Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What is the replacement for a Drayton Theta YBM2A Valve Body / Actuator assembly?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the replacement for a Drayton Theta YBM2A Valve Body / Actuator assembly?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Gary
    Gary
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8152 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the replacement for a Drayton Theta YBM2A Valve Body / Actuator assembly?

Picard Product_Support
‎2018-09-09 11:51 PM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-19 05:50 AM

Issue

The Drayton Theta YBM2A Valve Body / Actuator assembly is to be replaced.

Product Line

Field Devices

Environment

  • Replacement
  • Drayton
  • Actuator
  • Valve
  • YBM2A

Cause

The Drayton Theta YBM2A Valve Body / Actuator assembly is obsolete.

Resolution

OVERVIEW

The Drayton Theta YBM2A Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement.

The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits.

No Valve Body / Actuator assemblies are currently available in these sizes.

Details of the YB Valve Body may be viewed here.

 

VALVE BODY REPLACEMENT

To replace the YBM2A Valve Body the following is required:-

S-E Satchwell MB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2")

Details of the MB Valve Body may be viewed here.

 

ACTUATOR REPLACEMENT

The YBM2A Actuator comprised a 3-wire electrical connection enabling it to be operated by a Mains Voltage changeover contact device as follows :-

Terminal M1 – Open signal

Terminal M2 – Close signal

Terminal M3 – Common

The YBM2A Actuator may be replaced by one or other of the following S-E Actuators :-

MD10B-230

MD20B-230 (if MD10B-230 not available)

Details of the MD10B-230 Actuator may be viewed here.

Details of the MD20B-230 Actuator may be viewed here.

N.B.

The YBM2A Actuator also included an additional 3-wire electrical connection associated with an integral S.P.C.O. Auxiliary Switch wired as follows :-

Terminal S1 – Normally Closed Contact

Terminal S2 – Common

Terminal S3 – Normally Open Contact

Where external wiring is connected to the YBM2A Actuator Auxiliary Switch then an Auxiliary Switch Kit containing a S.P.C.O. Auxiliary Switch should be installed on the MD Actuator.

Auxiliary Switch Kit MD-S1 (914-1060-000)

Details of the MD-S1 Auxiliary Switch Kit may be viewed here.

The MD-S1 Auxiliary Switch Kit should be wired as follows :-.

Terminal S1 – Common

Terminal S2 – Normally Closed Contact

Terminal S3 – Normally Open Contact

 

LINKAGE KIT

A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body.

Linkage Kit LMD/AR-MB (914-1071-000)

Details of the LMD/AR-MB Linkage Kit may be viewed here

In such 3-wire installations the YBM2A Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (2)
  • Find more articles tagged with:
  • 5416
  • GaryMontague22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore