09-07 11:20 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:58 PM

Labels:
  • EcoStruxure Building Operation
6044 Views

IP setup for a Xenta server (Xenta 5/7/9xx) through serial communication

Issue How to set the IP address of a Xenta 5/7/9xx through serial communication. Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Servers Xenta 511, 527, 555, 701, 711, 721, 731, 913 Cause If the IP address of a Xenta 5/7/9xx is not known initially, then no configuration can be done through the IP interface. The IP address must be set through serial communication. If the device is new out of the box, or has attempted recovery after a format command, please see Default IP address following Xenta Server "format" command is different than from factory for the known default IP addressing. Resolution Preparation: You need to have an RS-232 serial cable (TAC Xenta Programming Serial Kit 0-073-0920-0). Plug the RS-232 cable in to the RS-232 B port. The RS-232 B port is the second left port at the front. Then connect the other end to the computer. Configuration steps: Go to Start > All Programs > Accessories > Communications > HyperTerminal, and open the HyperTerminal. In Connection Description Windows, type any name you like in the Name box. Click OK. In the Connect to window, choose the correct COM port that the RS-232 cable is using. If you do not know which COM port it is using. Go to your computer device manager. (Right click on “My computer” icon, and choose “Manage”. Then under “System Tools”, choose “Device Manager”. Find “Ports (COM & LPT)” and expend it Find the COM port number that is used by the RS-232 cable. Click OK. In the COM Properties window, type 9600 for “Bits per second”, 8 for “Data bits”, “Parity” is None, “Stop bits” is 1, and “Flow control” is None. Click OK. Options: you can save this setting for future use. Click on File Menu and Save. Press ENTER to activate the command prompt. Default username and password is both “root”. Type “root” and press ENTER for both the username and password. Type “setip” and press ENTER. Type the appropriate information for DHCP, IP-address, Subnet mask, Default gateway, DNS, Website name, Domain name, and Host name. Type “yes” for “Do you want to restart the IP interface”. Quit HyperTerminal when the restart is finished. See [Video] Setting the IP address of a Xenta 5/7/9xx through serial communication to watch a video of this process.
View full article
Picard Product_Support
‎2018-09-07 04:07 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:35 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
6011 Views

Part number information required for ordering the Vykon Energy Suite (VES) for Niagara G3.

Issue Ordering the proper software options for a Vykon Energy Suite installation on a Niagara G3 jobsite. Environment Niagara G3 Cause The Vykon Energy Suite is only available for purchase via Sourced Products from Tridium.  The part numbers and descriptions are difficult to locate. Resolution The feature that licenses TEA-BASE (eas) is included with the standard ENS-1. So, a separate purchase of TRD-TEABASE-G3 is no longer required (since it is not usable without licensing stations or points). TRD-TEASTA-G3 increments the station limit parameter and allows unlimited points from an ENC. TRD-TEAPNT-G3 increments the point limit parameter and allows individual points from an ENC as well as points within the ENS as required. Additional documentation: VES G3 Users Guide VES G3 Datasheet These two part numbers are now available on iPortal for ordering.  Contact Customer Care at ccc.orders@schneider-electric.com or 1-888-444-1311 (press 1) to place an order.
View full article
Picard Product_Support
‎2018-09-09 11:26 PM

Labels:
  • TAC IA Series
6001 Views

Why do Continuum controllers go into bootloader mode?

Issue Why do controllers go into bootloader mode? Product Line Andover Continuum Environment Bootloader NC2 BCX CX99xx CX96xx i2 b3 Cause Continuum controller are placed into bootloader mode if they repeatedly hit a firmware level exception. An exception is when the controller tries to do something that cannot be done.  Some examples of an exception are... A controller tries to read from memory that it cannot read from. A controller attempts write to memory that cannot be written to. On startup, flash generation controllers load the application from flash RAM.When they hit an exception, older, non-flashable controllers would simply clear the application software from ram, power up and wait for the software to be loaded from the front end.  If there is a bad application there needs to be a means by which a user can intervene before the application is loaded so that the controller firmware can be reloaded or upgraded.  When a flashable controller hits more than three exceptions within a ten minute time period the controller is placed into bootloader mode intentionally. Resolution When a controller repeatedly goes into bootloader mode it is time to take a close look at environment which might be driving the controller to hit exceptions A controller usually goes into bootloader mode due to environmental issues such as Heavy ARP traffic Controller grounding Controller power issues Problems with the communication bus. A controller that repeatedly hits exceptions is placed in bootloader mode by design.  Flashing a controllers firmware is the only way to get a controller out of bootloader mode. 
View full article
Picard Product_Support
‎2018-09-06 11:05 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-11 09:00 AM

Labels:
  • Andover Continuum
6003 Views

Using Modbus Register Group to batch read registers

Issue Modbus Register Groups feature can overcome some Modbus communication problems. It has been seen before where the Modbus controller falls offline for a few seconds then comes back online. This cycle will repeat every few seconds. When register groups are not used, there may also be issues with the amount of time it takes for a Modbus points to update. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Enterprise Server Building Operation Automation Server Premium (AS-P) Building Operation Automation Server Bundled (AS-B) Cause In a normal Modbus network, a Modbus polling device obtains data from a polled device by sending a query message to the device and then waiting for the response message that contains the requested value from the selected register. If data from another register is required, the polling device sends out a new query message and awaits the response message. This process is repeated until all subscribed points values have been read. The Modbus Register Groups are a batch read function to poll Modbus devices. Instead of reading each register individually, the batch read function reads registers in manually created groups. When all registers in a group have been read, the response message returns subscribed register values for the whole group. Register grouping provides a dramatic saving in the time taken to poll your devices. For more guidance and tips on this topic, see Section "Batch Read Function" in the EcoStruxure Building Operation Technical Reference Guide.  Note: When viewing a graphic containing Modbus values, those values will update at the same interval as their Modbus register group. Resolution When grouping Modbus points, it is important to keep in mind some of the following points. Try to ensure that as many Modbus points as possible are contained in as few groups as possible. This will reduce the overall time it takes the Enterprise Server or Automation Server to read all the subscribed points in each Modbus device. Network performance can be enhanced by choosing the method of grouping that is most suitable for each device in the Modbus network.  Network performance can be enhanced by selecting a different default poll time for each register group. Network performance can also be enhanced by grouping points that have the same or similar polls. Start with higher group poll times to ensure a stable system before reducing the poll time. Make sure to delete Modbus points out of a register group individually before deleting the group. If this is not done, it can cause system delays. See article Modbus Batch Read Multiple Registers Groups Creating a Modbus Register Group In Workstation, in the System Tree pane, right-click on a Modbus device and select New Object (1).  In the create object window select Modbus Register Group (2), provide a name and select Create (3). Now that the group has been created, existing Modbus points can be dragged and dropped into the group. New Modbus points can also be created in the group.  Right-click on the Modbus Register Group and select New Object (1).  In the create object window expand Modbus Point (2), select a point type (3), provide a name and select Create (4).
View full article
Picard Product_Support
‎2018-09-11 04:22 AM

Last Updated: Sisko GavinHe Sisko ‎2023-03-31 03:35 AM

Labels:
  • EcoStruxure Building Operation
6019 Views

Max Info Frames attribute in a Continuum BACnet controller

Issue What is the purpose of the Max Info Frames attribute in a Continuum BACnet controller? Product Line Andover Continuum Environment BACnet MS/TP, MaxInfoFrames Optimizing MSTP Cause Information on the Max Info Frames function. Resolution The Max Info Frames setting on the BACnet controller object editor specifies how many messages that the controller can send out to other controllers when it has the token on the network. For instance, a B3 controller has a default of 2 for this setting. If it receives the token on the MSTP network and it has 5 COV or Event notifications to send to other controllers or workstations, it will send the first 2, and wait until it gets the token the next time around and send 2 more, etc. The BCX controller has a default of 8 for Max Info Frames. This setting is changeable through the BACnet controller editor, however care should be taken not to increase it to too large a number. The larger the setting, the more time that particular controller can hold the onto the token, which in turn denies other controllers on the network the capability of sending out their data in a timely manner. It should only be adjusted if there is a definite need for increased messaging, but on the MSTP network it is not recommended to go above 10, although we do not limit the value. In a Cyberstation Version 1.8 or above the setting can be made on the details page of the BACnet controller device editor. If adjustment of this parameter is done using any Cyberstation prior to version 1.8, the setting will not stay at the new value after a controller reload from the Infinity side, it will revert to it's default. You will need to create a PE program in the controller to set this parameter to the desired value if it is reloaded. The program should be autostart and fallthru, and use the "Writeproperty" keyword to set the parameter. The syntax should be as follows: Line SetMaxInfo WriteProperty ("Full Bacnet path name of controller", MaxInfoFrames, "New Value") Stop
View full article
Picard Product_Support
‎2018-09-06 02:59 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-06-18 02:10 PM

Labels:
  • Andover Continuum
5936 Views

BACnet/IP devices on different subnets are not discovered when doing a Discover on a Niagara G3 ENC controller.

Issue There are BACnet/IP devices on several different IP subnets. Each subnet has one BACnet/IP device setup as a BBMD, however when doing a discover, no BACnet/IP devices from the different subnets are not being discovered. Environment Niagara G3, ENC-520 Cause Setting up the BBMD in the ENC-520 is as simple as Changing its “Ip Device Property Type” from its default of “standard” to “Bbmd”. Once the ENC is configured as a BBMD device, then the BBMD’s required Broadcast Distribution Table (BDT) is automatically created. The ENC’s BDT includes its own IP address and Broadcast Distribution Mask (BDM), as well as the IP address and BDM of all other BBMD devices on the other IP subnets. The BDT allows for manual editing. We have found in some cases that the BDMs were being confused with the IP address subnet mask. The BDMs were being changed to reflect devices’ IP address subnet mask, which were something other that the standard BDM of 255.255.255.255. BBMD devices’ BDM must be set to 255.255.255.255. Resolution The Broadcast Distribution Mask must be set to “255.255.255.255” for each BACnet /IP Address listed in the ENC’s Broadcast Distribution Table. This is also true for other BACnet/IP devices configured as BBMDs on the other subnets. 1. Expand the ENC’s BACnetNetwork 2. Expand Bacnet Comm and then expand Network 3. Expand Ip Port and then expand Link 4. Expand the Broadcast Distribution Table 5. Expand any devices listed and set their Broadcast Distribution Mask to 255.255.255.255 for any one not listed as such. Save changes. Try and discover again.  
View full article
Picard Product_Support
‎2018-09-06 10:49 AM

Labels:
  • TAC IA Series
5944 Views

Connecting to a Link or Site

Issue Connecting to a Link or Site Environment I/NET Seven Site Cause Knowledge on how to connect to a Link or Site Resolution I/NET displays this dialog box when you select Connect from the main menu. This dialog box allows you to choose a link or remote site. Connect to a device as follows: Select Connect from the main menu. The system displays a summary list of available link devices or sites. Note: A dash (-) appearing next to a device name indicates that the device is not currently available for communication. An asterisk (*) indicates that the name of the controller or the type has changed. Highlight a link device or site in the list. Select OK to connect. After the system connects to the selected device or site, the status bar at the bottom of the screen shows the connected levels.
View full article
Picard Product_Support
‎2018-09-06 03:08 PM

Labels:
  • TAC INET
5908 Views

What is the replacement for a Drayton Theta YBL1A Valve Body / Actuator assembly?

Issue The Drayton Theta YBL1A Valve Body / Actuator assembly is to be replaced. Product Line Field Devices Environment Replacement Drayton Actuator Valve YBL1A Cause The Drayton Theta YBL1A Valve Body / Actuator assembly is obsolete. Resolution OVERVIEW The Drayton Theta YBL1A Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement. The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits. No Valve Body / Actuator assemblies are currently available in these sizes. Details of the YB Valve Body may be viewed here.   VALVE BODY REPLACEMENT To replace the YBL1A Valve Body the following is required:- S-E SatchwellMB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2") Details of the MB Valve Body may be viewed here.   ACTUATOR REPLACEMENT (6-WIRE INSTALLATION) The YBL1A Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :-  Terminal M1 – Open signal Terminal M2 – Close signal Terminal M3 – Common  Terminal M4 – 135 ohm Feedback Potentiometer – winding Terminal M5 – 135 ohm Feedback Potentiometer – wiper Terminal M6 – 135 ohm Feedback Potentiometer – winding Where 6 wires are connected to the YBL1A Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here Details of the MD20B-24 Actuator may be viewed here. N.B. The YBL1A Actuator also included an additional 3-wire electrical connection associated with an integral S.P.C.O. Auxiliary Switch wired as follows :-  Terminal S1 – Normally Closed Contact Terminal S2 – Common Terminal S3 – Normally Open Contact Where external wiring is connected to the YBL1A Actuator Auxiliary Switch then an Auxiliary Switch Kit containing a S.P.C.O. Auxiliary Switch should be installed on the MD Actuator. Auxiliary Switch Kit MD-S1 (914-1060-000) Details of the MD-S1 Auxiliary Switch Kit may be viewed here. The MD-S1 Auxiliary Switch Kit should be wired as follows :-. Terminal S1 – Common Terminal S2 – Normally Closed Contact Terminal S3 – Normally Open Contact   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here   IMPORTANT NOTE In such 6-wire installations not only will the YBL1A Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.   CONTROLLER REPLACEMENT The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller. Details of the CSC Controllers may be viewed here.   SENSOR REPLACEMENT Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate. Outside Air Temperature Sensor (STO 600) Contact Temperature Sensor (STC 600), or alternatively :- Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001) Room Temperature Sensor (STR 600) – OPTIONAL ONLY Details of the STO 600 Outside Air Temperature Sensor may be viewed here. Details of the STC 600 Contact Temperature Sensor may be viewed here. Details of the STP 660 Water Temperature Sensor may be viewed here. Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here. Details of the STR 600 Room Temperature Sensor may be viewed here.   N.B. ACTUATOR REPLACEMENT (3-WIRE INSTALLATION) Should only 3 wires be connected to a YBL1A Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here. N.B. The YBL1A Actuator also included an additional 3-wire electrical connection associated with an integral S.P.C.O. Auxiliary Switch wired as follows :-  Terminal S1 – Normally Closed Contact Terminal S2 – Common Terminal S3 – Normally Open Contact Where external wiring is connected to the YBL1A Actuator Auxiliary Switch then an Auxiliary Switch Kit containing a S.P.C.O. Auxiliary Switch should be installed on the MD Actuator. Auxiliary Switch Kit MD-S1 (914-1060-000) Details of the MD-S1 Auxiliary Switch Kit may be viewed here. The MD-S1 Auxiliary Switch Kit should be wired as follows :-. Terminal S1 – Common Terminal S2 – Normally Closed Contact Terminal S3 – Normally Open Contact   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here In such 3-wire installations the YBL1A Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
View full article
Picard Product_Support
‎2018-09-10 12:17 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 06:45 PM

Labels:
  • Field Devices
5985 Views

Replacement of VTRA Valve Body by VTRE or MB/MBF Valve Body due to obsolescence.

Issue VTRA Valve Body requires replacement due to obsolescence. Product Line Field Devices Environment VTRA 3-port Mixing Valve Body Cause Obsolescence of VTRA Valve Body Resolution VTRA Valve Bodies are obsolete and have been for many years. VTRA Valve Bodies were available with either Flanged or Screwed connections.  Details of the various size / connection combinations available appear VTRA Specification Sheet. REPLACEMENT OF VTRA FLANGED CONNECTION VALVE BODY A replacement for the VTRA Flanged Valve Body (32-80mm) may be selected from the VTRE range of Flanged Valve Bodies, see VTRE S-E Specification Sheet for more datails. N.B. It should be noted that the VTRE Valve Body is rated PN6 whereas the VTRA was rated PN10. The VTRE Flanged Valve Body may be operated by the EM9 Actuator, see Alternatively the VTRE Flanged Valve Body may be operated by the M9B Actuator, See EM 9 Specification Sheet for more details. No Linkage Kit is required to mount the EM9 or M9B Actuator on the VTRE Valve Body. Alternatively a replacement for the VTRA Flanged Valve Body (65-80mm only) may be selected from the the S-E VG311F and V321 3-Port Flanged Valve Bodies, more details can be found in the Venta VG311F 65-150C Specification Sheet and the Venta V321 Specification Sheet N.B. It should be noted that the S-EVG311F and V321 Valve Body are rated PN16 whereas the VTRA was rated PN10.   REPLACEMENT OF VTRA SCREWED CONNECTION VALVE BODY A replacement for the VTRA Screwed Valve Body (15-50mm) may be selected from the MB range of Screwed Valve Bodies, see the MB/MBF data sheet for more details. The MB Screwed Valve Body may be operated by the MD10B series Actuator, see the MD10B specification sheet for more details. Alternatively the MB Screwed Valve Body may be operated by the MD10A Actuator, see the MD10A specification sheet for more details.  
View full article
Picard Product_Support
‎2018-09-10 05:19 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-22 07:08 AM

Labels:
  • Field Devices
5948 Views

Continuum installation error SQLncli_x64.msi file is missing

Issue During Continuum installation error comes up that SQLncli_x64.msi file is missing. Microsoft SQL Server 2005 Setup An installation package for the product Microsoft SQL Server Native Client cannot be found. Try the installation again using a valid copy of the installation package 'sqlncli_x64.msi'. Product Line Andover Continuum Environment CyberStation Windows SQL Cause The Microsoft SQL Server Native Client has not been installed. It must be present before installing Continuum software. Resolution Before installing SQL Server, download and install Microsoft SQL Server Native Client x64 file (sqlncli_x64.msi) from Microsoft Download Center: Feature Pack for Microsoft SQL Server 2005.
View full article
Picard Product_Support
‎2018-09-11 03:05 PM

Labels:
  • Andover Continuum
5902 Views

SNMP with StruxureWare Building Operation

Issue Wanting to use SNMP to be able to create alarm traps from the network Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation site Cause Simple Network Management Protocol (SNMP) is an "Internet-standard protocol for managing devices on IP networks. Devices that typically support SNMP include routers, switches, servers, workstations, printers, modem racks, and more. SNMP is used mostly in network management systems to monitor network-attached devices for conditions that warrant administrative attention such as an alarm in StruxureWare Building Operation.  Resolution For SNMP to be able to create alarms from the network in StruxureWare Building Operation, beginning with Building Operation 1.3 - StruxureWare Building Operation supports an older version of this service which uses the default community password. As such, the decision to open this port should be done based upon a risk/benefit assessment. The only form of SNMP that is currently supported is the ability of SmartStruxure to respond to the network management queries that might be issued by an SNMP client.  Through release 1.5, SNMP is only supervising the equipment and can not receive traps from SNMP. Beginning in the 1.6 release, you can send SNMP traps from an alarm. In future releases it may be able to export alarm traps to SNMP, but this is really an IT function. Release 1.6.1 introduces support for SNMP alarm traps v3.0 notifications. This requires an add-on option on for the corresponding server, either the Automation Server and/or Enterprise Server. Refer to Testing SNMP alarms with SmartStruxure for further help on testing SNMP in 1.6.1 version and above
View full article
Picard Product_Support
‎2018-09-06 01:45 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:18 AM

Labels:
  • EcoStruxure Building Operation
5904 Views

Virtualization or Virtual Machines with EcoStruxure Building Operation

Issue Does EcoStruxure Building Operation support virtualization?  Can the Enterprise and Reports server be on a virtual machine? Can EcoStruxure Building Operation be installed in cloud environments? Product Line EcoStruxure Building Operation Environment VMWare Hyper-V Microsoft Azure Amazon Web Services EcoStruxure Building Operation 2.0 through current release. Cause Desire for virtualization or cloud environment. Resolution Emulating environments Virtualization has several interpretations. In this article, we'll specifically address running EcoStruxure Building Management software in emulating environments like VMware or Hyper-V. These emulating environment software packages replicate a physical PC environment, allowing multiple computers to operate on a single machine, hence the term "virtualization". Several software vendors offer emulating systems, with VMware and Hyper-V being the most prominent. The advantages of running an emulating environment include reduced physical machines, minimized space requirements, and lower maintenance costs.   It's important to note that other potential meanings of "virtualization" such as remote desktop, remote control software, terminal server environment, or cluster environment are not covered in this article.   EcoStruxure Building Management in emulating environments Currently, numerous installations are running EcoStruxure Building Management on VMware and Hyper-V without significant issues. Some challenges have been observed related to Veeam setup, which doesn't seem to integrate seamlessly with ES (and possibly EC).   VMware is utilized internally in R&D and Product Support teams with positive feedback on its performance. Users should have familiarity with the emulating product to configure settings correctly, ensuring network functionality. It's important to highlight that no specific efforts have been made to develop EcoStruxure Building Management to comply with emulating environments. Additionally, there are no specific tests to verify its functionality in emulating environments. Certain issues have been seen with the License system used by EcoStruxure Building Operation when running on specific emulating environments due to limitations in the license system's support for these environments.   Support for EcoStruxure Building Management installations running in emulating environments Product Support provides support for EcoStruxure Building Management software, irrespective of whether it runs on PC hardware or in an emulating environment. Support is provided for problems related to the EcoStruxure Building Management Software itself, but not for issues related to the environment it runs on. Except for approved operating systems and minimum memory requirements, Product Support does not offer guidance on configuring specific PC hardware or emulating environments. Cloud environments Cloud computing environments such as Microsoft Azure and Amazon Web Services provide on-demand availability of computer system resources without direct active management by the user. Cloud computing relies on sharing of resources and typically uses a pay-as-you-go model, which can help in reducing capital expenses.   One of the challenges of cloud computing is reduced visibility and control. Cloud users may not have full insight into how their cloud resources are managed, configured, or optimized by their providers. They may also have limited ability to customize or modify their cloud services according to their specific needs or preferences.   Support for EcoStruxure Building Management installations in Cloud environments EcoStruxure Building Operation has not been developed or tested with Cloud environments in mind and it is therefore not currently a supported environment.  
View full article
Picard Product_Support
‎2018-09-06 01:05 PM

Last Updated: Administrator CraigEl Administrator ‎2024-06-26 11:10 PM

Labels:
  • EcoStruxure Building Operation
5933 Views

EBO SmartDriver and Smart Connector

Issue What is the difference between an EBO SmartDriver and Smart Connector? Product Line EcoStruxure Building Operation Environment Building Operation SmartDriver Cause SmartDriver and Smart Connector enhance the openness for the EcoStruxure Building Operation, EBO, BMS system. They enable integration between EBO and 3rd party systems, even via not supported or nonstandard protocols. Resolution SmartDriver: SmartDriver enables you to create a customized interface to monitor and control 3rd party devices from the EBO server. The following block diagram shows a SmartDriver Interface and a SmartDriver Driver. The SmartDriver Interface (similar in concept to other protocol interfaces such as Modbus and BACnet) is part of EcoStruxure Building Operation software and enables you to create SmartDriver objects in the System Tree pane. The SmartDriver Driver is installed on the server drive and provides the network communications control. More information at Web Help SmartDriver Overview. Smart Connector: A development framework that simplifies and accelerates integrations with third-party systems or other data sources. It is an open, extensible and configurable application framework that allows developers to create innovative new capabilities, applications, and solutions that extend and enhance EcoStruxure Building solutions. The Smart Connector itself runs outside the EBO server and consume or server data to EBO server via the EcoStruxure web services "EWS". Watch short explainer video for more information: https://www.youtube.com/embed/DXHvRRL4ycY   For more information, visit the Smart Connector Developer Community on the Exchange: https://community.se.com/t5/SmartConnector/ct-p/smart-connector   For developers wanting to get started using the Smart Connector framework visit: https://www.smartconnectorserver.com   Smart Connector shop at Exchange:  https://shop.exchange.se.com/en-US/home 
View full article
Janeway Jonas_Brissman Janeway
‎2020-03-06 12:48 PM

Last Updated: Janeway Omaelk ‎2022-10-19 02:28 AM

Labels:
  • EcoStruxure Building Operation
5928 Views
  • « Previous
    • 1
    • …
    • 11
    • 12
    • 13
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now