Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Understanding BACnet BBMD Distribution Mask.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Understanding BACnet BBMD Distribution Mask.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • David_Kendrick
    David_Kendrick
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8098 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Understanding BACnet BBMD Distribution Mask.

Picard Product_Support
‎2020-12-17 06:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-09-12 08:46 PM

Issue

When configuring a BBMD what is the Broadcast Distribution Mask and what are the valid settings for the field.

ContinuumContinuum

EcoStruxure Building OperationEcoStruxure Building Operation

Product Line

EcoStruxure Building Operation, Continuum

Environment

  • Building Operation Automation Server
  • Building Operation Enterprise Server
  • Continuum CyberStation
  • bCX4xxx

Cause

Documentation

Resolution

When configuring a BBMD the BACnet protocol defines two methods of propagating the broadcasts messages to other networks.
The two methods are referred to as One-Hop also known as a Directed Broadcast and Two-Hop.

 

Note: In this article the subnet mask is shown using Classless Inter-Domain Routing(CIDR) notation. An IPV4 address is 32 bits long, CIDR notation defines the number of bits used for the subnet mask. The most commonly used are:

  • /8 or 255.0.0.0
  • /16 or 255.255.0.0
  • /24 or 255.255.255.0
  • /32 or 255.255.255.255

One-Hop

With the One-Hop method the local BBMD transfers the message directly to the remote devices via the remote router. In this case the IP routers have to support the transfer of IP broadcast messages to remote IP subnets

Figure 1Figure 1

Figure 1 above illustrates the one-hop method, when the bCX1 which has been configured to take the role of BBMD for network 172.16.0.0/16 detects broadcast messages such as WHO-IS, I-AM etc, it sends a message directly to the broadcast address of the 192.168.1.0/24 subnet, it is then up to Router2 to send the directed broadcast to all devices on the subnet. Any device on the subnet that is acting as a router to other networks will then also re-broadcast the message on those networks. (i.e a bCX hosting an MSTP network on COMM2)

 


Two-Hop

With the Two-Hop procedure a BBMD device transfers broadcast messages to a further BBMD in the remote IP subnet, which then distributes the messages in its local network as IP broadcast messages for its IP subnet. Any device on the subnet that is acting as a router to other networks will then also re-broadcast the message on those networks.(i.e a bCX hosting an MSTP network on COMM2)

Figure 2Figure 2

Figure 2  above illustrates the two-hop method, when the bCX1 which has been configured to take the role of BBMD for network 172.16.0.0/16 detects broadcast messages such as WHO-IS, I-AM etc, it sends a unicast message to each BBMD device on its table, it is then up to each BBMD device on each subnet to send a broadcast that will be heard by all devices on the subnet.


Which distribution mask should be used?

As mentioned earlier, in order for the one-hop method to work, the router on the remote subnet MUST be configured to process incoming messages sent to the broadcast IP address, the two-hop method on the other hand is guaranteed to work, so when in doubt use the two-hop method.
Most sites use two-hop distribution for the reason stated above,, the only obvious disadvantage of the two-hop method is that it is a little more verbose than the one-hop method since the message appears twice on the subnet, once as a unicast sent to the BBMD device and then again as a broadcast sent by the BBMD device.
In Building Operation and Continuum the distribution mask defaults to the two-hop method (/32 or 255.255.255.255)


How to configure the distribution mask

For one-hop enter the subnet mask of the remote network in the distribution mask, the system will apply the mask to the IP address to obtain the broadcast address for the remote network.
For two-hop enter 255.255.255.255, this tells the system not to do a direct broadcast and instead do a unicast to the remote BBMD device.


Sample distribution mask

TinyTake13-09-2022-01-41-59.png

In the BBMD table of a bCX shown in the screen shot above, BDT #1 and #3 use the two-hop method while BDT entry #2 uses the one-hop method.

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
Tags (3)
  • Find more articles tagged with:
  • 15619
  • CraigEllis22
  • DavidKendrick20
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore