Issue
There is no complete end-to-end guide on how to test SNMP alarms in EcoStruxure Building Operation (EBO). Existing documentation only covers creating SNMP alarms, not validating their functionality.
Product Line
EcoStruxure Building Operation
Environment
SNMP Notifications
Cause
Documentation provides steps for creating SNMP alarms but lacks instructions for testing and verifying alarm notifications. For general information regarding SNMP traps, refer to the following Web Help links:
Resolution
Follow these steps to test SNMP alarms in EBO:
-
Install MIB Browser
- Download and install MIB Browser from iReasoning.
-
Load Building Operation MIB File
- Download the Building Operation MIB file.
- In MIB Browser, go to File → Load MIBs, and select the Building Operation MIB file.
-
Create and Trigger an Alarm in EBO
- Configure a simple alarm on a digital point in EBO.
- Ensure the alarm can be triggered manually for testing.
- Configure a simple alarm on a digital point in EBO.
-
Configure SNMP Notification in EBO
- Create an SNMP notification with the following settings:
- Address: SNMP manager IP (use
localhostif manager is local). - User Name: SNMP manager user credentials.
- Address: SNMP manager IP (use
- In Filter Settings, select Normal and Alarm states.
- Add condition:
Source server = *. - Important: Open the SNMP notification object (double-click or press Enter) to access filter settings. Viewing properties alone will not display filters.
- Create an SNMP notification with the following settings:
-
Enable Trap Receiver in MIB Browser
- Navigate to Tools → Trap Receiver in MIB Browser.
-
Trigger the Alarm
- Activate the alarm in EBO.
- Verify that the SNMP trap appears in the MIB Browser’s Trap Receiver window.