The File or Directory \VISTA DB\$queues\insertevents is corrupt and unreadable

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The File or Directory \VISTA DB\$queues\insertevents is corrupt and unreadable
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1742 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The File or Directory \VISTA DB\$queues\insertevents is corrupt and unreadable

Picard Product_Support
‎2018-09-10 11:19 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:19 AM

Issue

Error Messages:

Windows - Delayed Write Failed
Windows was unable to save all the data for the file D:\VISTA
DB _23032011\$queues\insertevents. The data has been lost.
This error may be caused by a failure of your computer
hardware or network connection. Please try to save this file
elsewhere.
Windows - Corrupt File
The file or directory \VISTA DB
_23032011\$queues\insertevents is corrupt and unreadable.
Please run the Chkdsk utility.

Product Line

TAC Vista

Environment

TAC Vista

Cause

Problem with Operating System (or) Hard Disk Fault (or) Link between $queues with Vista Database.

Resolution

As there may be several issues that are causing this, there are three options to look at:

OPTION 1:

  1. Restore the OLD TAC Vista Data Base Backup.
  2. Refer to TAC Vista Technical Manual chapter 26 for re-storing database procedure.

 

OPTION 2:

There might be a linking problem with this folder and Vista.  Here are the steps to check if this is the problem: If the problem still exists, Check for hard disk errors.

  1. Find the $queues - folder in existing database folder ( \DB\$queues)
  2. Copy the files to an other location and delete current folder (Refer to An efficient method for deleting all queued files in the $queues folder)
  3. Recreate it with same folder names and copy back the files into $queues-folder.
  4. If the problem still exists, Check for hard disk errors.

 

OPTION 3:

Check for hard disk errors, follow the below procedure:

  1. Go to "My Computer", Right click on Hard Disk Drive – typically - C, and Click on Properties.
  2. Go to Option "Tools" and Click on "Check Now" under "Error-Checking"
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5305
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore