Issue
Xdriver is enabled, Open the BCX1 editor, click "options" tag, display comm port attribute as"Xdriver comm1: 00000009", but there is no "xdriver" listed from the drop down menu when click the arrow on the right of default type of the comm port.
Product Line
Andover Continuum
Environment
- BCX1-CR-X, 4.500065
- Cyberstation 1.81
Cause
Continuum support xdriver with BCX1-CR(BCX4040) from 1.82, any version earlier than 1.82 not support xdriver with BCX1-CR controller.
Resolution
Upgrade all the Cyberstation to 1.9X.
To determine if a controller comm port is Xdriver enabled, refer to Determine if a controller comm port is Xdriver enabled.