Using Modbus Register Group to batch read registers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Modbus Register Group to batch read registers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6980 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Modbus Register Group to batch read registers

Picard Product_Support
‎2018-09-11 04:22 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:56 AM

Issue

Modbus Register Groups feature can overcome some Modbus communication problems. It has been seen before where the Modbus controller falls offline for a few seconds then comes back online. This cycle will repeat every few seconds. When register groups are not used, there may also be issues with the amount of time it takes for a Modbus points to update.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation
  • Building Operation Enterprise Server
  • Building Operation Automation Server Premium (AS-P)
  • Building Operation Automation Server Bundled (AS-B)

Cause

In a normal Modbus network, a Modbus polling device obtains data from a polled device by sending a query message to the device and then waiting for the response message that contains the requested value from the selected register. If data from another register is required, the polling device sends out a new query message and awaits the response message. This process is repeated until all subscribed points values have been read.

The Modbus Register Groups are a batch read function to poll Modbus devices. Instead of reading each register individually, the batch read function reads registers in manually created groups. When all registers in a group have been read, the response message returns subscribed register values for the whole group. Register grouping provides a dramatic saving in the time taken to poll your devices.

For more guidance and tips on this topic, see Section "Batch Read Function" in the EcoStruxure Building Operation Technical Reference Guide. 

Note: When viewing a graphic containing Modbus values, those values will update at the same interval as their Modbus register group.

Resolution

When grouping Modbus points, it is important to keep in mind some of the following points.

  • Try to ensure that as many Modbus points as possible are contained in as few groups as possible. This will reduce the overall time it takes the Enterprise Server or Automation Server to read all the subscribed points in each Modbus device.
  • Network performance can be enhanced by choosing the method of grouping that is most suitable for each device in the Modbus network. 
  • Network performance can be enhanced by selecting a different default poll time for each register group. Network performance can also be enhanced by grouping points that have the same or similar polls. Start with higher group poll times to ensure a stable system before reducing the poll time.
  • Make sure to delete Modbus points out of a register group individually before deleting the group. If this is not done, it can cause system delays.
  • See article Modbus Batch Read Multiple Registers Groups

Creating a Modbus Register Group

  1. In Workstation, in the System Tree pane, right-click on a Modbus device and select New Object (1).  In the create object window select Modbus Register Group (2), provide a name and select Create (3).
    01. Create Group.png
  2. Now that the group has been created, existing Modbus points can be dragged and dropped into the group.
    02. Move Points to Group.png
  3. New Modbus points can also be created in the group.  Right-click on the Modbus Register Group and select New Object (1).  In the create object window expand Modbus Point (2), select a point type (3), provide a name and select Create (4).
    03. Add Points to Group.png
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (8)
  • Find more articles tagged with:
  • 13628
  • DavidShore20
  • GavinHeward23
  • PeterLarsen21
  • PeterLarsen24
  • populating
  • RobertAndriolo21
  • updating
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore