Integrating Xenta programmable controllers into a Niagara R2 UNC-520 Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Integrating Xenta programmable controllers into a Niagara R2 UNC-520 Controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1915 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Integrating Xenta programmable controllers into a Niagara R2 UNC-520 Controller

Picard Product_Support
‎2018-09-07 05:41 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:06 AM

Issue

Since both products -- Xenta programmables and the UNC 520 -- speak LON protocol, there is some assumption that integration should be seamless.  In the case of ASCs, this is true, but Xenta programmable controllers use some forms of proprietary communication that can complicate the integration.

Product Line

TAC IA Series, TAC Vista

Environment

  • Xenta programmables
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • UNC-520
  • Niagara
  • Tridium

Cause

Xenta programmables use proprietary communications for three main purposes:

  1. To communicate their online status between group members and group masters
  2. To communicate between a base unit and associated I/O modules
  3. To pass proprietary TAC Network Variables between two programmable controllers

In a UNC-520, the first function would be taken over by the new network manager (Local Lon Device).  However, the second two must use Group Bindings set through a Vista compatible network management tool like LonMaker or NL220.  If the controllers are commissioned into the UNC-520, that communication will be broken and I/O modules will go offline and no network variables will pass.

Resolution

 It is possible to engineer a TAC Vista network as usual, using an LNS management tool to create group bindings to facilitate proprietary communications.  A UNC-520, set to non-network management mode could then be implemented on top. However, any attempt to commission the devices into the UNC-520 network will break that proprietary communication.  To prevent this scenario from occurring, the simplest method is:

  1. Do not use proprietary TAC Network Variables to pass data between controllers.
    1. Use only SNVTs which will be available to a third party LON network manager like the UNC-520
    2. Make no SNVT bindings in a temporary LonMaker or NL220 database.  Let the UNC-520 handle all network management duties.
  2. Do not define Xenta I/O modules in the Menta Device Specification.
    1. Use only Xenta 421A, 422A, 451A and 452A I/O modules.  These have the capability to act as stand-alone LON nodes.
    2. Define the modules as LON nodes, configure them using Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node.
    3. Bind to the inputs and outputs of the I/O modules in the UNC-520.
Labels (2)
Labels:
  • TAC IA Series
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4512
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of