Major changes in Xenta 102-AX version 2.19

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Major changes in Xenta 102-AX version 2.19
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • LeeCravens
    LeeCravens
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1958 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Major changes in Xenta 102-AX version 2.19

Picard Product_Support
‎2018-09-10 10:26 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:15 AM

Issue

Xenta 102-AX version 2.19 included 6 major updates and changes. They are outlined below.

Product Line

TAC Vista

Environment

  • Vista
  • Xenta 102-AX

Cause

  1. M/STAT Air Flow Calibration Errors
    Error Description: When calibrating a Xenta 102-AX using the M/STAT a Velocity Pressure Offset is not generated in circumstances where one would be generated in the 102-AX Plug-in. This adversely affects the accuracy of the calibration, in particular at the low flow setting.
    Note: All steps for calibration using the M/STAT are found in Calibrating Airflow on a Xenta 102-AX (or MR-VAV-AX) using the M/STAT.
    Workaround: Perform the calibration using the LNS 102-AX plug-in tool or the TMGL plug-in tool
  2. Xenta 102-AX does not perform wink function properly
    Error Description: Attempts to perform the wink function fail. When a wink function is performed, the red light on the controller is expected to come on and flash to identify the controller and the STR-250 should display "00" with the man logo displayed as well. This should last approximately 45 seconds.
  3. STR-250 connected to the Xenta 102-AX is not controlling the fan properly
    Error Description: The STR-250, stat when connected to the Xenta 102-AX, reacts incorrectly to buttons being pressed when in the fan menu. The increase button causes a decrease and the decrease button causes an increase among other odd behaviors. Also, if the fan is set to shut off (this action should not be allowed) the Xenta 102-AX performs a resynchronization.
  4. Pressure dependent mode erroneously requires airflow and fan enabled
    Error Description: The 102AX requires 80% Airflow Setpoint to run Heat1 in Pressure Dependent mode.
  5. Xenta 102-AX Hot Water floating control resynch fails
    Error Description:  When the Xenta 102AX does a hot water floating control valve resynch based on being in the 10-90% "happy" zone for 60 seconds and then goes to 100% it does not resynch at the 100% open position for the full stroke time. It gets to 100% commands the resynch, then closes the valve, re-opens the valve to 100% then allows the valve to control back to a normal position.
  6. Xenta 102-AX Floating Hot Water valve control failures
    Error Description:  Heating outputs stop working on Xenta 102-AX sporadically causing hot water valve to open even though application is calling for it to be closed. This occurs when the 102-AX is set up for a floating valve actuator (PWM 2) and occurs sometimes within a day but could take a few of days to show up. The resynchronization of the valve seems to have no effect and the only way to fix the controller is to cycle power or by switching nviEmergCmd to something other than its default and then back again a moment later.

Resolution

If any of these errors are occurring, upgrade the Xenta 102-AX to version 2.1.9 or higher. Click here to download the APB file.

Complete upgrade instructions can be found at Upgrading a Xenta 102-AX to version 2.16 or later

Version 2.19 addresses the problems listed above as follows:

  1. M/STAT Air Flow Calibration Errors
    Fix: When calibrating a Xenta 102-AX using the M/STAT a Velocity Pressure Offset is now properly generated.
  2. Xenta 102-AX does not perform wink function properly
    Fix: After clicking Wink the a red LED on the controller flashes to identify the controller and the STR-250 displays "00" and the man icon. After approximately 45 seconds both the controller and the STR-250 return to normal.
  3. STR-250 connected to the Xenta 102-AX is not controlling the fan properly|
    Fix: The ability of the STR-250 to override the fan command on the 102-AX is disabled by default. If this functionality is required it can be turned on by setting DamperActuator.SCPTdirection.bit15 to 1.
  4. Pressure dependent mode erroneously requires airflow and fan enabled
    Fix: The 102AX no longer requires 80% Airflow Setpoint to run Heat1 in Pressure Dependent mode.
  5. Xenta 102-AX Hot Water floating control resynch fails
    Fix:  Logic has been corrected to only resynch open or resynch closed as needed. Additionally, the heating output resynchronization algorithm has changed to operate as follows:
    Two internal timers have been added to track the accumulated amount of time that heat load is 0% and at 100%. Once either of these timers reaches 30 minutes, a resynch is initiated in the respective direction of the timer. The resynch consists of activating either the open or close triac output for an amount of time equal to the user defined stroke time.
  6. Xenta 102-AX Floating Hot Water valve control failures
    Fix:  Heating output logic corrected to prevent failure.
Labels (1)
Labels:
  • TAC Vista
Attachments
102ax_2p19.zip
Tags (3)
  • Find more articles tagged with:
  • 7709
  • PeterLarsen24
  • thermostat
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of