Vista Server start hangs on trend log initialization

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Vista Server start hangs on trend log initialization
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1667 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Vista Server start hangs on trend log initialization

Picard Product_Support
‎2018-09-07 08:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:13 AM

Issue

When starting the Vista Server, the splash screen displays the current state of the startup.  It gets to the "Trend Log Initialization" screen and then hangs.

Product Line

TAC Vista

Environment

Vista Server

Cause

Queued files in the $queues folder in the Vista database are being written to the SQL database.  If the queued files folder has grown very large, it can take a very long time (hours) to write this data to SQL.  If the connection to the SQL database has been broken, then it will take an infinite amount of time.

Resolution

Check for queued files in the $queues folder

  1. Navigate in a Windows Explorer window to the Vista Database. (If you are unsure of the location, you can verify it in the TAC Vista Server Setup Vista Database tab).
  2. Go to the $queues folder
  3. Look inside the insertevents and insertlogvalues folders. This is where data is stored temporarily before it is written to the SQL database. Having queued files is not necessarily a sign of a problem. However, if there is a connection problem, these folders will continually grow in size without older queued files being written from the folder.

Allow time for the files to write the SQL

  1. Start Vista Server.
  2. Insure that TAC DSS Writer Service is running.
  3. When it gets to trend log initialization, leave the PC alone and allow time for the files to write to the SQL server.  If the size of the $queues folders are shrinking, then the process is working and after enough time, the server will start.

    Note: If you have cleared the $queues folder but it still hangs on trend log initialization, still allow plenty of time for the server to come up. There is a good chance that the Xenta controllers are passing all of their trend logs over to the SQL server. This could take hours or even overnight to complete.

Delete the queued files

  1. If the data is not of dire importance, delete all the files inside both of the $queues folder.  For an efficient method for deleting many queued files, see An efficient method for deleting all queued files in the $queues folder.

Check the SQL connection

  1. Open the TAC Vista Server Setup
    1. In version 5.1.3 and prior: Start > Programs > TAC > TAC Vista Server X.X.X > Server Setup
    2. In version 5.1.4 and later: Start > Programs > Schneider Electric > TAC Vista Server X.X.X > Server Setup
  2. Go to the SQL Server tab
  3. In the lower right-hand corner of the tab, press the Test Connection button.
    1. If it pops up a window that says "Connection test succeeded!" then your SQL connection is okay.
    2. If it fails the connection test, check the instance name. If you are using default settings it should be:
      SQL Server name: PCname\TACVISTA or (local)\TACVISTA
      Log database name: taclogdata
    3. If these are set correctly and the connection still fails, one method for reestablishing the connection is to uninstall/reinstall the Vista software.

Remove TRL files

This can also occur if the database has been upgraded from a lower versions, and still has information in the TRL files in the database.

  1. Stop the server
  2. Locate all TRL files in the $thisfil folder
  3. Delete any TRL file over 32Kb.
  4. Start the server again.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4823
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of