Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Update b3 or i2 OS, changing (converting) a controller, BACnet to Infinet or Infinet to BACnet

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Update b3 or i2 OS, changing (converting) a controller, BACnet to Infinet or Infinet to BACnet
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7680 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Update b3 or i2 OS, changing (converting) a controller, BACnet to Infinet or Infinet to BACnet

Product_Support
‎2018-09-07 11:02 AM

Last Updated: ContentModerator Explorer ‎2025-09-25 03:21 AM

Issue

Update OS, changing a controller, BACnet to Infinet or Infinet to BACnet
Can b3 controllers be converted to i2 controllers?
Can i2 controllers be converted to b3 controllers?
Converting between bCX4040 and bCX9640
 

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • i2 b3 Controllers - See Compatibility Matrix
  • bCX Controllers - Continuum 1.7 onwards

Cause

Only a limited number of controllers can be converted, BACnet to/from Infinet, using Update OS.

Resolution

The following controllers can be converted between Infinet and BACnet, using the appropriate firmware files:

  • bCX (bCX4040 to/from bCX9640) (options like Xdrivers, node count, IO modules and expansion IO modules are not effected)
  • i28xx-V - b38xx-V (i2865-V to/from b3865-V, i2866-V to/from b3866-V, i2885-V to/from b3885-V)
  • Please see link for swapping the firmware of non -V model i2/b3

Attempting to flash (Update OS) any other controllers BACnet to/from Infinity is not recommended.
In nearly every instance, the result will be a non-functioning controller.

 

UPDATE:

A procedure is now available to convert the non -V i2s to b3s in the field

https://community.se.com/t5/Building-Automation-Knowledge/Conversion-of-Continuum-devices-from-i2-to... 

 

(Note: In the bCX controllers, the ACCNetID will revert back to the default of "1", you may need to change this in the Controllers configuration webpage back to what it should be.  See Will IP settings persist when flashing a bCX4040 (BACnet) to a bCX9640 (Infinet)? for details.)

 

Please refer to Exchange for specific firmware:

  • BACnet Firmware
  • Infinet Firmware

The following can be used as a general rule to determine which OS is currently running in the controller. bCX only. (b3 & i2 CPU is green)

  • CPU LED is Green = BACnet OS
  • CPU LED is Yellow = Infinet OS
Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 4330
  • AbeMeran23
  • DavidShore19
  • GavinHeward23
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore