What is the replacement for a Drayton CRL 240 Actuator / Valve assembly.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the replacement for a Drayton CRL 240 Actuator / Valve assembly.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Gary
    Gary
  • Product_Support
    Product_Support
  • DavidChild
    DavidChild

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8067 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the replacement for a Drayton CRL 240 Actuator / Valve assembly.

Picard Product_Support
‎2018-09-10 12:21 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-19 05:52 AM

Issue

The Drayton CRL 240 Actuator / Valve assembly is to be replaced.

Product Line

Field Devices

Environment

  • Replacement
  • Drayton
  • Actuator
  • Valve
  • CRL 240

Cause

The Drayton CRL 240 Actuator / Valve is obsolete

Resolution

The Drayton CRL 240 Actuator / Valve assembly is obsolete and there is no purpose built replacement.

The associated Drayton Valve Body was available in numerous sizes. 

These sizes are not available in current combined Actuator / Valve designs.

To replace one of the above Actuator / Valve Body combinations the following are required :-

  1. Valve sizes ½” – 2”
    1. Valve – MB(1/2" - 2")
    2. Actuator -  MD10B-230 (  MD20B-230 could  be used if MD10B-230 is not available)
    3. Auxiliary Switch - MD-S1 ( MD-S2 could be used if MD-S1 is not available)
    4. Linkage Kit - LMD/AR-MB
    5. or the RM3601 actuator without the need for a linkage kit
  • Linkage Kit
  • Select S-E LMD/AR-MB Linkage Kit. (914-1071-000)
  1. MBF Valve sizes 65mm – 100mm
  • Could be replaced by the VTRE range

To view the MB Valve Data Sheet, please click here.
To view the MD10B Actuator Data Sheet, please click here.
To view the MD-S1 Auxiliary Switch Data Sheet, please click here.
To view the LMD/AR-MB Linkage Kit Data Sheet, please click here.
To view the LMD/AR-MBF Linkage Kit Data Sheet, please click here.

To view the RM 360 data sheet please click here

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (3)
  • Find more articles tagged with:
  • 5449
  • crl240
  • GaryMontague22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore