Calibrating Airflow on a Xenta 102-AX (or MR-VAV-AX) using the M/STAT

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Calibrating Airflow on a Xenta 102-AX (or MR-VAV-AX) using the M/STAT
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3869 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Calibrating Airflow on a Xenta 102-AX (or MR-VAV-AX) using the M/STAT

Picard Product_Support
‎2018-09-07 07:09 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:08 AM

Issue

  • Step-by-step instructions for calibrating airflow on a Xenta 102-AX (or I/NET MR-VAV-AX) using the M/STAT.
  • Test and air balance procedure for balancing airflow

Product Line

EcoStruxure Building Operation, TAC INET, TAC Vista

Environment

  • Xenta 102-AX
  • MR-VAV-AX
  • M/STAT

Cause

The preferred method for calibrating airflow in Xenta 102-AX or MR-VAV-AX is through the plug-in.  However, this is not always an option, especially when the responsibility for calibrating is given to a third party test and balance company.  Pocket references exist for navigating through the M/STAT menu, but there aren't clear step-by-step instructions to tell exactly how to perform the calibration.

Resolution

Click here to download this document in Microsoft Word format

Step1.gif
  1. Connect M/STAT
    • Plug the M/STAT into the jack on the thermostat. The initial display shows the set temperature.
Step2.gif

 

  1. Enter Password
    • Press the Service button. This prompts you to enter the service mode password. Default password is 183. Use the +/- keys to set each digit and the enter key to submit. If the password is incorrect, the display will blink.
Step3.gif
  1. Airflow Parameters
    • If the password is correct, the first menu option – Unit Parameters (UP) – is displayed. Hit the select button down twice until Airflow Parameters (AP) is displayed. Press enter.
Step4.gif
  1. Cooling Low Flow Setpoint
    • The first option is Cooling Low Flow Setpoint (CLF). Press enter to view the setpoint (divided by 1000). Record this value. Press the service key to escape out of the menu.
Step5.gif
  1. Cooling High Flow Setpoint
    • Navigate to Cooling High Flow Setpoint (CHF). Press enter to view the value (divided by 1000). Record this value. Press the service key to escape out of the menu.
Step6.gif
  1. Reset Factory Calibration
    • Navigate to Factory Calibration Settings (FCS) and press enter. Use the change keys to display “YES” and press the enter key. This will set the box back to default settings. This is a good idea to do prior to every calibration. Press the service key to escape out of the menu.
Step7.gif
  1. Calibrate Low Airflow
    • Navigate to Calibrate Low Airflow (CPL). Press enter and the current airflow is displayed. Wait for the airflow to reach the CLF and level out. Once the value is steady at setpoint, press the enter key only once. The display does not change.
Step8.gif
  1. Enter Actual Low Airflow
    • Measure the actual airflow. Use the change keys to set the display value to the measured value. Press the enter key.
Step9.gif
  1. Choose One or Two-Point
    • Now Calibrate High Airflow (CPH) is displayed. If one-point (offset only) calibration is desired, press the service key to escape out of this mode and calibration is complete. If two-point (gain and offset) calibration is desired, press enter to continue to the next step.
Step10.gif
  1. Calibrate High Airflow
    • The current airflow is displayed again. Wait for it to rise to meet the CHF and level out. Once the value is steady at setpoint, press the enter key only once. The display does not change.
Step11.gif
  1. Enter Actual High Airflow
    • Measure the actual airflow. Use the change keys to set the display value to the measured value. Press the enter key. CPH is displayed again, this time as a general menu item.
Step12.gif
  1. Escape Service Mode
    • Press the service key to escape out of the menu. If you are finished configuring the box, escape all the way back out of the service menu before disconnecting the M/STAT. Disconnecting in configuration mode can leave the stat displaying “00” or other incorrect numbers.
Labels (3)
Labels:
  • EcoStruxure Building Operation
  • TAC INET
  • TAC Vista
Attachments
Tags (1)
  • Find more articles tagged with:
  • 3988
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore