Change the firmware version in a Continuum controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Change the firmware version in a Continuum controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6857 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Change the firmware version in a Continuum controller

Picard Product_Support
‎2018-09-10 12:08 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:35 AM

Issue

How to change the firmware version in a controller.

Product Line

Andover Continuum

Environment

All flash-upgradeable controllers: CX9900, CX9940, ACX5720, ACX5740, all i2, b3, and bCX controllers. 

Cause

Controller firmware needs to be changed.

Resolution

  1. Locate the firmware version that you need for each controller you want to change. The Continuum firmware files can be downloaded from the Schneider Electric Ecobuilding Exchange. The downloaded files are often a zip file which includes the release notes in PDF format and the flash file (UPD file).

    Note: You may need to upgrade or downgrade firmware (see also Is a controller shipped from the factory with the latest firmware revision supported in older versio...) Make sure you check the document Andover Continuum Software and Firmware Compatibility Matrix for the appropriate firmware version for your system.
     
  2. Copy the file to a disk drive accessible to your CyberStation workstation.
  3. Edit the controller object in ContinuumExplorer and click on the "Update OS" button.
  4. Browse to the file location in step 2 and click "Open". A progress box "Updating Controller OS..." will appear. During this time the controller is reset and not functional. 
  5. Once complete, and if successful, you will get  a dialog box indicating that the upload was successful and the controller will return On-Line momentarily. Click OK.
  6. Click the refresh button in the controller editor. Once the controller is on-line the version field should indicate the new version.
  7. At this point some controllers may need a reload, others will be reloaded from flash memory. This depends on the controller type. For example, the CX9900 has no flash memory and therefore will need to be reloaded.

This procedure also applies to upgrading controller options such as adding Xdriver support. In this case a UPD file will be provided by the Repair Dept. In the case of added Xdriver support, after doing the Update OS procedure the version will not change. Look at the controller Options tab after it comes back online following the upgrade. The information here, such as a non-zero entry in the numbers next to the appropriate Xdriver Commport will be changed.

The above procedure was based on an IP level controller such as the CX, bCX and ACX II. Infinet and MSTP controllers are done in a similar manner. IOU models are also upgraded similarly via the "Update IOU" button in the IOUModule editor. However, the files are .IOU files instead of .UPD files and the versions are in the fourth pair of characters in the Program ID field.  

Labels (1)
Labels:
  • Andover Continuum
Tags (7)
  • Find more articles tagged with:
  • 5601
  • ACX 57xx
  • bcx
  • cx
  • firmware
  • netcontroller
  • update
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore