Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

I/NET support for dual Network Interface Cards (NIC)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET support for dual Network Interface Cards (NIC)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2039 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET support for dual Network Interface Cards (NIC)

Picard Product_Support
‎2018-09-10 01:59 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:07 AM

Issue

Does I/NET support dual NICs (Network Interface Cards)?

Is it possible to change which network interface card I/NET uses?

Dual Network Interface Cards (NIC) will not allow selection between the Networks, option is grayed out.

Product Line

TAC INET, EcoStruxure Building Operation

Environment

  • I/NET 2.40 and above

Cause

Requirement for I/NET to have dual NIC support and option to change which network interface card I/NET uses.

Resolution

A New feature released with I/NET Seven 2.40 now allows I/NET to support dual network interface cards (NIC). The intent is to allow I/NET and Video the capability of using different Ethernet networks. This option also allows which network I/NET (and / or Video) uses.

These settings are changed via the Advanced WAN Configuration (Advanced IP button) via the I/NET Configuration Editor (see image below).

Requirements: I/NET Configuration needs to have TCPIP enabled and hardware (Ethernet card) needs to be installed on PC, I/NET (or I/O Server) must be running to select the Advanced IP button (Advanced WAN Configuration).

If the PC is configured with multiple network cards, the above shown drop-down lists will be active:

  • I/NET network
  • Video network

Use the drop-downs to select a network card for each network. You can use the same card for both networks, or you can use a unique card for each network. By using two networks, you can separate I/NET traffic from video traffic and conserve bandwidth on each network.

NOTE: If you have dual Network Interface Cards and you are not able to select between these networks (so they are grayed out) you must have the following minimum requirements configured for this option to be available in the I/NET Editor:

  • A Physical connection to its connection media. (i.e. A connected network status. If you have a status indicating Limited or no connectivity you will not be able to select between Interface cards).
  • Valid IP address and subnet mask
  • Valid Gateway IP address. (If you have no gateway router on the network then select a valid IP address within the same IP range, usually the IP of the PC is the best option here.)

If you are using wireless NIC and have issue to choose it, refer to Host number conflict on a computer with dual Network Interface Cards (NIC).

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 6140
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore