Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 96
    • 97
    • 98
    • …
    • 508
  • Next »

Difference between Deny Entry Sched (Schedule) and Deny Entry Sel (Select) transaction messages when using Traditional Elevator Control

Issue Receiving "Deny Entry Sched." (Schedule) transaction message for all individuals on a single Interface (SLI). Receiving "Deny Entry Sel." (Select) transaction message for all individuals on a single Interface (SLI). Product Line TAC INET Environment I/NET Seven Traditional Elevator Control Cause In traditional elevator control, the Reader (Door Point) must have a schedule assigned for the Group / Individual to allow access to the Lift (reader) itself. Then in Floor Maps you can allocate access to the individual Floor Points. In the floor mapping you must also remember to allocate the associated floor points otherwise the Individual is not Scheduled to have access to the floor (Hence a Deny Entry Sched message is received). Recommendation is to migrate sites to Extended Elevator Control which makes this process much simpler. For details of this refer to Extended Elevator control (Step by step instructions). Resolution Under Access Elevators check that the Floor mapping is correctly set for each Floor DO point. If no DO 's are selected for that particular Tenant Schedule, the individual will receive a Denied Entry Sched when attempting to gain access to the floor. Deny Entry Sel (Selection) is received when the Elevator Reader is not selected for the Tenant / Group or Tenant / Individual. A schedule (Group or Personnel) must exists on the reader (door ) point for the Group or Individual in question. A list of all Event messages, and their descriptions, received in AMT is available in AMT Event message definitions.
View full article
Picard Product_Support
‎2018-09-10 07:48 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:16 AM

Labels:
  • TAC INET
1753 Views

Major changes in Xenta 102-AX version 2.19

Issue Xenta 102-AX version 2.19 included 6 major updates and changes. They are outlined below. Product Line TAC Vista Environment Vista Xenta 102-AX Cause M/STAT Air Flow Calibration Errors Error Description: When calibrating a Xenta 102-AX using the M/STAT a Velocity Pressure Offset is not generated in circumstances where one would be generated in the 102-AX Plug-in. This adversely affects the accuracy of the calibration, in particular at the low flow setting. Note: All steps for calibration using the M/STAT are found in Calibrating Airflow on a Xenta 102-AX (or MR-VAV-AX) using the M/STAT. Workaround: Perform the calibration using the LNS 102-AX plug-in tool or the TMGL plug-in tool Xenta 102-AX does not perform wink function properly Error Description: Attempts to perform the wink function fail. When a wink function is performed, the red light on the controller is expected to come on and flash to identify the controller and the STR-250 should display "00" with the man logo displayed as well. This should last approximately 45 seconds. STR-250 connected to the Xenta 102-AX is not controlling the fan properly Error Description: The STR-250, stat when connected to the Xenta 102-AX, reacts incorrectly to buttons being pressed when in the fan menu. The increase button causes a decrease and the decrease button causes an increase among other odd behaviors. Also, if the fan is set to shut off (this action should not be allowed) the Xenta 102-AX performs a resynchronization. Pressure dependent mode erroneously requires airflow and fan enabled Error Description: The 102AX requires 80% Airflow Setpoint to run Heat1 in Pressure Dependent mode. Xenta 102-AX Hot Water floating control resynch fails Error Description:  When the Xenta 102AX does a hot water floating control valve resynch based on being in the 10-90% "happy" zone for 60 seconds and then goes to 100% it does not resynch at the 100% open position for the full stroke time. It gets to 100% commands the resynch, then closes the valve, re-opens the valve to 100% then allows the valve to control back to a normal position. Xenta 102-AX Floating Hot Water valve control failures Error Description:  Heating outputs stop working on Xenta 102-AX sporadically causing hot water valve to open even though application is calling for it to be closed. This occurs when the 102-AX is set up for a floating valve actuator (PWM 2) and occurs sometimes within a day but could take a few of days to show up. The resynchronization of the valve seems to have no effect and the only way to fix the controller is to cycle power or by switching nviEmergCmd to something other than its default and then back again a moment later. Resolution If any of these errors are occurring, upgrade the Xenta 102-AX to version 2.1.9 or higher. Click here to download the APB file. Complete upgrade instructions can be found at Upgrading a Xenta 102-AX to version 2.16 or later Version 2.19 addresses the problems listed above as follows: M/STAT Air Flow Calibration Errors Fix: When calibrating a Xenta 102-AX using the M/STAT a Velocity Pressure Offset is now properly generated. Xenta 102-AX does not perform wink function properly Fix: After clicking Wink the a red LED on the controller flashes to identify the controller and the STR-250 displays "00" and the man icon. After approximately 45 seconds both the controller and the STR-250 return to normal. STR-250 connected to the Xenta 102-AX is not controlling the fan properly| Fix: The ability of the STR-250 to override the fan command on the 102-AX is disabled by default. If this functionality is required it can be turned on by setting DamperActuator.SCPTdirection.bit15 to 1. Pressure dependent mode erroneously requires airflow and fan enabled Fix: The 102AX no longer requires 80% Airflow Setpoint to run Heat1 in Pressure Dependent mode. Xenta 102-AX Hot Water floating control resynch fails Fix:  Logic has been corrected to only resynch open or resynch closed as needed. Additionally, the heating output resynchronization algorithm has changed to operate as follows: Two internal timers have been added to track the accumulated amount of time that heat load is 0% and at 100%. Once either of these timers reaches 30 minutes, a resynch is initiated in the respective direction of the timer. The resynch consists of activating either the open or close triac output for an amount of time equal to the user defined stroke time. Xenta 102-AX Floating Hot Water valve control failures Fix:  Heating output logic corrected to prevent failure.
View full article
Picard Product_Support
‎2018-09-10 10:26 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:15 AM

Labels:
  • TAC Vista
2016 Views

Temperature Inputs on controller having sporadic readings of +327

Issue Fluctuating temperature readings where they jump up to +327 randomly. Product Line Andover Continuum Environment Continuum controllers i2866-V Cause Readings like that are usually caused by wiring or power issues. There was also a Firmware fault that caused this in an old version of the i2866-V Firmware. Resolution Confirm the following wiring considerations:   That your input and output cables shield is wired to Earth ground at one end of the run only (preferably the controller chassis). That your controllers power supply is earthed on the secondary side of the 24vac transformer to ensure a proper controller ground to Earth. Confirm that the power supply is not being shared with any field devices, especially field devices feeding inputs back into the controller. One way to troubleshoot if it is a cabling or controller problem is to replace the sensor cable with a 10K ohm resistor. See Temperature inputs not reading the correct value for details. Also, in i2866-V controllers with firmware versions less than v3.501049, temperature inputs could randomly go to +327 when Analog Outputs were changing value frequently. Uprev your controller. See TPA-BOST-09-0007.00 for details.
View full article
Picard Product_Support
‎2018-09-10 08:35 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:14 AM

Labels:
  • Andover Continuum
2336 Views

Vista Server start hangs on trend log initialization

Issue When starting the Vista Server, the splash screen displays the current state of the startup.  It gets to the "Trend Log Initialization" screen and then hangs. Product Line TAC Vista Environment Vista Server Cause Queued files in the $queues folder in the Vista database are being written to the SQL database.  If the queued files folder has grown very large, it can take a very long time (hours) to write this data to SQL.  If the connection to the SQL database has been broken, then it will take an infinite amount of time. Resolution Check for queued files in the $queues folder Navigate in a Windows Explorer window to the Vista Database. (If you are unsure of the location, you can verify it in the TAC Vista Server Setup Vista Database tab). Go to the $queues folder Look inside the insertevents and insertlogvalues folders. This is where data is stored temporarily before it is written to the SQL database. Having queued files is not necessarily a sign of a problem. However, if there is a connection problem, these folders will continually grow in size without older queued files being written from the folder. Allow time for the files to write the SQL Start Vista Server. Insure that TAC DSS Writer Service is running. When it gets to trend log initialization, leave the PC alone and allow time for the files to write to the SQL server.  If the size of the $queues folders are shrinking, then the process is working and after enough time, the server will start. Note: If you have cleared the $queues folder but it still hangs on trend log initialization, still allow plenty of time for the server to come up. There is a good chance that the Xenta controllers are passing all of their trend logs over to the SQL server. This could take hours or even overnight to complete. Delete the queued files If the data is not of dire importance, delete all the files inside both of the $queues folder.  For an efficient method for deleting many queued files, see An efficient method for deleting all queued files in the $queues folder. Check the SQL connection Open the TAC Vista Server Setup In version 5.1.3 and prior: Start > Programs > TAC > TAC Vista Server X.X.X > Server Setup In version 5.1.4 and later: Start > Programs > Schneider Electric > TAC Vista Server X.X.X > Server Setup Go to the SQL Server tab In the lower right-hand corner of the tab, press the Test Connection button. If it pops up a window that says "Connection test succeeded!" then your SQL connection is okay. If it fails the connection test, check the instance name. If you are using default settings it should be: SQL Server name: PCname\TACVISTA or (local)\TACVISTA Log database name: taclogdata If these are set correctly and the connection still fails, one method for reestablishing the connection is to uninstall/reinstall the Vista software. Remove TRL files This can also occur if the database has been upgraded from a lower versions, and still has information in the TRL files in the database. Stop the server Locate all TRL files in the $thisfil folder Delete any TRL file over 32Kb. Start the server again.
View full article
Picard Product_Support
‎2018-09-07 08:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:13 AM

Labels:
  • TAC Vista
1655 Views

Personnel does not have access. Invalid Attempt messages stating "Personnel record is not yet active" seen in the Access Events

Issue Personnel does not have access. Invalid Attempt messages stating "Personnel record is not yet active" seen in the Access Events. Product Line Andover Continuum Environment Continuum Access Control Cause Personnel object Activation Date attribute is set to a future time. Resolution Open the Personnel object and confirm the Activation Date and Expiration Date fields are realistic. Make sure the Activation Date is in the past. Check that the time on the Controller and Cyberstations are synchronised properly. See Configure Time Zone and UTC Offset settings so that time is synchronized across your system for how.
View full article
Picard Product_Support
‎2018-09-11 07:42 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:10 AM

Labels:
  • Andover Continuum
1655 Views

I/NET physical layer issues

Issue I/NET Physical Layer Issues, Lan Reconfigure, and/or Controllers going on or offline 1 at a time. Product Line TAC INET Environment I/NET Cause Physical Layer Issue Resolution Some or all of the following may indicate a physical layer issue. Abnormally large number of Lan Reconfigure messages Controllers going offline individually or in groups and sometimes all together Large numbers of Station Lost/Restore Messages Frequent problems connecting to controllers and data interruption To Troubleshoot a suspected Physical Layer error: Determine if this is a Controller LAN layer issue by direct connection to the Controller LAN using a tap.  If you continue to experience the same errors, as while connected via TCP/IP then the issue is on the Controller LAN Verify that you are using the correct wire gage (22 or 24) and that you controller LAN is less than 4000 feet for 24 AWG and less than 5000 feet for 22 AWG. Verify shield drain wire. Shield drain wire continuity must be maintained as the LAN cable passes through each controller. Shield drain wires from each controller LAN cable must be twisted together, insulated, and tied back such that wires do not come in contact with ground or any conductive surface within a controller. Shield drain wire must be directly connected to Electrical Service Earth Ground at only one end of the cable. The issue at this point can either be a wiring fault or a controller that is broken. Disconnect all controllers from the controller LAN by removing the LAN terminal strip from each controller Reconnect each controller one at a time and watch for the original errors. During this process a LAN Reconfigure is expected each time a device comes online While at each controller watch for any frayed wire, unusual/unneeded splices and if needed re-seat each wire into the terminal block When a controller is brought online and the error returns, examine that leg of the LAN wire for shorts or replace that section of wire Replace the suspect controller with a different device to ensure that the controller is not the source of the problem. (On critical systems you can plug in a spare controller at the location for testing without taking the existing controller offline) Typically if a controller is causing the error it will display alarms or LAN reconfigure on it's LEDs. Consult the TCON for the specific controller for more details (TCON Cross Reference available in TCON Number and Title Cross Reference (with links)). If it is not feasible to replace long sections of wire, or if it is determine that the controller LAN exceeds the specified length, then you may want to consider using Distributed Link Architecture.
View full article
Picard Product_Support
‎2018-09-07 02:09 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:09 AM

Labels:
  • TAC INET
1702 Views

WebPinpoint crashes on Failed to call piLiveData>GetLiveData(). AccdataServices has an error

Issue WebPinpoint crashes on "Failed to call piLiveData>GetLiveData(). AccdataServices has an error" on both WebServer and Client PCs. Product Line Andover Continuum Environment WebClient IIS WebPinpoint Pinpoint  Cause The asp_net account does not have permission to access the ILiveData interface. ILivedata is an internal engine that WPinpoint uses for polling points values.   Resolution In Workstation Preferences on the Web Server, increase the value of WPinPoint Continuous Polling Rate until  from crashes no longer occur.  If this is for a Windows Server 2008, Windows 7 or Windows Vista, make sure the web.config file has been edited. See also Error: "DNWacserverFactory/WACServerFactory.soap" when accessing Webclient 1.9x Pinpoint.
View full article
Picard Product_Support
‎2018-09-10 03:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:08 AM

Labels:
  • Andover Continuum
1665 Views

I/NET support for dual Network Interface Cards (NIC)

Issue Does I/NET support dual NICs (Network Interface Cards)? Is it possible to change which network interface card I/NET uses? Dual Network Interface Cards (NIC) will not allow selection between the Networks, option is grayed out. Product Line TAC INET, EcoStruxure Building Operation Environment I/NET 2.40 and above Cause Requirement for I/NET to have dual NIC support and option to change which network interface card I/NET uses. Resolution A New feature released with I/NET Seven 2.40 now allows I/NET to support dual network interface cards (NIC). The intent is to allow I/NET and Video the capability of using different Ethernet networks. This option also allows which network I/NET (and / or Video) uses. These settings are changed via the Advanced WAN Configuration (Advanced IP button) via the I/NET Configuration Editor (see image below). Requirements: I/NET Configuration needs to have TCPIP enabled and hardware (Ethernet card) needs to be installed on PC, I/NET (or I/O Server) must be running to select the Advanced IP button (Advanced WAN Configuration). If the PC is configured with multiple network cards, the above shown drop-down lists will be active: I/NET network Video network Use the drop-downs to select a network card for each network. You can use the same card for both networks, or you can use a unique card for each network. By using two networks, you can separate I/NET traffic from video traffic and conserve bandwidth on each network. NOTE: If you have dual Network Interface Cards and you are not able to select between these networks (so they are grayed out) you must have the following minimum requirements configured for this option to be available in the I/NET Editor: A Physical connection to its connection media. (i.e. A connected network status. If you have a status indicating Limited or no connectivity you will not be able to select between Interface cards). Valid IP address and subnet mask Valid Gateway IP address. (If you have no gateway router on the network then select a valid IP address within the same IP range, usually the IP of the PC is the best option here.) If you are using wireless NIC and have issue to choose it, refer to Host number conflict on a computer with dual Network Interface Cards (NIC).
View full article
Picard Product_Support
‎2018-09-10 01:59 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:07 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1876 Views

Integrating Xenta programmable controllers into a Niagara R2 UNC-520 Controller

Issue Since both products -- Xenta programmables and the UNC 520 -- speak LON protocol, there is some assumption that integration should be seamless.  In the case of ASCs, this is true, but Xenta programmable controllers use some forms of proprietary communication that can complicate the integration. Product Line TAC IA Series, TAC Vista Environment Xenta programmables Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B UNC-520 Niagara Tridium Cause Xenta programmables use proprietary communications for three main purposes: To communicate their online status between group members and group masters To communicate between a base unit and associated I/O modules To pass proprietary TAC Network Variables between two programmable controllers In a UNC-520, the first function would be taken over by the new network manager (Local Lon Device).  However, the second two must use Group Bindings set through a Vista compatible network management tool like LonMaker or NL220.  If the controllers are commissioned into the UNC-520, that communication will be broken and I/O modules will go offline and no network variables will pass. Resolution  It is possible to engineer a TAC Vista network as usual, using an LNS management tool to create group bindings to facilitate proprietary communications.  A UNC-520, set to non-network management mode could then be implemented on top. However, any attempt to commission the devices into the UNC-520 network will break that proprietary communication.  To prevent this scenario from occurring, the simplest method is: Do not use proprietary TAC Network Variables to pass data between controllers. Use only SNVTs which will be available to a third party LON network manager like the UNC-520 Make no SNVT bindings in a temporary LonMaker or NL220 database.  Let the UNC-520 handle all network management duties. Do not define Xenta I/O modules in the Menta Device Specification. Use only Xenta 421A, 422A, 451A and 452A I/O modules.  These have the capability to act as stand-alone LON nodes. Define the modules as LON nodes, configure them using Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node. Bind to the inputs and outputs of the I/O modules in the UNC-520.
View full article
Picard Product_Support
‎2018-09-07 05:41 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:06 AM

Labels:
  • TAC IA Series
  • TAC Vista
1957 Views

Receive "TAC C503Boot/x.x.x.x not configured" message when navigating to the Xenta Server web interface

Issue Receiving the following error when attempting to navigate to the Xenta web interface. "TAC C503Boot/x.x.x.x not configured". Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Server 511, 527, 555 Xenta Server 701, 721, 731 Cause Device web interface has stopped working or flash drive / hard disk has been corrupted on the Xenta Server. Resolution Attempt the following steps to resolve this problem: Try restarting the device and see if the unit comes back online, remember to wait 1-2 minutes for the unit to restart.  Check the RUN LED on the panel, if the LED is a solid green this indicates the device is running normally, and your access should be restored. If the LED is RED, solid or flashing this would indicate a problem with the device. Attempt to restore or upgrade the device to the latest firmware.    You can download the latest firmware version from the Schneider Electric Exchange. If this fails then then reference Xenta Server "Run" light is solid red with no communication via Ethernet.
View full article
Picard Product_Support
‎2018-09-07 01:30 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 02:00 AM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
1872 Views

Problems receiving emails from Xenta Server

Issue Problems receiving emails from Xenta 511/527 Product Line TAC INET, TAC Vista Environment Xenta Server Xenta 511, 527, 701, 711, 721, 731, 913 Cause Some email servers have been found to filter UTF-7 character encoding as spam. The Xenta products require this encoding to support Swedish characters, but this can be configured by manually editing some files. Resolution Use an FTP program (Internet Explorer) to connect to the Xenta you are trying to change and download the \sys\langstring.cfg file. Edit the file and modify the following lines to replace all instances of 7 with an 8: ALARM_CODE_1= =?utf-7?Q? ALARM_CODE_3=charset=UNICODE-1-1-UTF-7 Upload the edited file back to the Xenta device Cycle power The device will now use UTF-8 character encoding which is more commonly used in the United States. For more troubleshooting tips, see Troubleshooting sending emails from a Xenta Server.
View full article
Picard Product_Support
‎2018-09-07 12:39 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:59 AM

Labels:
  • TAC INET
  • TAC Vista
1961 Views

Location of Technical Product Advisory's (TPA)

Issue Where are the reports of fixed issues/bugs for the various product lines located? Product Line TAC Vista, TAC INET, Andover Continuum, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, EcoStruxure Building Operation, EcoStruxure Building Expert, Access Expert, Security Expert Environment Technical Product Announcements Cause TPAs contain information of changes made per version of the different product lines. A TPA may report enhancements and/or broken functionality. Resolution Navigate to Exchange Extranet to view all TAC Vista documents tagged as TPA. The documents will be listed in reverse chronological order. Log in to view these documents. See Register for The Exchange Download Center for more information on registration.
View full article
Picard Product_Support
‎2018-09-11 04:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:58 AM

Labels:
  • Andover Continuum
  • EcoStruxure Access Expert
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1779 Views

I/NET AMT Time Sync Error

Issue 3:15am Time Sync error in AMT Product Line TAC INET Environment I/NET site with DCU Time Sync enabled Daylight Savings Time Cause Outdated SAV file No DST observed Enabled DCU Time Sync from Host PC Resolution Make sure versions of Bin Files are up to date with current revision of I/NET across all controllers. For how to do this read How to upgrade bin and SAV files in I/NET controllers.  Make sure SAV files are backed up and current. For how to do this read How to upgrade bin and SAV files in I/NET controllers. As the host workstation synchronizes the daylight savings time settings in a controller, it will also check for the existence of a corresponding SAV file. If a SAV file for the controller is found, the host workstation processes it as follows SAV file is current If the controller's SAV file is current, the host automatically updates it with the daylight savings settings from this editor. This ensures that if you later restore the controller using this SAV file, the correct daylight savings time settings will be downloaded. SAV file is old If the controller's SAV file is out-of-date, the host does not change it. In this case, you can manually update the controller's SAV file or use the Automatic DCU Save function in order to create an up-to-date SAV file for the controller. Refer to Station Save and Restore for more information.  Beginning with I/NET revision 2.41, I/NET allows the DCU Time Sync and no observance of DST.  Work around is to remove DCU Time Sync if your time zone does not observe DST.
View full article
Picard Product_Support
‎2018-09-06 09:37 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:58 AM

Labels:
  • TAC INET
1719 Views

ENC or Enterprise Network Server I/A Series G3 Modbus TCP communications to Modbus devices stop

Issue I/A Series G3 Modbus TCP communications to random Modbus devices randomly drop offline and stop communicating with the ENC or Enterprise Network Server.  Both the modbusCore and modbusTcp modules are at version 3.6.31. Product Line TAC IA Series Environment I/A Series G3, Modbus TCP 3.6.47 and lower Cause There were a few updates to the Modbus core and TCP modules between 3.6.31 and 3.6.47. Issue 18656 corrected communication reliability when there are a large number of Modbus TCP devices under a single ModbusTcpNetwork. Issue 19897 corrected transaction ID synchronization when a retry occurred. Issue 23578 added the ability to control the maximum transactionID used for ModbusTcp (I/A Series G3 Modbus TCP communications to Siemens Moore 353 controller stops updating after a period of time after ENC/JACE reboot or station start). Resolution Download the following modules from The Exchange Download Center: modbusCore-3.6.47.1.zip modbusTcp-3.6.47.1.zip Install to the appropriate I/A Series G3 Workbench modules folder Upgrade the modules in the ENC/JACE.
View full article
Picard Product_Support
‎2018-09-11 03:59 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:56 AM

Labels:
  • TAC IA Series
1686 Views

Time Zone Database shows +0 for all time zones when the platform date is in 2016

Issue Time Zone Database shows +0 for all time zones when the platform date is in 2016. IA Series G3 version 3.6.407 IA Series G3 version 3.7.108 IA Series G3 version 3.8.41 Product Line TAC IA Series Environment IA Series G3 versions 3.6.407, 3.7.108, and 3.8.41 Cause This error appears when listing the contents of the Niagara Time Zone database where the Time Zone Database shows +0 for all time zones when the platform date is in 2016.  The issue is related to an error within the 3.8.41 baja and hx modules and only affects the display within the Platform view only.  The actual behavior and operation of the Time Zone remains accurate.  Prior IA Series G3 versions (e.g. 3.8.38, 3.7.106, and 3.6.406) or earlier will not exhibit this issue. Resolution Download and upgrade the baja and hx modules available in the latest consolidated patch files. baja 3.6.407.3 (or higher) and hx 3.6.407.1 (or higher) baja 3.7.108.3 (or higher) and hx 3.7.108.1 (or higher) baja 3.8.41.2 (or higher) and hx 3.8.41.1 (or higher) The consolidated patch files are available for download on the Buildings Download Center.  Login to the Schneider Electric Buildings Download Center and enter Consolidated_Patches in the search area (reference Latest consolidated patch files for I/A Series G3 maintenance builds with details).  Download and install the appropriate patch for the version.
View full article
Picard Product_Support
‎2018-09-10 01:51 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:56 AM

Labels:
  • TAC IA Series
2002 Views

Xdriver enabled on Comm port, but no xdriver option list down for the comm port type

Issue Xdriver is enabled,   Open the BCX1 editor, click "options" tag, display comm port attribute as"Xdriver comm1: 00000009", but there is no "xdriver" listed from the drop down menu when click the arrow on the right of default type of the comm port. Product Line Andover Continuum Environment BCX1-CR-X, 4.500065 Cyberstation 1.81 Cause Continuum support xdriver with BCX1-CR(BCX4040) from 1.82, any version earlier than 1.82 not support xdriver with BCX1-CR controller. Resolution Upgrade all the Cyberstation to 1.9X. To determine if a controller comm port is Xdriver enabled, refer to Determine if a controller comm port is Xdriver enabled.
View full article
Picard Product_Support
‎2018-09-11 07:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:55 AM

Labels:
  • Andover Continuum
1718 Views

How to setup automatic table truncation on Single-User SQL Express systems

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue How to setup automatic table truncation on Single-User SQL Express systems. Product Line Andover Continuum Environment Continuum Cyberstation Single-User SQL Express SQL Server 2005 Cause Only the ExtendedLog table is automatically truncated on an Single-User SQL Express Continuum system. The other tables that can fill up quickly and need to be truncated regularly are not catered for (accessevent, activityevent, alarmevent, and errorevent). Resolution IMPORTANT: Make sure to perform a full SQL Database backup before attempting to make any changes to the database. (See Move / Backup / Restore a database on a Single User SQL2005 Express system for details on how to backup your database and, if not already installed, where to get Management Studio from) Use the attached file SQLExpress to add table truncations.zip, to configure your Single-User SQL Express system to automatically truncate these tables when it does the ExtendedLog truncation. After downloading the file, follow the steps below. There are three files in the archive, these need to be copied to your Continuum folder on your Single-User system running SQLExpress as the database engine. LogTruncate.SQL This file is the SQL script that performs the truncation of the four tables (accessevent, activityevent, alarmevent, and errorevent) to the number of days you specify - I have selected 90 days as my default but you can change this to whatever you require for each table. CS_LogTruncate_OneOff.bat This batch file will run the LogTruncate.sql script once when manually executed. You will need to change the server name "PC3" to whatever your PC's name actually is on your system. CS_Hrly - with LogTruncat.bat This is the batch file that will be renamed and replace the existing "CS_Hrly.bat" file currently located in your Continuum folder. This is the same as your current file except it has added the LogTruncate.sql script so that this will now be executed every hour along with the rest. Backup "CS_Hrly.bat" file in Continuum folder by renaming the file to something like "CS_Hrly ORIGINAL.bat". Rename "CS_Hrly - with LogTruncat.bat" to "CS_Hrly.bat", copy into (overtop the existing file if you haven't renamed it) the Continuum folder, and change the server name "PC3" to your PC's name. This should now execute this table truncation script along with the other database maintenance scripts every hour.
View full article
Picard Product_Support
‎2018-09-10 10:05 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:54 AM

Labels:
  • Andover Continuum
1920 Views

The File or Directory \VISTA DB\$queues\insertevents is corrupt and unreadable

Issue Error Messages: Windows - Delayed Write Failed Windows was unable to save all the data for the file D:\VISTA DB _23032011\$queues\insertevents. The data has been lost. This error may be caused by a failure of your computer hardware or network connection. Please try to save this file elsewhere. Windows - Corrupt File The file or directory \VISTA DB _23032011\$queues\insertevents is corrupt and unreadable. Please run the Chkdsk utility. Product Line TAC Vista Environment TAC Vista Cause Problem with Operating System (or) Hard Disk Fault (or) Link between $queues with Vista Database. Resolution As there may be several issues that are causing this, there are three options to look at: OPTION 1: Restore the OLD TAC Vista Data Base Backup. Refer to TAC Vista Technical Manual chapter 26 for re-storing database procedure.   OPTION 2: There might be a linking problem with this folder and Vista.  Here are the steps to check if this is the problem: If the problem still exists, Check for hard disk errors. Find the $queues - folder in existing database folder ( \DB\$queues) Copy the files to an other location and delete current folder (Refer to An efficient method for deleting all queued files in the $queues folder) Recreate it with same folder names and copy back the files into $queues-folder. If the problem still exists, Check for hard disk errors.   OPTION 3: Check for hard disk errors, follow the below procedure: Go to "My Computer", Right click on Hard Disk Drive – typically - C, and Click on Properties. Go to Option "Tools" and Click on "Check Now" under "Error-Checking"
View full article
Picard Product_Support
‎2018-09-10 11:19 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:53 AM

Labels:
  • TAC Vista
1597 Views

Database size limitation and recover options on a Single User system in Continuum

Issue Is there a limitation to the size the database can be on a Single User system in Continuum? Product Line Andover Continuum Environment Single User Continuum system MSDE database Cause Microsoft has put a limitation in the size of the MSDE database. Once you hit this limitation your Single User Continuum system will not operate properly. Resolution The size limitation is 2 Gb. It may be possible to recover after hitting this limit by removing un-needed log entries from the database, but this is not always a guarantee you will be able to recover the database. Another way to recover from this is to back up the database, if you can, and restore it to standard SQL installation. From this point you can remove any unwanted logs and shrink the database. Then you can back up the database and restore it back to the Single User system. Another way to recover from this is to back up the database, if you can, and restore it to standard SQL installation and convert the Single User system to a LAN installation. Finally if all the above do not work for your system you will have to restore from the last known good backup of the database. See Microsoft Database size Limitations and Continuum for SQL Express information.
View full article
Picard Product_Support
‎2018-09-07 12:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:52 AM

Labels:
  • Andover Continuum
2027 Views

Set extra DCOM Settings when TAC Vista Server and Remote Workstation in Workgroup.

Issue Set extra DCOM Settings when TAC Vista Server and Remote Work Station in Workgroup. Environment TAC Vista Server Remote Workstation Cause Cannot access TAC Vista Server from Remote Workstation, even though DCOM's set properly (in Workgroup). Resolution When using Remote Workstation and TAC Vista Server in same Workgroup and completing the DCOM settings based on the TAC Vista Installation Manual (04-00001-xx) and you still cannot access the TAC Vista Server PC, try the settings in the attached the document. Click here to download. Also refer these articles for more information: Helpful Vista Utilities - Configure DCOM instantly, Register ASP.NET Error: The RPC server is unavailable. Connecting from a TAC Vista Remote Workstation says "Ensure that TAC Vista Server is started" error, even though DCOM is set correctly Necessary Accounts for DCOM and Firewall Security Settings
View full article
Picard Product_Support
‎2018-09-10 01:34 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:51 AM

Labels:
  • TAC Vista
1878 Views
  • « Previous
    • 1
    • …
    • 96
    • 97
    • 98
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of